Hi all,

just wandering what the view is on running a 2.5mm radial circuit behind a skirting board when it's fully protected by a new 17th ed. RCD protected CU.

thanks in advance

Neil
 
Do you mean running round the perimeter of the room behind the skirting or simply running up to the socket from floor level behind skirting.

I think one is fine

I think the other stinks.
 
My view is that this should not be done presuming you mean running the cable horizontally behind the skirting board to the next outlet. Behind the skirting board is NOT a designated safe zone and will be at risk of damage unless MECHANICALLY protected. RCD protection is ADDITIONAL protection only and should not be relied on as a sole method of protection.

:thumbsup
 
Do you mean as in zonal ....................... well as Trev said quite a lot of times cables come into sockets via skirting but that of course would be classed a zone due to the accessory.

Technically a skirting is not a zone
 
Yeah, we bought an ex-navy property, the installation is done in 20 mm steel conduit! Where would you find this nowadays?
 
IMO the area below a socket is a zone and cables can be ran up from below floor level STRAIGHT up to the outlet. The skirting around the room whether or not it is within 150mm of floor level is not a safe zone as the wood butchers will need to come along and put pointy things in it to fix it. I would not therefore run cables around the perimiter of a room behind skirting boards.
Rough as a badger's arse(as we say in the frozen north)
:)
 
safe zones:

Safe-Zones.jpg
 
Although i do have a quiery with this.. My brother is wanting skirting board lights.. (DONT ASK WHY! lol) but he has a solid floor.. Meaning im going to have to run cable from each light UP and DOWN and UP and DOWN to the ceiling and then to the light.. Thats alot of cable.. and alot of chasing! :p

Any way around this?
 
Although i do have a quiery with this.. My brother is wanting skirting board lights.. (DONT ASK WHY! lol) but he has a solid floor.. Meaning im going to have to run cable from each light UP and DOWN and UP and DOWN to the ceiling and then to the light.. Thats alot of cable.. and alot of chasing! :p

Any way around this?

Skirting trunking - probably get some nice looking stuff nowadays.
 
Although i do have a quiery with this.. My brother is wanting skirting board lights.. (DONT ASK WHY! lol) but he has a solid floor.. Meaning im going to have to run cable from each light UP and DOWN and UP and DOWN to the ceiling and then to the light.. Thats alot of cable.. and alot of chasing! :p

Any way around this?

Stick an accessory (ie lights) in there and you have created a safe zone vertically and horizontally so no issue, also the skirting board lights are low voltage. You can even purchase specially designed/constructed skirting for this sole purpose, GOOGLE is your friend :thumbsup
 

Reply to Cable Behind Skirting Boards? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
312
Hi guys. It would be really useful to run this past you and get a consensus/input from you for what would be a realistic amount to charge for an...
Replies
15
Views
2K
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
898
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock