Can an MCB be used instead of an RCBO for a supply to a UPS centeral battery system if the required disconnection times are met?
 
As a matter of interest, what sort of size is this central battery system?? At what point in the that system are you intending to replace the existing RCBO??
 
If my memory serves me right, it is a 6kVA system that is installed. (by a different company)

Originally I was told by my boss that a 50A supply was needed to the comms room. I installed a 16mm cable protected by a 50A 30mA RCBO.

The engineer who installed the system has now requested that a 32A MCB be put in place of the RCBO as there will be a high earth leakage which may trip the 30mA RCBO.
 
Further thinking on this - if the earth current is over 30mA, what does the Designer say about the Installation? Surely there is a standard design for these installations?
Now that you know it could be over 10mA earth current, then you need to read 543.7.
 
The cable is run on tray above a suspended ceiling. It is a 16mm 3 core hi-tuf cable. Single phase. I haven't been speaking to the designer yet. Should see him on Monday.
 

Reply to centeral battery UPS system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm moving into telecoms and looking for some help on disconnecting battery strings. I come from a domestic background so have not got...
Replies
6
Views
2K
We have a 5.5kW incoming supply, which cannot practicably be upgraded due to our remote location in the mountains. Can I use a PV array and...
Replies
1
Views
447
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582
So I'm looking to connect my car's battery directly to a Pure Sine Wave 2000w power inverter So I can use it on job sites etc to power a microwave...
Replies
1
Views
516
Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
925

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock