Discuss Can't confirm bonds in hotel complex - what should i do? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

Matt_M

Good afternoon everybody,

I have recently installed an Electric Vehicle charging station at a hotel complex and couldn't verify earthing arrangements on the site.

The circuit I installed was a 32A radial with a Zs value of 0.24ohms, fed from a db with a Zsdb of 0.16ohms so nothing to worry about there.

The site has it's own 20,000V transformer to which I gained access, however the supply cut out was concealed in its own cabinet which has a padlock protecting the main switch and it looks as though the MET was contained inside it. In order to gain access to the MET I would have had to shut down power to the entire site (which was not going to happen). There were no obvious earth cables entering the supply kiosk (they must all run underground).

The site itself is huge and I have never been there before, the site maintenance man was useless so I couldn't find the sites incoming Gas or Water (or bonds).

How should i certify this?

Many thanks in advance.

Matt
 
injform the hotel management that you can't issue a certificate until they grant you access. it's their problem if they need to kill the power.get 'em to do a fire drill, then when everone is out, switch off the supply. :smilielol5:
 
you could run new bonds to as near as you can get to the intake of the service pipes. but, did you not say that you could not access the MET? i would make it clear on your cert that you were unable to access MET and therefore further investigation is required to ensure that the installation is safe.
 
Can't see the problem myself actually in this case, you did your job right, the readings are fine and the circuit cabling and protection fine, what I would do is certify your works and staple a note to the certificate saying due to access you couldn't confirm bonding and you recommend they have this confirmed ASAP by an approved contractor to satisfy any problems which may relate to insurance claims should there be any incidents in the future. Your covered, they have the ownus on them, look, lets imagine then being asked by lets say london childrens hospital to install a double socket in a corridor for a cleaner, you have no access to any wards or areas due to security except the one where the socket is, now do you refuse to do the job unless you can confirm bonding to gas and water and structured steel and lightning conductor etc????, I think not, get the certificate out with the note and don't worry about it.
 
Good answer MDJ !

Running new bonds would be a significant job due to the size of the incomer (50mm bonds!). I also believe incoming gas and water supplies are approximately 30m away from main incomer and would need to be run underground.

I'll go with MDJ's suggestion - Thanks
 
Can't see the problem myself actually in this case, you did your job right, the readings are fine and the circuit cabling and protection fine, what I would do is certify your works and staple a note to the certificate saying due to access you couldn't confirm bonding and you recommend they have this confirmed ASAP by an approved contractor to satisfy any problems which may relate to insurance claims should there be any incidents in the future. Your covered, they have the ownus on them, look, lets imagine then being asked by lets say london childrens hospital to install a double socket in a corridor for a cleaner, you have no access to any wards or areas due to security except the one where the socket is, now do you refuse to do the job unless you can confirm bonding to gas and water and structured steel and lightning conductor etc????, I think not, get the certificate out with the note and don't worry about it.

I would have to agree with Mike here; your reading are good so simply state the limitations and reccommendations regarding the MET and bonding issues (i.e. stating you could not gain access and confirm the ME bonding to services etc & Earthing at the MET... and advise that these are confirmed by an Approved Contractor ASAP). As long as you state what you HAVE done and HAVE NOT done on the certificate with reccomendations you are covered. Like Mike said, put the ownus on the client.
 
agree with above. basically what i said in fewer words. your a spark, not a miracle worker. they get crucified. make sure you don't. put it all down on the cert.
 
Never seen a 20KV transformer in the UK before!! The MET will as you say be in the main switchboard, but i doubt if the bonding your talking about will be in that board, especially if the work you have been doing is remote from this transformer. Each building will have it's own DB/CU it's own EMT, and it's own bonding, so you only need to check the installation from which you gained your supply from!!
 
@ Engineer 54 - I've never seen a 20KV transformer before either but there was a massive sign on it so it stuck in my memory.
 
the OP doesnt actually need access to the kiosk MET , instead locate the incoming gas / water service locations , see if they're earthed and work back from there.
 

Reply to Can't confirm bonds in hotel complex - what should i do? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
I was recently watching John Ward's video series on Electrical Installation Testing. In the part where he discusses measuring Ze, he states that...
Replies
21
Views
5K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K
In addition to the 4 main, well known competent persons schemes (NICEIC, ELECSA, NAPIT and STROMA), there is apparently another, lesser known...
Replies
18
Views
7K
I have a customer who has 4 12v spotlight that are intermittent. The original installer decided to install the transformers where they couldn't be...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock