DT1991

-
Reaction score
166
Can anyone assist me in finding out if all cables involved with a fire alarm system must be FP or similar.

By fire alarm I mean sounders, call points, door holders etc.

Thanks.
 
I would like to further my knowledge.

If its existing can detectors/Sounders be wired in T&E.

And I'm guessing all new must be FP or similar.

Edit by existing I mean before a certain year. Obviously not installed yesterday
 
Last edited:
years ago, T/E was allowed for dire alarm detectors as long as they were EOL monitored. that.s 25 years ago though. all now in FP or MICC,some specs even call for the super FP , called enhanced or summat. thank the devil i use wireless detectors.
 
Not an expert on fire but I would think any work your doing needs to be FP or pyro and if the existing wiring is T+E then record it and make recommendations to the customer in writing.
 
years ago, T/E was allowed for dire alarm detectors as long as they were EOL monitored. that.s 25 years ago though. all now in FP or MICC,some specs even call for the super FP , called enhanced or summat. thank the devil i use wireless detectors.
I remember doing fire alarms in 2/3 story communal areas with detectors & call point wired in T&E and the bell circuits in FP.
 
Yes that was the old standards whereby the sounder circuits were deemed most critical you could actually get red T&E.
 

Reply to Can anyone help with a fire alarm query. in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi all, i'm just after a definitive answer regarding a fire alarm system in a communal area/stairwell. There are call points, smoke heads &...
Replies
4
Views
610
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
596
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
317
Anyone ever took part in any of the virtual classroom training sold by the NICEIC? Interested in learning more about fire alarm systems and...
Replies
5
Views
1K
Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
703

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock