Discuss C3s putting you in harms way ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Does the legislation say "Metal" or "Flame proof" or even "Flame retardant"? Haven't got my copy to hand.
Non-Combustible is the phrase I believe - and an example is given of steel. No idea if the BS standard for CUs says something different now, but there's no reason in principle why they couldn't find a suitable plastic or other material that was non-combustible - I just suspect it would cost more so they went with the cheapest option.

It would be handy to have a non-combustible AND non-conducting material for TT installations.
 
https://electrical.------.org/wirin...ble-enclosure-requirement-for-consumer-units/

The backs of boards should be sealed on reading this, and manufactures can bring new.materials to market if they prove non combustable.
Care homes and the.like ain't part of this even tho no differnece in my eyes ..

And over all they are blaming bad workmanship, but the work could of been good for 10 years prior to fire.
 
You may be over-thinking it. That bit in the Introduction says that non-compliant installations do not have to be upgraded. It does not say that existing installations that have been installed in accordance with earlier editions of the regulations are deemed to comply with this edition if they are not unsafe for continued use.

What has yet to be determined by a court ruling is whether the law requiring that "electrical safety standards are met" means that an existing installation has to comply with every aspect of BS 7671:2018 or only some, and if the latter, which.

A consensus seems to have emerged that it must have no non-compliances coded as C1 or C2. Superficially reasonable, if we think it reasonable to enshrine in law the can of worms which is the significantly indeterminate nature of many C2-or-C3 decisions ¹ .

But, and this is where you may be under-thinking it, there is no basis in fact for any determination based on C1/C2/C3. None whatsoever.

The lawmakers have done a truly abysmal job. Leaving aside the is-it-a-C2-or-a-C3 issue, they could have required landlords to have an EICR carried out which complied with the current edition of the Wiring Regulations (i.e. the carrying out of the EICR had to be in accordance, not the installation) and that any C1 or C2 conditions be rectified within x days and a new EICR done.

But they didn't. What they did was unbelievable, really. (Or is it, sadly, all too believable?)

They required that private landlords must ensure that the electrical safety standards are met during any period when the residential premises are occupied under a specified tenancy.

And they defined "electrical safety standards" as "the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018".
QUOTE]

From the Gov guidance document @timhoward linked to above, section 8:
 
Non-Combustible is the phrase I believe - and an example is given of steel. No idea if the BS standard for CUs says something different now, but there's no reason in principle why they couldn't find a suitable plastic or other material that was non-combustible - I just suspect it would cost more so they went with the cheapest option.

It would be handy to have a non-combustible AND non-conducting material for TT installations.
Non-flame propagating would be term;

Non-flame propagating. Liable to ignite as a result of an applied flame but, after the flame is removed, does not propagate further and extinguishes itself within a limited time.

That term however applies to containment systems.

The Regulation pertaining to domestic CUs is;

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation
132.12.
NOTE: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.

How about because the Wiring Regulations, and hence the law, do not mandate it?

Or because the fact that at the time you did the inspection plastic CUs could still be installed in offices, shops, schools, pubs, restaurants, care homes, indicated to you that plastic CUs did not need to be replaced as a matter of urgency?
I don't normally berate other members but I'm sorry, get a clue. Wiring Regulations are non-statutory (not law), the statue (law) applicable to Electricians and Electrical Installations is Electricity at Work 1989.
If you're going to spout rubbish,please make it informed and researched rubbish, other you just look stupid.
 
Non-flame propagating would be term;

Non-flame propagating. Liable to ignite as a result of an applied flame but, after the flame is removed, does not propagate further and extinguishes itself within a limited time.

That term however applies to containment systems.

The Regulation pertaining to domestic CUs is;

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation
132.12.
NOTE: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.


I don't normally berate other members but I'm sorry, get a clue. Wiring Regulations are non-statutory (not law), the statue (law) applicable to Electricians and Electrical Installations is Electricity at Work 1989.
If you're going to spout rubbish,please make it informed and researched rubbish, other you just look stupid.
Your forgetting the EICRs for rented properties are now a legal requirement. And the guidance to landlords is that the EICR ensures there properties Comply with the latest version of BS7671. An EICR was not a mandatory document. But has that changed. I will not comment yes or no because I am not a trained lawyer barrister or judge. Thats the whole point. We are only putting our personal view points on a forum. A court and there interpretation of case law is another matter entirely
 
Yes, but when you read the 18th you see that it does not contain a single standard which existing installations have to meet - it only applies to the design, erection, additions, alterations, and verification of electrical installations designed after 31st December 2018.

The guidance you quote doesn't change what the numpty lawyers wrote. If they even were lawyers, and not junior off-shore office clerks working self-employed for Serco.
 
Your forgetting the EICRs for rented properties are now a legal requirement.
They aren't, strictly speaking - there's nothing in the law which makes them so. It's just that it's the way that makes the most sense. It's a bit like Part P not actually requiring work to comply with BS 7671, but the reality being it makes precious little sense to do otherwise.


And the guidance to landlords is that the EICR ensures there properties Comply with the latest version of BS7671.
Except of course that is impossible, unless you use the special definition of "comply".

A court and there interpretation of case law is another matter entirely
Which in all probability will never happen - any landlord faced with a report he doesn't like could have the place totally rewired using russ andrews cryogenically treated cables and a gold-plated CU for less than the cost of lawyers.
 
Yes, but when you read the 18th you see that it does not contain a single standard which existing installations have to meet - it only applies to the design, erection, additions, alterations, and verification of electrical installations designed after 31st December 2018.

The guidance you quote doesn't change what the numpty lawyers wrote. If they even were lawyers, and not junior off-shore office clerks working self-employed for Serco.
It doesn't matter what the 18th says as it has no legal standing. The legal authority comes from the landlords having a legal obligation to have an eicr that complies with the 18th. And thats from government legislation not any edition of BS7671.
 
It doesn't matter what the 18th says as it has no legal standing. The legal authority comes from the landlords having a legal obligation to have an eicr that complies with the 18th. And thats from government legislation not any edition of BS7671.
Since you clearly disagree with
They aren't, strictly speaking - there's nothing in the law which makes them so.
perhaps you'd like to quote the part of The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020 - http://www.legislation.gov.uk/uksi/2020/312/contents/made which imposes a legal obligation to have an eicr that complies with the 18th.
 
Since you clearly disagree with

perhaps you'd like to quote the part of The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020 - http://www.legislation.gov.uk/uksi/2020/312/contents/made which imposes a legal obligation to have an eicr that complies with the 18th.
And thats exactly where this thread gets a definitive answer phew ? There is a lot of information out there. But nothing in government guidelines that says Landlords EICRs or anyone else's EICRs have to legally comply with the current edition of the regulations. Just a legal requirement for landlords to have an EICR carried out every 5 years. ?
 
And thats exactly where this thread gets a definitive answer phew ? There is a lot of information out there. But nothing in government guidelines that says Landlords EICRs or anyone else's EICRs have to legally comply with the current edition of the regulations. Just a legal requirement for landlords to have an EICR carried out every 5 years. ?
Given that the wording in the above legislation doesn't, iirc, state that the outcome MUST be satisfactory, a LL could just have an EICR undertaken to 18th edition, have it come back as unsatisfactory and yet still have met the requirements of the legislation. Surely not?
 
Given that the wording in the above legislation doesn't, iirc, state that the outcome MUST be satisfactory, a LL could just have an EICR undertaken to 18th edition, have it come back as unsatisfactory and yet still have met the requirements of the legislation. Surely not?
Indeed.
But the law further stipulates that any remedial work that is deemed necessary, resulting in the unsatisfactory report, must be done within 28 days from when the report was issued.
 

The backs of boards should be sealed on reading this, and manufactures can bring new.materials to market if they prove non combustable.
Care homes and the.like ain't part of this even tho no differnece in my eyes ..

And over all they are blaming bad workmanship, but the work could of been good for 10 years prior to fire.
The IET also put out other guidance in a Q+A, apparently contradicting the guidance you linked to above. The forum censors links to wiring matters, but if you put "Consumer units: a brief overview" into your search engine (quote marks included) it should come up top of the list:


When I put cables into a new metal consumer unit, do I have to use intumescent glands to enforce the fire protection of the consumer unit?

No, the metal consumer unit is designed to encase a fire within it and restrict the likelihood that a fire may spread. Manufactures’ have carried out exhaustive tests on this issue and have found that the cable entry does not have to continue the fire rating of the consumer unit, for it to be effective. The only requirement is to keep IPXXD or IP4X on the horizontal surfaces (Reg 416.2.1) and IPXXB or IP2X on all other surfaces (Reg 416.2.2). Intumescent glands and sealants may be used to ensure the IP ratings are maintained, but they are not a requirement and existing methods of ensuring IP are acceptable.
 
Very interesting analysis of this ver hot topic! Above this is why it is down to the inspectors own engineering judgement on the day to an extent. As there are no real rules or legislation to cover every eventually we may come across. The electrical industry is so varied and wide that a dossier to cover all would be ridiculous in size!
 
Very interesting analysis of this ver hot topic! Above this is why it is down to the inspectors own engineering judgement on the day to an extent. As there are no real rules or legislation to cover every eventually we may come across. The electrical industry is so varied and wide that a dossier to cover all would be ridiculous in size!
almost as bigb as my dossier at Police HQ., Anfield.
 

Reply to C3s putting you in harms way ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
558
Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
644
Hi I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back...
Replies
7
Views
902
Hi, I have just had an EICR carried out and it has comeback with a few C2s. The only one I disagree with is the electrician raised as a C2 the...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock