Discuss Circuit design for this water heater? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
20
Hi all

I'm doing a kitchen rewire and in kitchen client has also had a new water cylinder installed. It is a Main unvented direct 170L. I have been trying to get through to customer support but is non existent. I have not wired many new circuits for water heaters and am a bit confused with the power ratings of it, so what size breakers and cable to use and also does it require two seperate supplies. As stated not great deal of experience with these so any point in right direction appreciated. I've included the manual and power ratings sticker. Thanks
 

Attachments

  • Main_Unvented_Direct_Indirect_36005994_issue_09.pdf
    1.9 MB · Views: 31
  • IMG-20210108-WA0000.jpg
    134.6 KB · Views: 33
You say it's direct so it's either one or two 3Kw elements.
The rest is down to you re circuit design.
The MI's say 1.5 ho cable to the elements, from the isolator back to the CU is up to you.
 
You need two separate feeds from the consumer unit @ 16 or 20amp.
Keep them separate or there will be problems if on element fails (and they do)
if the op his putting on here .
 
Hi. I hope it was installed by a plumber with an unvented ticket!

Simple solution is to put a Horstmann Electronic 7 controller by the cylinder in an accessible place:
and run (not necessarily) 2.5 T&E back to the CU on a 16A breaker. Then wire the two immersions to the unit. This will allow the bottom immersion to be timed to suit, and provides the boost function. The unit ensures both immersions cannot come on at once.

However if the customer wants to be able to have both immersions on at once, wants the constrols somewhere else than at the tank, or maybe to use 'smart' controls, you might need to run a seperate supply for each immersion, and have a different unit controlling each.

If the customer is not fussed, the Horstmann unit is the simple solution!

sorry I'm wrong. Both immersions seem to be at the bottom so the above is not the intended way of operating it.
sorry!

still going to need some sort of controller though!
 
Last edited:
Hi. I hope it was installed by a plumber with an unvented ticket!
It is usual to power the lower immersion from cheap-rate overnight, and the upper from a 'boost' switch that allows the customer to top up the heat if they are running out. It depends really how the customer wants to operate it.

Simple solution is to put a Horstmann Electronic 7 controller by the cylinder in an accessible place:
and run 2.5 T&E back to the CU on a 16A breaker. Then wire the two immersions to the unit. This will allow the bottom immersion to be timed to suit, and provides the boost function. The unit ensures both immersions cannot come on at once.

However if the customer wants to be able to have both immersions on at once, wants the constrols somewhere else than at the tank, or maybe to use 'smart' controls, you might need to run a seperate supply for each immersion, and have a different unit controlling each.

If the customer is not fussed, the Horstmann unit is the simple solution!
I would hold back from recomending 2.5 Avo without knowing a bit more about the installation.
 
It depends a lot on what the customer's requirements for hot water are, and what supply tariff they have.
If they have economy 7, and use very little hot water, then the supply could be from the switched 7 hour one to a sink/bath + isolator switch, next to the cylinder, giving the option of heating water at night only, and heating either a full tank or half a tank. If the hoot water runs out during the day, then tough.
Next up, is to run a cable from the 7 hour supply, through a simple isolator switch next to the cylinder, connected to the lower element, and to run another cable from the 24 hour supply to an isolator with neon indicator, or isolator plus run back timer, connected to the upper element. This will give the customer the option of additional, more expensive, hot water during the day, if they've used up all the cheap stuff.
An alternative to the immediate above is to run a single cable from the 24 hour supply to the Hortsmann E7 controller, mentioned in another post, which combines all the isolating and timing functions, but is an ugly lump on the wall, that can't be flush fitted.
If the customer doesn't have an E7 tariff, or similar, then the first method of installation can be used, fed from the 24 hour supply. This will allow the customer to only heat half a tank if their hot water demands are low, or more when they need it.
The next more sophisticated set up where no E7 supply is available is a single cable from the supply to an isolator and time switch near the cylinder with a second switch selecting the element to be heated.
The last method I can think of, is to run two cables from the supply to two isolators, one feeding a time switch and then the lower element, and the other, either incorporating a neon indicator, or feeding a run back timer, and then the upper element.
All supplies should be fed by a 16A breaker, and the size of the cable will be a minimum of 2.5mm2 T&E, but may need to be larger, depending on insulation it may have to pass through and the length of the run.
 
Hi. I hope it was installed by a plumber with an unvented ticket!

Simple solution is to put a Horstmann Electronic 7 controller by the cylinder in an accessible place:
and run (not necessarily) 2.5 T&E back to the CU on a 16A breaker. Then wire the two immersions to the unit. This will allow the bottom immersion to be timed to suit, and provides the boost function. The unit ensures both immersions cannot come on at once.

However if the customer wants to be able to have both immersions on at once, wants the constrols somewhere else than at the tank, or maybe to use 'smart' controls, you might need to run a seperate supply for each immersion, and have a different unit controlling each.

If the customer is not fussed, the Horstmann unit is the simple solution!

sorry I'm wrong. Both immersions seem to be at the bottom so the above is not the intended way of operating it.
sorry!

still going to need some sort of controller though!

It depends a lot on what the customer's requirements for hot water are, and what supply tariff they have.
If they have economy 7, and use very little hot water, then the supply could be from the switched 7 hour one to a sink/bath + isolator switch, next to the cylinder, giving the option of heating water at night only, and heating either a full tank or half a tank. If the hoot water runs out during the day, then tough.
Next up, is to run a cable from the 7 hour supply, through a simple isolator switch next to the cylinder, connected to the lower element, and to run another cable from the 24 hour supply to an isolator with neon indicator, or isolator plus run back timer, connected to the upper element. This will give the customer the option of additional, more expensive, hot water during the day, if they've used up all the cheap stuff.
An alternative to the immediate above is to run a single cable from the 24 hour supply to the Hortsmann E7 controller, mentioned in another post, which combines all the isolating and timing functions, but is an ugly lump on the wall, that can't be flush fitted.
If the customer doesn't have an E7 tariff, or similar, then the first method of installation can be used, fed from the 24 hour supply. This will allow the customer to only heat half a tank if their hot water demands are low, or more when they need it.
The next more sophisticated set up where no E7 supply is available is a single cable from the supply to an isolator and time switch near the cylinder with a second switch selecting the element to be heated.
The last method I can think of, is to run two cables from the supply to two isolators, one feeding a time switch and then the lower element, and the other, either incorporating a neon indicator, or feeding a run back timer, and then the upper element.
All supplies should be fed by a 16A breaker, and the size of the cable will be a minimum of 2.5mm2 T&E, but may need to be larger, depending on insulation it may have to pass through and the length of the run.
Thank you all. All really helpful. There's still things I'm encountering that not got great deal of experience with so always think it's best to check things out. Turns out the previous spark has made bit of balls up and has already been wired off a new ring. I had checked some things out earlier and got clearer on how an unvented direct cylinder works. It is not an economy 7 property only has one supply. My initial thoughts were to something similar to what you suggest Avo I am a bit short of spare ways so was going to use something similar to the Horsemann timer and supply both the top and bottom immersions from this from 16 amp 2.5. Am I correct that you still think this is viable option? I don't think I require any sort of isolation switch for this do I? As the controller would effectively do this, so just hardwire supply to Horsemann and then the 2 flexes from this?

Thanks
 

Reply to Circuit design for this water heater? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

At Electrical2Go, we have recently broadened our product range to include water heaters. Our goal is to offer comprehensive solutions for both...
Replies
0
Views
724
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
905
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock