Discuss Certification advice? in the UK Electrical Forum area at ElectriciansForums.net

-Matt

-
Reaction score
152
Basically a property has two electrical supplies. (It used to be two flats, now one property).

Client wants to keep both consumer units, with one as a sub main off the other.

There is not a whole amount on the top floor board as the kitchen etc is downstairs.
So a 40/50A submain will be more than enough. (Its just bedrooms and a bathroom, shower off boiler).

The electricity board want a electrical certificate of the work before they will remove the second supply.


Now im a little unsure as to what needs to go on the electrical cert.

As its essentially a new circuit/submain, however the second consumer unit and connected circuits are not new....

So do i need to do a full testing and certificate for the whole of the second consumer unit and connected circuits?
Or just the sub main feed?

Its not something that has cropped up before.

Cheers
 
Would imagine they want a cert for the CU that you are asking them to connect to.
 
The supply being removed is still in operation, I presume. Why do they want a certificate for removing a supply?
They'll need to disconnect before you can do the work.
You're only adding to the other existing installation.

EICR for the existing, maybe.
 
The supply being removed is still in operation, I presume. Why do they want a certificate for removing a supply?
They'll need to disconnect before you can do the work.
You're only adding to the other existing installation.

EICR for the existing, maybe.

Yes this is what confused me, the client has spoken to his supplier twice:
first time they asked for a certificate to show that nothing was connected to the supply - now this I've never heard of....

The second time today while i was there, and spoke to them myself, and they asked for a certificate for the work I'm doing.
And they won't send anyone out to remove the supply until they have this.

There is a double pole isolator after the meter, so i can just remove the existing tails from this, and connect my sub main.

But I'm just not really sure what i need to put on the certificate, and what relevance this has to the supply being removed.....
 
Basically a property has two electrical supplies. (It used to be two flats, now one property).

Client wants to keep both consumer units, with one as a sub main off the other.

There is not a whole amount on the top floor board as the kitchen etc is downstairs.
So a 40/50A submain will be more than enough. (Its just bedrooms and a bathroom, shower off boiler).

The electricity board want a electrical certificate of the work before they will remove the second supply.


Now im a little unsure as to what needs to go on the electrical cert.

As its essentially a new circuit/submain, however the second consumer unit and connected circuits are not new....

So do i need to do a full testing and certificate for the whole of the second consumer unit and connected circuits?
Or just the sub main feed?

Its not something that has cropped up before.

Cheers
If you are unsure which type of certificate is required ask the Electricity Board what they require! much better idea than asking Forum members, and getting conflicting ideas.
 
I would ask the supplier in an email - then they can reply by email.

I did this last year for a client - fortunately I scheduled my works to be on site the same day as the suppliers engineer came - we had a quick chat and both of us were happy with what was going on, and who was doing what.
 

Reply to Certification advice? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
862
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
927
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
703
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
510

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock