I assume you are doubling Column 6 from Table 4D4A to get 92A, problem is it ain't a 2 core cable?
Yes I was doubling the tabulated CCC as recommended when using cables in parallel, however the regulations are thinking of two separate two core cables suitably arranged to ensure equal current sharing, which may well not be the case here, I agree.
However this is moot since the VD is something in the region of 50V!
 
Yes I was doubling the tabulated CCC as recommended when using cables in parallel, however the regulations are thinking of two separate two core cables suitably arranged to ensure equal current sharing, which may well not be the case here, I agree.
However this is moot since the VD is something in the region of 50V!
Not calculated the volt drop but under maximum loading I don't doubt it will exceed requirements.
 
OP: Email the concerns you have to the customer. That was you have proof that you have warned him about all the things. Just to CYA.
 
My view that cable if PVC insulated will be rated at 76A, if XLPE then 88A.

This is such a common mistake I see, you may well know this so it could just be for the benefit of others.

XLPE only has a higher current rating if everything it's connected to is also rated to operate at 90 deg C. If it isn't it's CCC is reduced to that of a PVC cable.
 
This is such a common mistake I see, you may well know this so it could just be for the benefit of others.

XLPE only has a higher current rating if everything it's connected to is also rated to operate at 90 deg C. If it isn't it's CCC is reduced to that of a PVC cable.

Reg 512.1.5 (Page 117) for reference to whoever wants to look it up.
 
This is such a common mistake I see, you may well know this so it could just be for the benefit of others.

XLPE only has a higher current rating if everything it's connected to is also rated to operate at 90 deg C. If it isn't it's CCC is reduced to that of a PVC cable.
Yeah know this, that however is the maximum rating of the cable where conditions satisfy.
 
In this case it clearly doesn't matter one jot what the CCC is, because at 300m the voltage drop limits you to about 6-7A as per RB above and the OP's observations.

If it were on my own turf, I would look at some kind of fun scheme like launching two phases into the two paralleled cores and transforming down 400 to 230 at the far end, which would give you three times the current for the same drop (before correcting for transformer regulation and loss which would undo some of the benefit) With 600/1000V cable and a tranny each end one could theoretically get about 29A through it at 3% drop and deliver over 100A at 230V at the far end, however the cost of buying and installing the transformers and the lifetime cost of their loss would probably exceed the cost of relaying in suitably sized cable.
 

Reply to Cables In Parallel, Max Load? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
What can be worse than electrical installations on a farm, or in a pub?...... Chippys! Got a phone call from my local.... Lights and kitchen...
Replies
6
Views
830
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
457
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock