Hi All,

Just after some advice, I have been to a customer today and they are having there house renovated. There meter is getting moved to a external box due to floor plans changing, I am planning on running a 3 core 25mm SWA cable to the new consumer unit which is roughly 6 meters from the meter. My question is would I have to chase the cable into the kitchen floor or could I cleat it low level as the kitchen units will be fitted above the cable all the way to the consumer unit. Any opinions would be appreciated.

Jim
 
Nothing wrong with cleating it. But explain to the Customer what you are doing and inform them that should they ever change the layout of the kitchen this needs to be taken into account.

Burying the cable wouldn't be a problem neither as long as you connect the SWA to the MET as you then wouldn't need to install it on a RCD/ RCBO.
 
What are you expecting the max demand to be? If you have a 100amp bomb I would install and 80a isolator to provide some discrimination between the fuses. And go for 16mm 3 core.
 
.....once buried you would struggle with safe zones.

didnt realise the safe zones extended to the floor ???

;-)

Indeed they do not, which is why i suggest cleat direct. Even though the swa is suitable to buried outside of safe zones, in my opinion it is still dodgy when presented with a Paslode. In this instance where the option exists to go direct it makes most sense to me
 
Indeed they do not, which is why i suggest cleat direct. Even though the swa is suitable to buried outside of safe zones, in my opinion it is still dodgy when presented with a Paslode. In this instance where the option exists to go direct it makes most sense to me

I see what you're saying but safe zones don't come into it at all in this case - it would be in the floor!
 
Cleating to the wall is fine. Just be aware that most "built-in" appliances go hard up against the wall with a recess at the base for power/water. If there's a ruddy great cable in the way, the appliances will stick out proud of the units.
 
Could you not run 25mm tails and 16mm earth in YT4 trunking Just thought it may be easier than making off a 3 core 25 mm SWA into the CU will the earth bar take a 25mm cable ?
 
Indeed they do not, which is why i suggest cleat direct. Even though the swa is suitable to buried outside of safe zones, in my opinion it is still dodgy when presented with a Paslode. In this instance where the option exists to go direct it makes most sense to me

I see what you're saying but safe zones don't come into it at all in this case - it would be in the floor!


Haha i clearly didnt register that information, ,aking my point moot. My apologies
 

Reply to Cable run to new consumer unit in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
739
hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Replies
2
Views
246
Hi, Hoping someone can clarify for me. I've recently moved into a rental property, the landlord had new electric radiators installed and a new...
Replies
3
Views
551
Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
899
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock