Discuss Can Someone Help? Melted Plug? in the Electrical Appliances Forum area at ElectriciansForums.net

Just re-reading th OP's post and .

That suggests to me we're not talking about a hand held hair dryer. It could be anything from a tumble-dryer through sit under hair dryer, to a seed dryer on a farm. I also wonder if the "dryer" came with a plug originally?

So, Fiona, what sort of equipment are we talking about here?

Do keep up, I asked that question 2 hours ago....... :lol:
 
Technically you slyed it in on the end of a post.
If this is a tumble dryer why was everyone talking about how much hair Tel has got?

because it was a good excuse to have a pop at me. just because i'm getting on a bit, don't mean i go to the barbers for a wax and polish.
 
would probably install a new socket and also have the wiring to the socket that was used checked out, the wiring going to that might be too thin for the load that was on it (about 11A continuous) and the current might have heated the wall socket innards and the plug pins up.....in turn heating the plug to the point of melting...this load would likely have been on for long durations, 1 or even 2 hours at a time....

The wiring going into the wall socket plate from behind might well be heat damaged as well, if you prefer you could just avoid using that socket until after the new year when you can get it sorted out...

can you dry things on radiators or a clothes horse for the next 2 weeks or so until you can get somebody to have a look? I think this would be better than melting electrical connections....
 
Would I pee people off if I took the conversation back to electrics?!

The this drier is knackered and drawing a high enough load (repeatedly) to melt a plug top and socket, then the 13A fuse clearly isn't there or isn't doing it's job.

As the OP has said, she has replaced the extension which rules out the plug top being at fault. She's also used an alternative socket, so that rules out a loose connection in the outlet.

My money would be on a faulty drier, drawing too much current so repeatedly popping the fuse, so someone has stuck an old nail and wrap of foil in the drier plug...

Does the driers own cable get hot?
 
Would I pee people off if I took the conversation back to electrics?!

The this drier is knackered and drawing a high enough load (repeatedly) to melt a plug top and socket, then the 13A fuse clearly isn't there or isn't doing it's job.

As the OP has said, she has replaced the extension which rules out the plug top being at fault. She's also used an alternative socket, so that rules out a loose connection in the outlet.

My money would be on a faulty drier, drawing too much current so repeatedly popping the fuse, so someone has stuck an old nail and wrap of foil in the drier plug...

Does the driers own cable get hot?

Makes sense but has gone through 2 extension leads, both of which would have fused plugs. so even if the dryer fuse was a nail they should have protected the plug/socket.

It really needs a spark to have a proper look at it......
 
Makes sense but has gone through 2 extension leads, both of which would have fused plugs. so even if the dryer fuse was a nail they should have protected the plug/socket.

Ah, that's a very good point...

*removes stupid hat*

That's a really odd one actually...

The MCB/fuse should be protecting the socket and isn't. But even if that's not working then the plug top fuse on the drier or extension should be popping, but isn't.

Usually down to a loose connection in the socket but clearly not in this case (unless of course the connections were loose in BOTH sockets the OP tried!)
 
of course it could also be that the person who wired the ring didn't do any of the terminal screws up properly. I've seen it before...........
 
Sorry for the delay in replying :)

Firstly, yes... sorry, a tumble dryer. Sited in the hall, where originally we had one of those wound extensions running into the kitchen under a door the we keep closed behind the dryer.... and into a socket in there - that socket was only installed maybe 3 years ago... with the new kitchen so shouldn't have been an issue. Though I see now that the wound extension may have been. Once that burned out, we bought a length of cord with a socket on one end and a plug on the other from an electrical shop and ran it down the hall to an older socket. This was the one that melted today. The plug from the dryer does get hot but it was the extension plug in both cases that melted.
Now.. one thing worth mentioning is that I moved the dryer to hoover yesterday and it may have been put back too close to the wall... possibly... I am not certain as hubby pulled it out when the plug got burned so not sure where it was :-\
 
Burnt plug top will ruin socket
Burnt socket pins will ruin plug top

Change all of them involved,check the wires at each item and try and avoid extra connections to the machine,eg extension leads
 
Sorry for the delay in replying :)

Firstly, yes... sorry, a tumble dryer. Sited in the hall, where originally we had one of those wound extensions running into the kitchen under a door the we keep closed behind the dryer.... and into a socket in there - that socket was only installed maybe 3 years ago... with the new kitchen so shouldn't have been an issue. Though I see now that the wound extension may have been. Once that burned out, we bought a length of cord with a socket on one end and a plug on the other from an electrical shop and ran it down the hall to an older socket. This was the one that melted today. The plug from the dryer does get hot but it was the extension plug in both cases that melted.
Now.. one thing worth mentioning is that I moved the dryer to hoover yesterday and it may have been put back too close to the wall... possibly... I am not certain as hubby pulled it out when the plug got burned so not sure where it was :-\
You may have noticed that your delay in responding has led to the conversation going somewhat off-topic, eg speculating as to how much hair our more elderly members have (or rather lack of).
A tumble dryer is one of the most current hungry appliances in a home so really needs it's own socket to be plugged directly into. Any wound extension which isn't fully unwound will use more power due to a phenomenon known as Lenz's law (basically the coils of wire form an electromagnet which fights against the current the appliance is trying to use) which would be more prevalent the higher the current consumption of the appliance. If you use a cheap extension lead the chances are it's only designed for lower current appliances such as lamps, mobile phone chargers, maybe computers etc. so may not be able to handle a tumble dryer being plugged into it and in the worst case scenario the fuse could blow or worse still melt.

My advice would be to get an electrician in to check the sockets where the overheating has occurred (including the cables supplying them) and install a new socket where you want the tumble dryer to go.

Fortunately for you there seem to be a lot of forum members around your area....
 
While your electrician is there you could get him/her to do an Insulation Resistance test on the extension leads you were using. I suspect they're what's we call "knackered" but stranger things have happened, like in 1542 when the mayor of Bavaria spontaneously combusted.
 
There's only actually three common points with this:

1) Machine itself / plug on it....... check plug is fitted properly and has correct fuse rating
2) Extension......check cable is rated for 13A, NOT a lightweight one, isn't on a drum/unwound
3) Socket outlet/s.....check terminations are tight.

There you go, and not a grey hair in sight. (Well, not me personally, I got loads of them thanks to three kids).
 

Reply to Can Someone Help? Melted Plug? in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Prima Tumble Dryer which I have had for 5 years. Just recently, the plug and socket melted. I replaced both and it melted again. I...
Replies
18
Views
3K
My tumble dryer broke, an electrician put a new and stronger capacitor in, couple months later I realised that the socket on the extension lead...
Replies
7
Views
3K
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
463
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
844
Good morning guys, I bought this neon sign for my cinema room to put above my arcade machines. I have the cinema controlled by Google voice...
Replies
1
Views
572

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock