Hello all, I'm not sure if this is the right forum but I will share what I have. I'm going to be installing a heater in my garage (see title) My plan is to run some 8/2 wire from the electrical panel in my basement through the floor boards and into my garage. I will install a disconnect box just below heater in garage and then use some flex conduit to run the wire to the back of the heater.

It looks like the heater pulls about 32.5 amps running on its highest setting so I'm thinking a 40 amp breaker for my panel should be sufficient.

Does everything sound like I'm setting this up right? Am I missing something?
 
what is 8/2 wire? are you outside the UK?
 
I'm going to hazard a guess from the terminology that you are in the USA?
If so you'll probably be better off with a USA based forum, the vast majority of the membership of this forum is UK based.
 
it's both 110 and 220. the 220 being derived from 2 phases ( i think).
 
@110V your current would be 68A though.
 

Reply to Comfort Zone 7500w garage heater in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
740
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
787
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
687
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
203

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock