So with no more information than a blue plastic pipe entering a building and then converting to copper you have decided it does not need bonding? Without any information as to where that copper goes or how it is installed which could make it extraneous?
You need to google the definition of extraneous.
 
Im not talking about the plastic pipe. I am talking about the copper installation in the outbuilding. You do not know that it is not extraneous without testing it first.
 
Im not talking about the plastic pipe. I am talking about the copper installation in the outbuilding. You do not know that it is not extraneous without testing it first.

Indeed. But if testing shows it to be extraneous, the problem may be working out WHY it's extraneous and therefore WHERE it should be bonded.
 
Well when I went to school plastic did not make a good material for conducting electricity.

Read post #26!! I know the plastic pipe is not conductive ffs. I am talking with regard to the copper installation in the outbuilding. We know nothing about it from the OP's opening post so you cannot possibly know if it is extraneous or not as you don't have enough information to make that judgement.
 
Last edited by a moderator:
Again, the definition of extraneous needs to be googled.

I know what an extraneous conductive part is and what defines it (Extraneous-conductive-part: A conductive part liable to introduce a potential, generally earth potential, and not forming part of the electrical installation). How do you know it is not from the limited information the OP has provided regarding the copper installation pipework?
 
NO the incoming pipe is plastic.

Yes the incoming pipe is plastic, but the installation it feeds is copper. There is no information as to how extensive the copper installation is or whether it is all surface pipework on plastic clips or mostly buried in the concrete floor structure or it could even go back underground as copper to feed another building.

Without further information there is no way to know whether or not the installation pipework will be an extraneous conductive part.
 
Yes the incoming pipe is plastic, but the installation it feeds is copper. There is no information as to how extensive the copper installation is or whether it is all surface pipework on plastic clips or mostly buried in the concrete floor structure or it could even go back underground as copper to feed another building.

Without further information there is no way to know whether or not the installation pipework will be an extraneous conductive part.

544.1.2 says "The main protective bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises."

Since it refers to the point of entry of the service, rather than the point of entry of the pipework, it appears to be saying that, even if the reason that the copper pipework is extraneous is that it feeds out underground in copper, the main bond should still be made at the incoming point.
 
Yes the incoming pipe is plastic, but the installation it feeds is copper. There is no information as to how extensive the copper installation is or whether it is all surface pipework on plastic clips or mostly buried in the concrete floor structure or it could even go back underground as copper to feed another building.

Without further information there is no way to know whether or not the installation pipework will be an extraneous conductive part.

So the incoming pipe is plastic with a bond on it that's not needed. Ok we got there.
Yes it could go underground again (like the gas has and we said move the bond over to that pipe), and if it was copper then it would be bonded at that point would it not.
Am I right in thinking if a house had plastic gas & water incoming pipes and copper installation pipes that did not go underground again, you would bond the pipe work?
TJ, I think your comment of the word "Stupid" over steps the mark!!
 
544.1.2 says "The main protective bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises."

Since it refers to the point of entry of the service, rather than the point of entry of the pipework, it appears to be saying that, even if the reason that the copper pipework is extraneous is that it feeds out underground in copper, the main bond should still be made at the incoming point.

Which supports my point exactly.

Although you would have to check exactly what they mean when they say 'service' and how you apply it. I would say in the situation that it is not the incoming service which is being bonded but the installation pipework and as such would be best to be bonded at the point that the extraneous part enters the installation.
 
?
Yes. your interpretation is correct.
My immediate thought was that it should be bonded, but I couldn't understand why it hadn't been done as the gas supply is an easy connection within 2 metres of the CU and all services were put in at the same time, 10 years ago. The water stopcock and bonding point are miles away.
Pete


Did it comply then?
 
Which supports my point exactly.

Although you would have to check exactly what they mean when they say 'service' and how you apply it. I would say in the situation that it is not the incoming service which is being bonded but the installation pipework and as such would be best to be bonded at the point that the extraneous part enters the installation.

I agree. It would be better to bond at the point where the metallic pipework enters the building, which isn't what the regs appear to be saying.
 

Reply to Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock