Discuss Cable size in the UK Electrical Forum area at ElectriciansForums.net

Why would they have ID'd two of the cables as silver right at the point where the SWA cores join onto the tails? its obviously covering over a through crimp on what looks like 2 different sized cables

Doh. That'll teach me to look properly. Apologies. Daz
 
i might be looking at this wrong but looking at amendment 2 i thought the reason a evcp should not be connected to a pme system was to prevent back feed from the battery if a fault occurred.

722.1
(ii) protection for safety when feeding back electricity from an electric vehicle into a private or public supply network

and says
722.312.2.1
for tn systems the final circuit supplying a charging point for electric vehicles shall not include a pen conductor

so would it not be easier to use 3 core swa, amour earthed at db but not at evcp and use a tt system for the charging point than trying to meet 722.411.4.1 (i) or (ii) or (iii)
 
Well I called the NICEIC today and they said do not put an earth rod in and just take the SWA out the building and make it part of the TN-C-S installation.

I explained everything in full and explained the proximity to the building etc and that the building it metal and so on.

They even emailed me to confirm as I asked them, they said its fine, they said that in reality its never ever going to be a problem.
 
so god has spoken, but god is not legally liable if the sh!t hits the fan. good old nicyuk
 
i might be looking at this wrong but looking at amendment 2 i thought the reason a evcp should not be connected to a pme system was to prevent back feed from the battery if a fault occurred.

722.1
(ii) protection for safety when feeding back electricity from an electric vehicle into a private or public supply network

and says
722.312.2.1
for tn systems the final circuit supplying a charging point for electric vehicles shall not include a pen conductor

so would it not be easier to use 3 core swa, amour earthed at db but not at evcp and use a tt system for the charging point than trying to meet 722.411.4.1 (i) or (ii) or (iii)

722.312.2.1 is irrelevant as the final circuit won't include a PEN conductor
 
Probably they are thinking on the lines of Archy's suggestion, if the buildings phases are reasonably balanced, exemption i)

They said the three phase part for section (i) and also the fact that its a steel building with the steel bonded, he said thats more than likely better than any rod you will put in.
 
Well I called the NICEIC today and they said do not put an earth rod in and just take the SWA out the building and make it part of the TN-C-S installation.

I explained everything in full and explained the proximity to the building etc and that the building it metal and so on.

They even emailed me to confirm as I asked them, they said its fine, they said that in reality its never ever going to be a problem.

So, will the judge accept 'the NIC said it's ok' in preference to 'I followed bs7671 to the letter' ?
 
so would it not be easier to use 3 core swa, amour earthed at db but not at evcp and use a tt system for the charging point than trying to meet 722.411.4.1 (i) or (ii) or (iii)

The problem here was the proximity of the PME bonded metal clad building to the TTd ECV, you would be able to touch both Earthing systems simultaneously, which is a shock hazard due to true Earth of the TT part relative to the PME part which may not be at true earth potential at any given time.
 
They said the three phase part for section (i) and also the fact that its a steel building with the steel bonded, he said thats more than likely better than any rod you will put in.

More than likely better? That's a very precise and technical response!

Once you've tested the effectiveness of the steel structure as an earth then you will be better informed about this. Then with test results to prove it you could make the informed decision that this is safe to do.
 
More than likely better? That's a very precise and technical response!

Once you've tested the effectiveness of the steel structure as an earth then you will be better informed about this. Then with test results to prove it you could make the informed decision that this is safe to do.

What would the best bethod be to achieve this on this type of buliding?
 
First off I would be looking at the formula in the annexe associated with exemption i), then clamping the individual tails to see how balanced the building actually is when it is normally loaded, and adding up any further loads from the DB to see if it is possible to severely unbalance it, this would be my starting point.

I hinted at this last night when I said "Archies suggestion is looking better by the minute" ;)
 
First off I would be looking at the formula in the annexe associated with exemption i), then clamping the individual tails to see how balanced the building actually is when it is normally loaded, and adding up any further loads from the DB to see if it is possible to severely unbalance it, this would be my starting point.

I hinted at this last night when I said "Archies suggestion is looking better by the minute" ;)

He's adding a 60A single phase load to the system, so unless the system is 60A out of balance then the system will be thrown out of balance when the charger is in use.

Clamping it will only give a brief snapshot of the loading, a couple of weeks load study would really be needed to establish a proper idea of what the loading is like.
 
He's adding a 60A single phase load to the system, so unless the system is 60A out of balance then the system will be thrown out of balance when the charger is in use.

Clamping it will only give a brief snapshot of the loading, a couple of weeks load study would really be needed to establish a proper idea of what the loading is like.

I thought he was fitting a 3 phase charger ?

Agree that longer term monitoring would be a better bet, but if it is outside of the parameters of exemption I) to begin with then he is going to have to load balance it better to start with no?
 
Yes they have two cars already that both draw 16A so that's 32A straight off.

I think without looking at my notes it was 8A on L1, about 30A on L2 and 8A on L3

I am going to put this on L1.

Im not being funny but nobody is ever going to monitor this for even a day let alone two weeks.
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
327
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
744
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock