Discuss Clarification on additional sockets on a spur in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
Evening all

Got a query excuse me if not seeing the simple logic. On reading regs book it states can install one unfused spur off ring in 2.5 but if more sockets required need to first wire through a fused spur. My question is, is this all because of possibility of overloading one leg of the ring or is it to protect the first cable coming off the ring? If this is the case can any justification be made if ran a 4mm off the ring to first socket and then a 4mm to second. Thanks
 
the reg.for fusing down is mainly to protect the spur cable (generally 2.5mm) from overload as the ring is protected @ 32A. if you were to install an unfused 4mm spur with several sockets, you run the risk of putting too muck load on 1 point of the ring, esp if it were close to one end of the ring.
 
the reg.for fusing down is mainly to protect the spur cable (generally 2.5mm) from overload as the ring is protected @ 32A. if you were to install an unfused 4mm spur with several sockets, you run the risk of putting too muck load on 1 point of the resp if it were close to one end of the ring.
Thanks Tel. So if a 4mm is used as initial cable of the ring this is then protected against overheating. If as you said though that socket coming off is at one end of ring is there now a over heating danger to one of these or is it just that because current isn't spread around ring adequately that it is just likely to trip out?
 
if the spur is taken close to one end of the ring, then the short leg of the ring will carry most of the spur current.
 
In practice it does not matter at what point on a ring a spur comes from.
In the case of an unfused spur feeding a twin socket then potentially a load of 26a could be drawn at that point on the ring. With a fused spur the number of sockets on the load side is unlimited because overload protection @13a protects the spur cable both upstream and downstream from the FCU.
So in theory a fused spur is far less likely to result in excess load on one point of the circuit. But unfused spurs are far more common than fused spurs. In practice diversity and spread of load means 2.5mm ring circuits are rarely stressed unless poorly designed for known high load situations like commercial kitchens.
 
What do you want to get around? If you ran 4mm, depending on correction factors you could most likely run it as a radial anyway with the 32A MCB.
In practice it does not matter at what point on a ring a spur comes from.
In the case of an unfused spur feeding a twin socket then potentially a load of 26a could be drawn at that point on the ring. With a fused spur the number of sockets on the load side is unlimited because overload protection @13a protects the spur cable both upstream and downstream from the FCU.
So in theory a fused spur is far less likely to result in excess load on one point of the circuit. But unfused spurs are far more common than fused spurs. In practice diversity and spread of load means 2.5mm ring circuits are rarely stressed unless poorly designed for known high load situations like commercial kitchens.
Thanks radiohead is there any scenarios then you would be comfortable doing what I proposed....2 double sockets off 4mm from ring.
[automerge]1595185833[/automerge]
If you require more than one additional socket then just split & continue the ring circuit
It's option dazzler but this job I'm already having to cut hole in plasterboard and another hole in skirting just to get a cable through trying to keep holes and trunking down to minimum
[automerge]1595185881[/automerge]
What do you want to get around? If you ran 4mm, depending on correction factors you could most likely run it as a radial anyway with the 32A MCB.
No chance of running new circuit TJ have to come off existing ring
 
IMO, you dont have any choice other than extending the RFC, or spur off with 13amp switched spur then you can run as many as you like. (radial off the spur)

Personally I Dont like the latter
 

Reply to Clarification on additional sockets on a spur in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
302
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
605
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
673

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock