Hi guys

Did an EICR last week in a council house and the occupant has complained to the council that during my testing I've damaged her TV! I did an insulation resistance test with line and neutral linked together, to earth. I normally do it at 250V then, if the reading is healthy, at 500V which I did in this case and recorded 140MegOhms. Also i usually switch off the sockets without unplugging the accessories but I can't actually remember switching the TV socket off on this occasion so it may have been in the on position. So is it possible to damage a TV at 500V with L+N together? I didn't test line to neutral seperately.

I went back and just checked the plug top and cordset and they are fine so maybe its an internal fuse that has operated. It's an LG LED TV and it's completely dead. Penny for your thoughts?

Thanks in advance

J.O.B.
 
Can you remember if it was the same TV that was there last week?

Need to make sure these people have not swapped it for another.

Its a bit strange as linking L and N is supposed to stop that from happening. I am glad I am paranoid and always unplug everything.
 
Last edited by a moderator:
seen this before years ago company replaced a load of plasma tv,s before I stopped it, same tv being passed around different houses.Boss just gave them a new tv and didn,t take old one which got passed on to next person.Stopped when I took the broken tv away.
 
After one decent homes rewire, Jabba The Hutt who inhabited the hovel (sorry I meant house, my fingers slipped) got in touch with tenant liaison and told them the night after we had finished there was a surge which damaged beyond repair her brand new (yeah right) fridge freezer (lots of other appliances were plugged in at the time but only this was damaged...hmmmm)
Furthermore she mentioned me by name and claimed that I had been round that morning and acknowledged that it had happened AND that it was my fault. After tenant liaison helped me recover from my laughing fit they rejected the claim only to receive a letter from a solicitor which stated something along the lines of "The new electricity I had installed was faulty"
Yeah the new electricity isn't a patch on the old stuff!
Chancers mate, the world is riddled with them. Tell them to prove it.
 
Last edited by a moderator:
IT equipment does have an earth rail which can still damage componants, hence why pc's must be disconnected from circuits being IR'd.
I know most tv's used to be double insulated class2 but more and more do now seem to have an earth so iv'e noticed, so could be the case here. Bit of luck it is just a fast blow fuse on it but i would not want to play with it if in your shoes.
If it has damaged it were only talking a tv so not the end of the world, if it was me just pay a £60 tv man callout and if it has gone pop stick it on the insurance or pay a new one, sounds like a coucil contract you have so not worth losing it over a tv, accidents happen so don't let it eat you up.
 
Funny how it always happens in Rented houses, I had it once on a test where I heard this noise and the bloke came in and said his computers just 'blown up' and must of been something you were doing. I said thats funny mate as I was just filling out paperwork! He then got really angry with me and I said 'numbers on the back of the van mate'
 
IT equipment does have an earth rail which can still damage componants, hence why pc's must be disconnected from circuits being IR'd.
I know most tv's used to be double insulated class2 but more and more do now seem to have an earth so iv'e noticed, so could be the case here. Bit of luck it is just a fast blow fuse on it but i would not want to play with it if in your shoes.
If it has damaged it were only talking a tv so not the end of the world, if it was me just pay a £60 tv man callout and if it has gone pop stick it on the insurance or pay a new one, sounds like a coucil contract you have so not worth losing it over a tv, accidents happen so don't let it eat you up.
Disagree strongly, if he accepts liability on this one word will spread like wildfire and if he goes back to that estate for any more testing there will be an avalanche of claims from the less than scrupulous. His premiums will rise exponentially
Stand your ground on this one mate
 
End of the day there's no way you blew the TV up because you ALWAYS unplug every appliance before doing any testing because otherwise you could get a wrong test result....

That's what you ALWAYS do without question....

I'm right aint i?




Just *nod* yes and stick with it....you know it's the right thing to do *nods slowly*
 
If you're IR testing with L+N to Earth @500V the only way that might cause a problem would be if there was an N-E reversal somewhere on a circuit.
However he has proven that there wasn't by following the full and correct method for testing an RFC
Nudge nudge wink wink
 
Disagree strongly, if he accepts liability on this one word will spread like wildfire and if he goes back to that estate for any more testing there will be an avalanche of claims from the less than scrupulous. His premiums will rise exponentially
Stand your ground on this one mate

Quite right. Linking Line and Neutral keeps everything at same potential but seeing as "it was unplugged" there was no chance of it blowing. We had council rewire and the tenant wanted us to move a socket - next it came the redecoration because of the mess and holes left - we made the mistake of offering a small fee, not for the damage but for the delay in repositioning the socket. Two weeks later it was her neighbour wanted a socket repositioned after the rewire. We refused because she marked the positions. Next she said she wanted new carpets due to the mess. We refused as we didn't use paint or nail varnish!! SEVEN months later a solicitors letter saying we hit a gas pipe and she was overcome with fumes for seven months.

Our insurance company investigated and discovered the gas fitter who gave her the report was her brother. TV always show cowboy builders but don't mention tenants from hell
 
Had something similar before, but with my mother in laws £8000 canvas printer...safe to say I lost a bit of sleep over that one!! luckily it was the fact I had forgotten to switch it back on that threw her!
 
I'm pretty sure you unplugged the TV... (your pretty sure he unplugged the tv?.....I KNOW THAT HE UNPLUGGED THE TV BECAUSE HE TOLD ME IN THE PUB THAT NIGHT!).
 
No way Jose!!

The TV will be a class II device with no earth conductor. If you get a chance to, check that - I am 98% certain you will find the plug has a plastic earth pin. Therefore, IR testing cannot have damaged it.

If you get to see the TV again, take a picture of the label with the serial number on your phone.

If you know the model, download the instructions from the manufacturers site to see if it says it is class II. BTW, my lads both have LG TVs of differing models, both are class II, as is my Panasonic plasma.
 
joking aside.....jimmy_one_ball you said that you normally switch off at the sockets but leave the appliances still plugged in?. i dont know if somebody can correct me if i am wrong but if the sockets are single pole and not double pole types would the I/R test voltage not travel through the neutral into the appliance connected (unless polarity reversed!) even if the switch was off and the appliance was still plugged in?
 
joking aside.....jimmy_one_ball you said that you normally switch off at the sockets but leave the appliances still plugged in?. i dont know if somebody can correct me if i am wrong but if the sockets are single pole and not double pole types would the I/R test voltage not travel through the neutral into the appliance connected (unless polarity reversed!) even if the switch was off and the appliance was still plugged in?
Yep, Always unplug for an RFC.
 

Reply to Can EICR damage TV? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
657
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
747
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock