Discuss Can I replace 3-way toggles with 3-way motion switches? in the DIY Electrical Advice area at ElectriciansForums.net

Grigate

DIY
Reaction score
1
Hi, I have two 3-way toggle switches by the opposite sides in my garage. Is it possible to replace both of them with motion sensors?
Thank you.
.grig
 
It probably is, however it would be best to get an electrician in to quote as it may be that they can reorganise the existing wiring to do it without adding any new cables and therefore you wont have to redecorate.
 
You no longer need a traditional 'two-way' (uk term) or 'three-way' (usa term) type wiring arrangement when using motion sensors.
You can wire two motion sensors in parallel (eg ones with relay contacts to do the switching) to the one light, to get the equivalent effect - you move within range of the sensor, the light goes on, you move away, it goes off. You don't need the 'other' sensor to do the turning off!

But you might consider whether this arrangement will actually work for you, having the light entirely controlled by motion. In my experience with simple sensors, when you stand still a while (or move out of range) the light eventually goes out, so doing any work in the garage at night might become a challenge!
 
You no longer need a traditional 'two-way' (uk term) or 'three-way' (usa term) type wiring arrangement when using motion sensors.
You can wire two motion sensors in parallel (eg ones with relay contacts to do the switching) to the one light, to get the equivalent effect - you move within range of the sensor, the light goes on, you move away, it goes off. You don't need the 'other' sensor to do the turning off!

But you might consider whether this arrangement will actually work for you, having the light entirely controlled by motion. In my experience with simple sensors, when you stand still a while (or move out of range) the light eventually goes out, so doing any work in the garage at night might become a challenge!
I probably did not explain my issue correctly. As I mentioned, I have two doors on the opposite sides of the garage. If I enter a door without a sensor with a vehicle parked inside, I will not be able to trigger the sensor at the other door (the vehicle will block it).
If you know a solution, can you provide an electrical diagram?
Thank you
.grig
 
I probably did not explain my issue correctly. As I mentioned, I have two doors on the opposite sides of the garage. If I enter a door without a sensor with a vehicle parked inside, I will not be able to trigger the sensor at the other door (the vehicle will block it).
If you know a solution, can you provide an electrical diagram?
Thank you
.grig
I should have prefaced my initial response by saying "yes" to your question!
My suggestion was to have two sensors on opposite sides of the garage (eg in the vicinity of the present switches and using their wiring) connected in parallel to the light you have. Whichever entrance you go in will trigger the sensor near that door and turn the light on, so I thought that would do what you required, if not then I haven't understood correctly.

There was a thread here on a slightly different issue, but it contains the basic circuit you would need (ignore the labels on the diagram - each switch represents each sensor: , ie the switched output of each goes to the light.

You should be able to work out how to connect the sensors from the principle illustrated in the above link, otherwise I suggest you get an electrician involved,
 
Last edited:
My suggestion was to have two sensors on opposite sides of the garage (eg in the vicinity of the present switches and using their wiring) connected in parallel to the light you have. Whichever entrance you go in will trigger the sensor near that door and turn the light on, so I thought that would do what you required, if not then I haven't understood correctly.

There was a thread here on a slightly different issue, but it contains the basic circuit you would need (ignore the labels on the diagram - each switch represents each sensor: , ie the switched output of each goes to the light.

You should be able to work out how to connect the sensors from the principle illustrated in the above link, otherwise I suggest you get an electrician involved,
You did understand my question correctly, it's I, who did not understand your answer, sorry. (I just have two 3-way motion sensors and wanted to use them so they don't go to waste.)
Thank you
.grig
 
You did understand my question correctly, it's I, who did not understand your answer, sorry. (I just have two 3-way motion sensors and wanted to use them so they don't go to waste.)
Thank you
.grig
I think you should be able to use those sensors you have. Good luck with the project.
 
Hi, I have two 3-way toggle switches by the opposite sides in my garage. Is it possible to replace both of them with motion sensors?
Thank you.
.grig
As long as you have a neutral in each switch box than sure and good luck. Welcome to the forum
 

Reply to Can I replace 3-way toggles with 3-way motion switches? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
454
Trying to install a Lutron Toggle/Dimmer (TGCL-153PR) Confused, as the current switch has 3 wires gong to it Black, White, and Red (there is also...
Replies
1
Views
674
Is the following set up possible with a 3 Gang 2 Way Smart Wifi Switch set up (the black glass type touch ones) One of the 3 switches, switches...
Replies
2
Views
542
Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
428
My 4 year old son won't go to bed without the light being left on and insists his door is closed when I leave. When the door is opened later to...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock