Discuss Calculate the appropriate size of the protective conductor exam question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Reaction score
3
fault = 400 A
Operating time of protective conductor = 0.15 s
Constant k, for the material of the conductor = 134

a 1.5mm
b 2.5mm
c 4.0mm
d 6.0mm

Just want to make sure I've got this right,
 
These are often difficult questions, because although your calculation is correct - leading to the answer 1.5mm^2 there are sometimes related regulations.

So if the question relates to final circuits etc (I.e. twin & earth or whatever), this would be correct.

However, if the question relates to other areas, there are minimum conductor sizes - depending upon if the conductor is protected or not.

On face value, I would assume 1.5mm^2

Examiners tend to have a specific situation in mind when they write questions, which often isn't clearly presented
 
These are often difficult questions, because although your calculation is correct - leading to the answer 1.5mm^2 there are sometimes related regulations.

So if the question relates to final circuits etc (I.e. twin & earth or whatever), this would be correct.

However, if the question relates to other areas, there are minimum conductor sizes - depending upon if the conductor is protected or not.

On face value, I would assume 1.5mm^2

Examiners tend to have a specific situation in mind when they write questions, which often isn't clearly presented
Thank you so much for your help 👍🏻 much appreciated 🙂
These are often difficult questions, because although your calculation is correct - leading to the answer 1.5mm^2 there are sometimes related regulations.

So if the question relates to final circuits etc (I.e. twin & earth or whatever), this would be correct.

However, if the question relates to other areas, there are minimum conductor sizes - depending upon if the conductor is protected or not.

On face value, I would assume 1.5mm^2

Examiners tend to have a specific situation in mind when they write questions, which often isn't clearly presented
thank you so much for your help, much appreciated 👍🏻🙂
 

Reply to Calculate the appropriate size of the protective conductor exam question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
529
Hello, I took the opportunity over the lockdown to do 18th Ed course but theres a few bits im struggling with. Because its distance learning, the...
Replies
5
Views
1K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Afternoon all, How do i solve these two questions, Feel like am missing something simple. doing my head in lol. I need to learn the calculation...
Replies
24
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock