Discuss Certifying mobile container install in the UK Electrical Forum area at ElectriciansForums.net

Ross1

-
Reaction score
16
Hi guys, I've completed a new install on a container That's to be sent off to unknown site? 63A commando skt (single phase).

I am to fill in an electrical installation certificate (which I am only able to input dead testing results). Is this correct

if I was to EICR a container the same would apply on that certificate.

many thanks
 
All you can do is the relevant dead test, its upto others on site to carry out the relevant live tests. Would be worth noting this on the EIC that you issue for it so your backside is covered.
 
Add an attachment to the EIC stating the onus of responsibility is on the customer for the on site testing of the relevant listed live electrical tests. You could also note of the need that the same tests are to be carried out at each and every location the mobile container is positioned and connected to an electrical supply in the future.

Probably won't take a blind bit of notice, but your arse is covered from here to doomsday!! lol!!
 
And on the retest date, simply put 'upon energising'. All liability will then be on the customer for the suitability of the supply. Although I would attach a sheet with the cert to recommend what supplies are suitable and ze reading etc
 
And on the retest date, simply put 'upon energising'. All liability will then be on the customer for the suitability of the supply. Although I would attach a sheet with the cert to recommend what supplies are suitable and ze reading etc


Post no 7.

If you suggest external Z readings you are getting involved in the entire install when the remit was for internal work only.

Any installer worth their salt can do ZS tests to see if the breakers comply with max ZS recommendations. Or, from the individual r1+r2 readings can work out the ZE (ZBD) required to comply
 
Nic do transportable building certificates, filled in millions of them when doing grp kiosks/buildings and steel containers. This is exactly what you need.

What do NICEIC have to do with it? Electrical installations have to comply with the relevant BS number not them bunch if eeejits.
 
Nic cert, simply r1+r2, IR, dead tests, max demand, bs numbers, etc . No ze and zs is available as the building is sent off to the customer. (Probably the other side of the country). Retest is upon energising. This is my bread and butter, company I HAVE worked for is the leader in the market for transportable buildings..... Take it easy lads. Home | Morgan Marine
 

Reply to Certifying mobile container install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
718
Hello, I am in the process of training to be an electrician and have a question. When filling out a EIC for a new circuit am I required to test...
Replies
2
Views
1K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
645
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
552
Hi all, I'm currently training thru a company called tradestech, not very impressed so far, I was told that within 6 months I'd be able to...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock