Discuss Connecting multiple drives to only one adapter/transformer in the DIY Electrical Advice area at ElectriciansForums.net

StefanL

DIY
Reaction score
2
Hi everyone, I have several external disk drives, all from the same manufacturer and all using the
same type of transformer - input 220V, output 12V, 1.5A, 18W. Currently I plug them all in a multiple socket
plug the length of a Dachshund:)) and it looks just horrible. Is there a way to have only one transformer powering
all the drives at the same time? If so, what should I look for?
Any suggestion is much appreciated. Thank you!
 
Say each drive requires 1.5Amps (18watts), then multiply the number of drives you have by those numbers to get the minimum size of power supply. Eg if your Dachshund is six PSU's long, you would need a 6 x 1.5A = 9A supply.
Round it up to 10A to be safe. So a 12V 10A (120W) power supply. But do the sum for the number you have.
I suggest you need a proper stabilised and filtered supply, not one for LED's etc, so you have a choice of a computer type "in-cord" type plastic box such as:
or you could use a chassis mount metal enclosed type, which you would need to put in a housing of some sort to protect the live mains connections - this is a higher power one:

Appreciate you are in Romania, so you would find local equivalents.

There is a possibility of conducted electromagnetic interference between the drives (because they would all be connected directly together, where previously they had the filters in the individual power units) and if that did happen it might be quite expensive to add filters between them all.
You also have the possibility of simultaneously blowing up all the drives, if you have a wiring problem, or if the power supply fails in such a way as to put excessive voltage on the output. Dachshund redundancy can be a good thing!
 
Say each drive requires 1.5Amps (18watts), then multiply the number of drives you have by those numbers to get the minimum size of power supply. Eg if your Dachshund is six PSU's long, you would need a 6 x 1.5A = 9A supply.
Round it up to 10A to be safe. So a 12V 10A (120W) power supply. But do the sum for the number you have.
I suggest you need a proper stabilised and filtered supply, not one for LED's etc, so you have a choice of a computer type "in-cord" type plastic box such as:
or you could use a chassis mount metal enclosed type, which you would need to put in a housing of some sort to protect the live mains connections - this is a higher power one:

Appreciate you are in Romania, so you would find local equivalents.

There is a possibility of conducted electromagnetic interference between the drives (because they would all be connected directly together, where previously they had the filters in the individual power units) and if that did happen it might be quite expensive to add filters between them all.
You also have the possibility of simultaneously blowing up all the drives, if you have a wiring problem, or if the power supply fails in such a way as to put excessive voltage on the output. Dachshund redundancy can be a good thing!

Always have a backup dog 🐕. Good advice.
 
Say each drive requires 1.5Amps (18watts), then multiply the number of drives you have by those numbers to get the minimum size of power supply. Eg if your Dachshund is six PSU's long, you would need a 6 x 1.5A = 9A supply.
Round it up to 10A to be safe. So a 12V 10A (120W) power supply. But do the sum for the number you have.
I suggest you need a proper stabilised and filtered supply, not one for LED's etc, so you have a choice of a computer type "in-cord" type plastic box such as:
or you could use a chassis mount metal enclosed type, which you would need to put in a housing of some sort to protect the live mains connections - this is a higher power one:

Appreciate you are in Romania, so you would find local equivalents.

There is a possibility of conducted electromagnetic interference between the drives (because they would all be connected directly together, where previously they had the filters in the individual power units) and if that did happen it might be quite expensive to add filters between them all.
You also have the possibility of simultaneously blowing up all the drives, if you have a wiring problem, or if the power supply fails in such a way as to put excessive voltage on the output. Dachshund redundancy can be a good thing!

Wow, thank you for such a detailed explanation! Much appreciated. The problem is that I have already 12
hard disk drives and this number is only going to grow as I store large amounts of data. On top of that some drives are back-ups, so I have duplicate data just to be sure I don't lose it. I will keep in mind all your comments and decide what to do. The thought of blowing them all at once suddenly makes the Dachshund cute after all!!
 
On top of that some drives are back-ups, so I have duplicate data just to be sure I don't lose it.
Surely back-ups on a separate fault tolerant system, preferably somewhere else, or in the cloud?
Unless the data doesn't really matter 🤔
 

Reply to Connecting multiple drives to only one adapter/transformer in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hi everyone, I'm looking to do some cable runs for cat6 etc in my house and was looking for some advice on blind wiring. I'm not skilled but I...
Replies
0
Views
849
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
936
Hi, So I ended up with a Ring video wired doorbell instead of a Byron video wired doorbell as B&Q were out of stock (had ordered online) and they...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock