- Reaction score
- 5
This can have several interpretations.
1. Break trip rating cant be above 145% of the ampacity rating of the wire? That doesnt make sense because the breaker should be protecting the wire by tripping first.
2. Load cant exceed 145% the ampacity rating of the wire? Load should be less than the ampacity of the wire.
3. If a 32 amp breaker feeds a 4mm circuit, no hot or neutral wires on the circuit shall have ampacity less than 1/1.45 = 72.5% of 32 amps. Not even on un-fused spurs.
4. Can someone please explain? TIA !
1. Break trip rating cant be above 145% of the ampacity rating of the wire? That doesnt make sense because the breaker should be protecting the wire by tripping first.
2. Load cant exceed 145% the ampacity rating of the wire? Load should be less than the ampacity of the wire.
3. If a 32 amp breaker feeds a 4mm circuit, no hot or neutral wires on the circuit shall have ampacity less than 1/1.45 = 72.5% of 32 amps. Not even on un-fused spurs.
4. Can someone please explain? TIA !