Discuss Boiler for static caravan - no earth in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi, currently we have a static caravan with a generator running electric to the caravan. We also have a boiler which lately have been having alot of problems with. Had plumbers out etc but still cuts out. I have an earth stake in the ground with 10mm earth to caravan fuseboard. Testing at the board 230v between live and neutral but 120v from live to earth! Does this mean the earth stake isn't deep enough in the ground or something wrong. Have found out that the boiler Infact needs an earth for it to function properly as has an electronic ignitor. So without a proper earth into the carvan the boiler becomes faulty. I have heard somewhere that generators have a floating earth and some people have said to link neutral and earth at the generator in order to get the boiler working. What other options is there.
 
This is likely to be a problem with the N not being tied to earth.
Have you tested earth loop impedance?
 
Check at the generator to see if the N & E are linked. If you have the manual (or make+model to search on-line) it might say how it is configured.

If you are feeding a single load than an IT (isolated) supply has some obvious safety advantages and allows systems to continue under single fault conditions, but it is not good for more than one load unless fitted with insulation monitoring and under competent supervision (e.g. ship supply, hospital theatre supply, etc).
 
Last edited:
The On Site Guide has a good section on earthing of generator sets. A floating earth is not to be used to supply more than one item of class 1 equipment, so a neutral to earth link will be needed I think.
 
As mentioned above the generator probably doesn't have L-N linked , Iv owned a few small (under 15 KVA) generators and all of them have not had a L-N link. The earthing point on the chassis of the generator just connects to the cpc/earth pins of the outlets,

The earth in this case is basically a bonding conductor and making sure if there is a fault then the earth for each appliances is at the same potential, and the set up is normally isolated from true earth (see attached picture)

It is normally very easy to see if the generator is this configuration by just removing the cover on the part with the socket outlets, obviously with the generator off
 

Attachments

  • Screenshot_20210125-131012_1.png
    994.6 KB · Views: 21

Reply to Boiler for static caravan - no earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
Hi all Mate of mine is getting a new utility room fitted, the kitchen fitting company have brought in their electricians for first fix and to be...
Replies
5
Views
2K
A customer has a 7kva open frame site generator.The 230v output is floating neutral which would have to be earthed. In an article titled invertor...
Replies
4
Views
1K
I was away at the weekend & the electrician came round to fix something. While there he decided to condemn an outdoor electrical light as he said...
Replies
13
Views
2K
Like a host of UK residents recently (230% increase in genny sales apparently), I've just invested in a small (3500W) portable, dual fuel...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock