Found two 25m cable reel extensions on a pat test yesterday with no RCDs should they be automatically taken out of service. They were at least 10 years old. The 5th addition says up to 15m max?
 
You can get extension reels in all sorts of length I see Screwfix selling a 45m one, from a reputable supplier. We have a rule of thumb that where the earth bond exceeds 0.18 ohm (I believe this equates to the suggested lengths in the CoP) that it is recommended it is only used with 30ma rcd protection, of course this does not take into consideration any volt drop issues.
 
You can get extension reels in all sorts of length I see Screwfix selling a 45m one, from a reputable supplier. We have a rule of thumb that where the earth bond exceeds 0.18 ohm (I believe this equates to the suggested lengths in the CoP) that it is recommended it is only used with 30ma rcd protection, of course this does not take into consideration any volt drop issues.
Unwound the 25m reel was failing at 0.56 ohms. Before I started doing the maths to check !
 
Your tester probably has a default setting and sees the earth bond reading as too high when in fact it is just the nature of reels length.
 
What tester are you using? Some have settings for different length reels or a setting to put your own pass/fail value in if it's an odd length reel.
 
You can't take them out of service for not having RCDs. The socket feeding them will more often than not have RCD protection.
 
Are you talking about the RCD on the DB ??? They’re certainly not using a plug in RCD.

But it's an extension lead, not a permanent bit of wiring. Can be plugged into any 13A socket.
 
Sorry, I've just realised the length of cable is your issue. I ignored that bit in my rush to read it. I'll dig out my code of practice and remind myself what it says.

I'm pretty sure you're right though. Isn't it over 12m they need to have a built in RCD?

Haven't got the 5th edition yet, not sure if anything has changed in that. I suspect not.
 
It's not always the same figure. It's 12, 15 or 25m depending on csa of cable.

See table 15.4 of code of practice.
 
13A fuses have Zs limit of 2.3 ohms (Table 41.2) so assuming your supply Zs is around 1 ohm at the socket then if your cable R1+R2 is 1.3 ohm or less no problem?
 
13A fuses have Zs limit of 2.3 ohms (Table 41.2) so assuming your supply Zs is around 1 ohm at the socket then if your cable R1+R2 is 1.3 ohm or less no problem?

They do give specific limits on length in the ISITEE code of practice though.
 
They do give specific limits on length in the ISITEE code of practice though.
Not as such.

They recommend max lengths of 12/15m for 1.25/1.5mm CSA in section 10.10, and also that longer leads should have RCD protection but that might be part of the installation.

However, 15m of 1.5mm is only 0.36 ohm R1+R2 (from OSG Table I1) so well short of any limit on OCPD disconnection.
 
Not as such.

They recommend max lengths of 12/15m for 1.25/1.5mm CSA in section 10.10, and also that longer leads should have RCD protection but that might be part of the installation.

However, 15m of 1.5mm is only 0.36 ohm R1+R2 (from OSG Table I1) so well short of any limit on OCPD disconnection.

But surely table 15.4 must be followed. And extension are tested as non fixed equipment, ie. separately to the installation.
 
But surely table 15.4 must be followed. And extension are tested as non fixed equipment, ie. separately to the installation.
Where is 'table 15.4' located?

Yes it is separate from the installation, but my point was more about what would you say is a safe maximum length. I only have a copy of the 5th edition ISITEE (ex-PAT) book and, while it has some recommendation on length, no hard limits.

We have all seen extension leads of 50m in use! So the point really is when testing such a lead, what is pass/fail? The ISITEE has flexible cable resistance value in Appendix 5 for the CPC so if you measure a lead and its end-end resistance is in keeping with the cable spec and overall length then it would look like a pass to me (i.e. "working as designed").

However, what is a reasonable limit on an extension lead length?

50m of 1.5mm has R1+R2 of 1.33 ohm (cold, from ISITEE table) and a 13A fuse as max Zs of 2.3 ohms, and with a typical socket outlet being of the order of 1 ohm Zs then that looks like the maximum length that is reasonable for such a lead before you are depending on RCD protection to disconnect.
 
I must admit I haven't got the 5th edition yet, I've only got the 4th. But I was thinking from the point of view of someone doing PAT testing - they will most likely have a big pile of things to test, and each one will be tested individually. They may not have any knowledge of the fixed wiring installation, or even any access to test it.

I take your points though.
 
My point goes back to the OP's belief the ISITEE has a definite limit and it is less then the 25m cables they had.

Also it would be rare today not to have RCD protection, either at the DB, at an RCD socket outlet (say on older properties for outside use), or if in any doubt a RCD plug-in adaptor.
 
Again I dont have a new copy of the CoP but I am certain those suggested lengths all equate to 0.18 ohm. I was actually doing some PAT last week on a site where the new workshop had rcd protected sockets but the old did not. They both had these long extension reels and we just recommend they only be used with rcd protection where the earth bond exceeded 0.18 ohm which invariably they do.
 
We have a rule of thumb that where the earth bond exceeds 0.18 ohm (I believe this equates to the suggested lengths in the CoP) that it is recommended it is only used with 30ma rcd protection
It is a little shorter, works out at 13.5m of 1.5mm flex, not allowing for plug/socket resistance (which ought to be very small).

5% VD at 13A would be 33m of 1.5mm flex, but I suspect it is rare that you would be using a lead at max current and in a situation where strictly meeting that matters.

TL;DR A 50m lead 0f 1.5mm is reasonable max for occasional/intermittent use, if it measures right, in my opinion.
 
Last edited:
Just found this Table and it shows both for different Classes so it is 13.3.
 
I think the text in the 4th edition could be clearer, mainly for when 'PAT testers' rather than electricians are doing the testing. We obviously have more knowledge than people who would often be doing the testing.

Be interesting to see how it is shown in the 5th edition when I get hold of it.
 
I think the text in the 4th edition could be clearer, mainly for when 'PAT testers' rather than electricians are doing the testing. We obviously have more knowledge than people who would often be doing the testing.
It is an issue for pass/fail equipment intended for relatively unskilled use, and even for the devices that give you an earth bond reading it is not always made clear how to decide if it is a fail (for short cable, as high R must be dodgy connection) or a pass (for extension lead of a given length).

Or indeed what sort of a length actually is reasonable!

Be interesting to see how it is shown in the 5th edition when I get hold of it.
Be prepared for disappointment!
 
If you limit the length of extension cables, all you're going to get is multiple extension leads daisy chained together.

Very true. But someone who is PAT/ISITEE testing should be using the code of practice. What someone decides to do with the equipment after that is not their concern.
 
The object of the exercise should be safety. A 100m extension lead is far safer than four 25m ones, which will have three plug and socket joints lying around in random places, getting wet, getting crushed or forming trip hazards.
 
The object of the exercise should be safety. A 100m extension lead is far safer than four 25m ones, which will have three plug and socket joints lying around in random places, getting wet, getting crushed or forming trip hazards.

I agree with that. But if you picture the poor guy you often see with a huge pile of cables and equipment in front of him, all he can do is test things as one-off items. He may well have no visibility of where they will be used.
 
Very true. But someone who is PAT/ISITEE testing should be using the code of practice.
But is it up to PAT/ISITEE testing to determine if a commercial product, like a 100m lead, is safe or not by design?

Of course they should check it is physically in good condition, and that the cable resistance matches expectations, and the manufacturer's recommended fuse size is fitted.
 
I'm not blaming the guy doing the testing, I'm blaming the ivory tower enclosed muppets that draw up ill thought out legislation.
If a worker needs power 100m away from the nearest power outlet, then he's going to do whatever it takes to get the power there. Those drawing up the legislation should be aware of this and legislate accordingly.
 
I'm not blaming the guy doing the testing, I'm blaming the ivory tower enclosed muppets that draw up ill thought out legislation.
If a worker needs power 100m away from the nearest power outlet, then he's going to do whatever it takes to get the power there. Those drawing up the legislation should be aware of this and legislate accordingly.
Thought Murdoch was back then???
 

Reply to Cable reels pat testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
714
Hi, I perform annual PAT checks for my company (office and workshop). The Apollo 400 machine we use has recently gone for calibration and service...
Replies
7
Views
925
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
310

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock