Discuss Cable Current Capacity - Solar Inverter vs Normal Loads in the DIY Electrical Advice area at ElectriciansForums.net

aesmith

-
DIY
Reaction score
25
Hi,first off this does not relate to work I intend to DIY. I'm trying to sanity check information I've been asked to provide to the installers.
I want the solar invertert to connect in the garage, where there's a DB fed from the house via SWA.

This is what's asked ..

As the proposed PV inverter is 5kW (21A) we would need to know what loads are regularly used in the garage to know if the 25mm2 cable has enough “room” left in it to carry an additional 21A.

I can provide information on the loads as requested, but then i started to think isn't this the wrong way round? Won't solar generation be subtracting from the load rather than adding to it? Or does it not work that way?


 

Reply to Cable Current Capacity - Solar Inverter vs Normal Loads in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I have a bathroom fan with a moisture detector that turns it on and off. It also has a control circuit to turn it on/off when moisture is not...
Replies
1
Views
262
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Good Morning All! Always appreciate reading the great ideas and conversations in the forums, and now actually have a chance to ask a question...
Replies
0
Views
871
Hi all. We have had 7x 400w solar panels for a number of years now on our roof which is se/nw facing end terrace. 4 on se side 3 on nw side...
Replies
0
Views
823
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
553

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock