Time will tell what code lack of AFDDs will be in 5 years time, only 99.99999% of properties affected by that one....some very unhappy landlords who were overcharged for a dual RCD board this time round no doubt...
 
I had a great one for remedials recently.
C1 for lack of RCD protection
C1 for plastic CU.
C2 for lack of two colours sticker
C2 for lack of last inspection sticker ?!
C2 for lack of RCD test sticker
C2 for cables inadequately supported

Apparently a quote of £1200 for a new RCBO board and "other urgent safety-critical repairs" though I didn't see this for myself.

So I slapped 3 stickers on, including one the inspector should have put on himself, knocked in 3 cable clips, then looked at the RCD issue.
It was a split load board and 4 of the 5 circuits on the non-RCD side had RCBOs. So only one B6 in the whole board was not RCD protected and it's sole purpose in life was supplying the light in the cupboard where the CU and meter was. And that got a C1! Needless to say I didn't change the board.
Not even AFDDs should get to £1200 for a new board unless it's ludicrously large!
 
I had a great one for remedials recently.
C1 for lack of RCD protection
C1 for plastic CU.
C2 for lack of two colours sticker
C2 for lack of last inspection sticker ?!
C2 for lack of RCD test sticker
C2 for cables inadequately supported

Apparently a quote of £1200 for a new RCBO board and "other urgent safety-critical repairs" though I didn't see this for myself.

So I slapped 3 stickers on, including one the inspector should have put on himself, knocked in 3 cable clips, then looked at the RCD issue.
It was a split load board and 4 of the 5 circuits on the non-RCD side had RCBOs. So only one B6 in the whole board was not RCD protected and it's sole purpose in life was supplying the light in the cupboard where the CU and meter was. And that got a C1! Needless to say I didn't change the board.
The guy who did that should be :

a) ejected from his scheme
b) charged with fraud.
 
And sadly, the way the world is heading I have to agree with him, trying to be honest and doing the right thing is just giving more leverage to a lawyer if god forbid it ever got that far
Have being reading this thread with great interest. No need for me to elaborate on previous posts concerns about what we as sparks "are leaving ourselves open for" as we go about our normal daily work. I am currently going through my first professional liability claim. 25 years with same insurance company. Have deliberately gone with the "top of the range" provider (840.00 euros a year for a sole trader).
In the case I, m involved in the issue has to do with the type of concrete used by the builder which has caused damage to cabling. Here's the interesting bit. Because I personally have not being negligent in any aspect my work, the insurance company feel they have no liability. It has been suggested to me to pursue the concrete supplier.
Not the kind of service I expected, but as "welchyboy" alludes to, its the "way the world is"
 
Have being reading this thread with great interest. No need for me to elaborate on previous posts concerns about what we as sparks "are leaving ourselves open for" as we go about our normal daily work. I am currently going through my first professional liability claim. 25 years with same insurance company. Have deliberately gone with the "top of the range" provider (840.00 euros a year for a sole trader).
In the case I, m involved in the issue has to do with the type of concrete used by the builder which has caused damage to cabling. Here's the interesting bit. Because I personally have not being negligent in any aspect my work, the insurance company feel they have no liability. It has been suggested to me to pursue the concrete supplier.
Not the kind of service I expected, but as "welchyboy" alludes to, its the "way the world is"
What was it about the concrete that caused the damage mate?
 
Have being reading this thread with great interest. No need for me to elaborate on previous posts concerns about what we as sparks "are leaving ourselves open for" as we go about our normal daily work. I am currently going through my first professional liability claim. 25 years with same insurance company. Have deliberately gone with the "top of the range" provider (840.00 euros a year for a sole trader).
In the case I, m involved in the issue has to do with the type of concrete used by the builder which has caused damage to cabling. Here's the interesting bit. Because I personally have not being negligent in any aspect my work, the insurance company feel they have no liability. It has been suggested to me to pursue the concrete supplier.
Not the kind of service I expected, but as "welchyboy" alludes to, its the "way the world is"
Unfortunately price of insurance seems to be no guarantee that they'll be any good when you need them - and the only way to find out is to need them, which isn't ideal!

Besides which, trying to work out who is actually doing the underwriting is often not simple and turns out to be the same very few names in any case...

I guess at least you get someone saying you weren't negligent! Sounds like the builder's insurance should be stepping in, but no doubt they'll claim it's an 'electrical issue...' etc...
 
I guess at least you get someone saying you weren't negligent! Sounds like the builder's insurance should be stepping in, but no doubt they'll claim it's an 'electrical issue...' etc...
Yes. Its a "cu de sac" basically. Builder long gone anyway. But when you consider the pages and pages of stuff you receive on paying for public liability it would be really nice if someone told you upfront what you can realistically expect to happen in the event of a claim. I am disappointed but can't say I, m totally surprised. Yes, it cost me a night or two, s sleep but I am determined to draw a, line in the sand and not allow it fester. I, m stung but not bankrupted. Am grateful for that
 
Have being reading this thread with great interest. No need for me to elaborate on previous posts concerns about what we as sparks "are leaving ourselves open for" as we go about our normal daily work. I am currently going through my first professional liability claim. 25 years with same insurance company. Have deliberately gone with the "top of the range" provider (840.00 euros a year for a sole trader).
In the case I, m involved in the issue has to do with the type of concrete used by the builder which has caused damage to cabling. Here's the interesting bit. Because I personally have not being negligent in any aspect my work, the insurance company feel they have no liability. It has been suggested to me to pursue the concrete supplier.
Not the kind of service I expected, but as "welchyboy" alludes to, its the "way the world is"
You say it’s a claim on your prof. Indemnity ins was the matter over an eicr you carried out I take it, or with cabling that you personally installed?
 
New posts

Reply to C3s putting you in harms way ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
589
Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
648
Hi I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back...
Replies
7
Views
907
Hi, I have just had an EICR carried out and it has comeback with a few C2s. The only one I disagree with is the electrician raised as a C2 the...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock