It is not nonsense, protective conductors have got to be continuous.
It is up to you if you want to use one conductor for water and another conductor for gas but continuity is key no breaks at all.
Guidance note 8 (earthing & bonding) page 57.

Yes it is nonsense, your post clearly stated that main bonding must be one continuous conductor and not two separate conductors.
There is nothing in the regulations or guidance notes to support this.
Main bonding can be two or more separate conductors, and it is often better to do it this way unless items requiring bonding are close to each other.

Following your suggestion of one continuous conductor for all main bonds would lead to an excessively long bonding conductor linking gas, water, ducting, structural steel, lightning protection etc etc, utter nonsense.
 
Quite right,

what if the water tap is 30 metres away from the gas meter LOL, I personally like to use an earth block and seperate cabling labelled, I have many many times used one cable when the 2 services are together, but it is no issue using seperate cables with the correct do not remove labelling on.
 
No 2 cabes not okay by the current regs.
The protective bonding cable has got to be continuous no breaks at all.
Well if you connect 1 to the water and 1 to the Gas, oth from the MET assuming it's the only bonding required both conductors would be continuous wouldn't they? they would be in my book, no breaks, just 2 conductors, how anyone can dispute this is, quite frankly beyond me.
 
Thanks Tel
Right that's war, actually it's not bad spelling, it's bad punctuation, can we please have a bad punctuation icon, for the pedants in the Forum? thanks is spelt thanks it's the apostrophe that's missing in thank's. So thank's for that, oh sorry, that should be a full stop.
 
NSomething has irked mycuriosity with this post and I have come to the conclusion that there is a degree of misinterpretation of the regulation regarding Main bonding.
Some folk are saying that the conductor must be continuous, I agree with that statement, but only if you are taking 1 conductor to the water or gas pipe and then on to the whichever pipe.
I get the impression that the Neuvo Electricians are reading thi literally, meaning you take 1 bonding conductor to 1 pipe and on to the next without a break, reasonable, if thats your prfered method, but the best way and most common way is to take 1 conductor from the MET to each bit that requires bonding, as I said before how can this be misconstrued? it's down to logic, far to many people read something, misunderstand it and think it's Gospel, I blame the training estabishments. Some good some not so good, this is what is wrong with the way we train people these days in my opinion. As Camerabloke would say "where is the popcorn"?
 
Right that's war, actually it's not bad spelling, it's bad punctuation, can we please have a bad punctuation icon, for the pedants in the Forum? thanks is spelt thanks it's the apostrophe that's missing in thank's. So thank's for that, oh sorry, that should be a full stop.
This is very petty.If it is a mistake why make it the main point and divert from real material content?
You guys you have a lot of time on your hands.
 
Right that's war, actually it's not bad spelling, it's bad punctuation, can we please have a bad punctuation icon, for the pedants in the Forum? thanks is spelt thanks it's the apostrophe that's missing in thank's. So thank's for that, oh sorry, that should be a full stop.
This is very petty.If it is a mistake why make it the main point and divert from real material content?
You guys you have a lot of time on your hands.
 
i
This is very petty.If it is a mistake why make it the main point and divert from real material content?
You guys you have a lot of time on your hands.
Not petty at all how many posts have you tried to read with bad spelling and punctuation, and ended up with a migraine? By and By I have all the time in the world now I have been retired, after spending 55 plus years in this trade.
 
You will fail am2 if using separate lengths in northern Ireland anyway I know that for a fact as our apprentice failed on that and only that. Use continuous lengh to be safe
 
You will fail am2 if using separate lengths in northern Ireland anyway I know that for a fact as our apprentice failed on that and only that. Use continuous lengh to be safe
So he failed for not following the design?
 
This is very petty.If it is a mistake why make it the main point and divert from real material content?
You guys you have a lot of time on your hands.
You are obviously someone who can read gibberish. We are not all as talented as you, can you please decipher the OP then? we are only mortals after all.
 
I am a pedant, so I am very tempted to jump in here right now, particularly as I like spelling and grammar to be correct, as also punctuation and the proper use of figures of speech, bearing in mind that additionally the use of a split infinitive should be avoided, always avoid aliteration and ending a sentence with a preposition is something up with which I will not put!
 
Question:
I have a bit of bonding cable that goes from my water pipe, (ok, the house's pipe) then to the gas pipe and thereafter to the MET. It leaves the waterpipe, with its nice safety label intact, then gets attached to the gas pipe with another proper safety label, the bare conductor being wrapped round the screw, not cut, and finally to the MET. That, in my view is one continuous conductor.
However, if it is snipped at the gas pipe label, say a terminal is added, then the next run also has a terminal added, and both terminated ends are properly secured to the warning label, then finally the second length goes to the MET, then is that not also a continuous conductor? In effect, it is, surely?
In practice, it differs because undoing the midpoint temporarily then leaves the system unbonded, but if the bonding cable is not cut and joined at the gas pipe, removing that gas pipe label will leave the rest of the system intact. Now, I'm just trying to get my head round this, ok? It seems like terminology is causing confusion...continuous may be meant to mean one unbroken run, or maybe it means don't go wandering off popping short lengths into connectors and joining them up any old where?
I'm thinking that if the MET is in the "middle" of a house, and the gas comes in 10m away on one side, and the water 10m away in the other direction, then we have two things:
1. Quite a big house
2. A situation where it might be preferable for 2 separate bonding cables, one from each incoming supply, to the MET, each about 10m long, rather than running a 20m cable from one to the other then another 10m to the MET, which I would think would be awkward and more prone to damage, especially the 20m run.
Just my ramblings, and not those of a qualified person, however I am old enough to be shouted at, if required.
 

Reply to Bonding to Gas and water am2 in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
526

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock