Discuss Can SWA be run in the same metal trunking as singles? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
7
I have checked the regs and can't find anything to say this can't be done. Although I'm worried about cable movement in the case of short circuit damaging singles in the trunking
 
You are fine with that. Of course usual good installation practice needed, but SWA won't move that much unless you are looking at really high energy faults, and more so for sets of AWA singles making up a really high current 3P set.
 
do you mean complete SWA? with the armour? or glanded into the trunking, and the inner cores within trunking?


"Singles" cable has a slightly tougher insulation than something like the inner basic insulation of t&e... Can take a bit of rough treatment no problem.
 
do you mean complete SWA? with the armour? or glanded into the trunking, and the inner cores within trunking?


"Singles" cable has a slightly tougher insulation than something like the inner basic insulation of t&e... Can take a bit of rough treatment no problem.
Yes, complete SWA. We have installed trunking for an installation with 2.5mm, 4mm and 6 mm singles.

We've now been asked to run a 10mm swa for a supply to a new dB and a lot of the trunking is along this route.
 
You are fine with that. Of course usual good installation practice needed, but SWA won't move that much unless you are looking at really high energy faults, and more so for sets of AWA singles making up a really high current 3P set.
Thanks for the reply, the fault current will be 10Ka (theoretical maximum at origin) for the swa as we are right by the site intake.

We have at a maximum 10 single conductors (2.5, 4 and 6mm) at the busiest points in the trunking. All single phase including SWA. I suggested it to the clerk of works and he said absolutely not allowed.

I disagreed and have since been searching high and low for a regulation that prohibits this.
 
Possible future plans require the space in the trunking?

Whats wrong with running the SWA alongside the trunking? Its mechanically protected already. Or, as i said earlier, gland it in and run it through without the armour.
 
Possible future plans require the space in the trunking?

Whats wrong with running the SWA alongside the trunking? Its mechanically protected already. Or, as i said earlier, gland it in and run it through without the armour.
For some reason he doesn't like it clipped direct. Unfortunately it's at the beginning of a 70m run so glanding into trunk is not an option. Clerk also refuses to allow us to clip direct.

I was only really looking for 2nd opinions on this matter as he has highlighted my suggestion to run in the trunking to the client and has questioned my competency
 
Clerk of works will have the final say. I wouldn't waste time arguing with him and would instead ask how he'd like it to be routed - limitations with regard to support might actually result in him having a change of mind. Do whatever he wants and invoice accordingly.
He has refused to make suggestions on how to actually do it as he states 'that's not his job'.

I wanted to triple check that this is in fact acceptable as he has reported my suggestion to his superiors.

Thank you for taking the time to reply!
 
Just one other thought, how would the SWA armour be connected?
I can see both sides of this, whilst I also cannot see a reason why it is Non compliant, it will take up more room in the trunking than the equivalent in singles?!
Personally I would if in trunking be using singles for ease and space saving.
When they ask you back again at a later date to install more circuits you will either be wishing for more space or thinking, glad I left some spare capacity in that trunking!
Just my 2pennies worth.
Sy
 
He has refused to make suggestions on how to actually do it as he states 'that's not his job'.

You've suggested two methods of installation which he has rejected and neither for any regulatory reason and this is something I'd make very clear to him - I'd contend that it's very much his job to decide how the cable is run, unless the client provides a spec.
 
If I had more than one run of SWA I would be tempted to put up cable tray and clip to that. If the tray is vertical (parallel to wall, supported off by short lengths of strut, for example) then you need the occasional metal tie for fire support in addition to regular ties of any other sort.

If the SWA sits on top of a horizontal tray (so it can't fall if clips melt), for example supported on cantilever arms, or suspended from a roof, then standard cable ties are OK. Personally I would always use the black UV-tolerant type even indoors as sometimes it will get sunlight from windows, etc, and it saves me keeping multiple bags.

However, I also get the feeling this person is being difficult for no obvious reason. I would be tempted to present your suggestions for alternatives in writing (e.g. email) and make sure they respond also in writing just to cover yourself.

Incidentally, when you said trunking I was thinking of the metal stuff, 50x50mm upwards, not plastic. Can you confirm the type?
 
If I had more than one run of SWA I would be tempted to put up cable tray and clip to that. If the tray is vertical (parallel to wall, supported off by short lengths of strut, for example) then you need the occasional metal tie for fire support in addition to regular ties of any other sort.

If the SWA sits on top of a horizontal tray (so it can't fall if clips melt), for example supported on cantilever arms, or suspended from a roof, then standard cable ties are OK. Personally I would always use the black UV-tolerant type even indoors as sometimes it will get sunlight from windows, etc, and it saves me keeping multiple bags.

However, I also get the feeling this person is being difficult for no obvious reason. I would be tempted to present your suggestions for alternatives in writing (e.g. email) and make sure they respond also in writing just to cover yourself.

Incidentally, when you said trunking I was thinking of the metal stuff, 50x50mm upwards, not plastic. Can you confirm the type?
100x100 metal trunking, only 1 SWA to run. After SWA goes in with the other circuits.we are at approx 10% capacity
 
You’re still going to have to gland the swa into the trunking somehow, even leaving armour on.

I have to agree that there is no valid reason that it can’t be clipped surface. It’s perfectly ok in every other building.
 
You’re still going to have to gland the swa into the trunking somehow, even leaving armour on.

I have to agree that there is no valid reason that it can’t be clipped surface. It’s perfectly ok in every other building.
The beginning of the swa run is internal (where the trunking is), then runs externally to an outbuilding to upgrade a feed there.

There seems to be no logical reason to a lot of his requests
 
Just one other thought, how would the SWA armour be connected?
I can see both sides of this, whilst I also cannot see a reason why it is Non compliant, it will take up more room in the trunking than the equivalent in singles?!
Personally I would if in trunking be using singles for ease and space saving.
When they ask you back again at a later date to install more circuits you will either be wishing for more space or thinking, glad I left some spare capacity in that trunking!
Just my 2pennies worth.
Sy
Entry and exit to trunking will be 32mm metal compression gland, there is then a 30m run beyond trunking to the next dB that the swa continues to.

100x100 trunking with, at a maximum, 10 singles conductors (2.5, 4 and 6mm) so trunking will be approx 10% capacity with SWA installed
 

Reply to Can SWA be run in the same metal trunking as singles? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Is anyone aware of any galv trunking that is smaller than 50x50. I'm drawing a blank online. I've taken over a job that's used 16mm twin and earth...
Replies
12
Views
796
I was working with some odd singles today from Batt Cables, they seemed to have a plastic like braid between the insulation and the copper, almost...
Replies
11
Views
540
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
553
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
755
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
854

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock