Discuss BS3871 on EICR classifiaction code? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
I have searched for an answer to this question but to no prevail.

BS3871's.... should these be changed? I have just done an EICR on a board with these and no RCD for lights serving bathroom but it has an RCD protecting all sockets, shower and the cooker circuit... now I have given 2 x C2 codes because 1 the RCD doesn't trip in the allowed time and 2 for no RCD protection or supplementary bonding etc for the lights in bathroom

BUT hypothetically... if it was all protected by a fully working RCD would I be ok in saying BS3871's are ok still? Or does it need to comply with regards to disconnection times? If so where do I find these disconnection times?

Thanks in advance
 
I have searched for an answer to this question but to no prevail.

BS3871's.... should these be changed? I have just done an EICR on a board with these and no RCD for lights serving bathroom but it has an RCD protecting all sockets, shower and the cooker circuit... now I have given 2 x C2 codes because 1 the RCD doesn't trip in the allowed time and 2 for no RCD protection or supplementary bonding etc for the lights in bathroom

BUT hypothetically... if it was all protected by a fully working RCD would I be ok in saying BS3871's are ok still? Or does it need to comply with regards to disconnection times? If so where do I find these disconnection times?

Thanks in advance
I believe BS3871s are still considered compliant. You'll find max Zs and other info for these in the current on site guide.
 
Surely if the lighting in the Bathroom is above 2.25m no RCD protection, CPC in place, its no code?
True, but irrelevant. If no RCD was required when it was installed, then it's a C3.
You test to the current regs. Anything that doesn't meet the current regs, but met the regs. in force when it was installed is a C3*. Anything that doesn't meet the current regs, and didn't meet the regs in force when it was installed is a C2.

* I'm referring to 'modern' wiring, not stuff installed pre '50's, so please don't bring up fused neutrals.
 
So are you saying if it’s above 2.25M in bathroom and has no RCD protection and no supplementary bonding that is a no code?

obviously C3 for no RCD on lighting in general, but the bathroom requirement I would have put at C2.

this is a question not a disagreement.
 
It seems its a C3 = Improvement recommended, as it does not conform to the latest regulations (which are deemed to be an improvement), but not a C2 or C1 as it does not present a hazard.
 
That would be 701.415.2, and 411.3.2.2, 701.411.3.3, 411.3.1.2, if this was a downlighter only accessible with a tool, how would you code that then?

I suppose in truth the sensible thing to do is to protect anything in a shower or bathroom with an RCD which in essence everything in a modern two RCD board is.
 
The location of the luminaire is not relevant it serves a location containing a bath or a shower, zones in this case are irrelevant.
IMO the location of the luminaire is relevant in some cases, from a coding point of view rather than compliance. If it could only be reached by climbing a ladder, then a C3 for no RCD and no supp bonding. If within reach, then C2 for the same
 
That would be 701.415.2, and 411.3.2.2, 701.411.3.3, 411.3.1.2, if this was a downlighter only accessible with a tool, how would you code that then?

I suppose in truth the sensible thing to do is to protect anything in a shower or bathroom with an RCD which in essence everything in a modern two RCD board is.
It is serving the location so whether a tool is required or not is neither here nor there.
 
True, but irrelevant. If no RCD was required when it was installed, then it's a C3.
You test to the current regs. Anything that doesn't meet the current regs, but met the regs. in force when it was installed is a C3*. Anything that doesn't meet the current regs, and didn't meet the regs in force when it was installed is a C2.

* I'm referring to 'modern' wiring, not stuff installed pre '50's, so please don't bring up fused neutrals.
Not really. A socket installed to an earlier edition which could reasonably be used to power equipment outside would be a C2 if no RCD protection.

I think you meant 'you inspect to the current regs' testing hasn't changed over the years (part for maybe AFDD's). ???
 
C2

Absence of supplementary bonding where
required, such as in a location containing a
bath or shower, where any of the following
three conditions are not satisfied:
❍ All final circuits of the location comply with
the requirements of Regulation 411.3.2 for
automatic disconnection, and
❍ All final circuits of the location have
additional protection by means of a 30 mA
RCD, and
❍ All extraneous-conductive-parts of the
location are effectively connected to the
protective equipotential bonding (main
earthing terminal).

So just because it was compliant 50 years ago doesn't mean it isn't a C2 on an 18th edition EICR
 
The latest best practise guide suggest that :
for class 2 fittings

Absence of supplementary bonding for installed Class II equipment where required (such as in a location containing a bath or shower), in case the equipment is replaced with Class I equipment in the future

this does not require reporting or any code
 

Reply to BS3871 on EICR classifiaction code? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
375
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
709
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
536
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
649

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock