I suppose if you have an understanding of power tools then it’s fine one of my best mates does it with impact and I cringe every time I see/hear him at the consumer but to be fair he understands the torque it’s the ones who don’t have knowledge/experience that cause the problems anyhow I don’t like power tools at consumer

The drill/driver is used in that video is not an impact driver and can be set to exceptionally low torques. I've no idea what it was set at and whether or not those terminals were over/under tightened, but it's worth noting that they are very different tools.
 
The drill/driver is used in that video is not an impact driver and can be set to exceptionally low torques. I've no idea what it was set at and whether or not those terminals were over/under tightened, but it's worth noting that they are very different tools.
Doesn’t matter shudn be using them unless like @telectrix just posted then that’s the exception “HAND TOOLS ONLY”
 
Doesn’t matter shudn be using them unless like @telectrix just posted then that’s the exception “HAND TOOLS ONLY”

Drill drivers can be set to exceptionally low torques - often so low that it wouldn't be considered much more than hand tight.

Having said that, I just looked at the video again and note that it is indeed an impact driver :tearsofjoy:
 
The drill/driver is used in that video is not an impact driver and can be set to exceptionally low torques. I've no idea what it was set at and whether or not those terminals were over/under tightened, but it's worth noting that they are very different tools.
What
The drill/driver is used in that video is not an impact driver and can be set to exceptionally low torques. I've no idea what it was set at and whether or not those terminals were over/under tightened, but it's worth noting that they are very different tools.
what do you use mate? Drill/driver is it?
[automerge]1601669683[/automerge]
Drill drivers can be set to exceptionally low torques - often so low that it wouldn't be considered much more than hand tight.

Having said that, I just looked at the video again and note that it is indeed an impact driver :tearsofjoy:
??
 
If people are using 18v impact drivers to tighten down terminal screws something went wrong with the trade...
I'll be honest if I've got a board full I'll wizz all the terminals fully open with the driver and tighten them back up just tight enough to hold then run down the lot with the torque driver.

If you use an impact enough then you can be quite gentle with it.

Never rounded a screw yet
 
I'll be honest if I've got a board full I'll wizz all the terminals fully open with the driver and tighten them back up just tight enough to hold then run down the lot with the torque driver.

If you use an impact enough then you can be quite gentle with it.

Never rounded a screw yet
Ok so you’re under the category of experienced but I’m sure you agree with the fact that it’s more sensible to hand tighten terminations so you can feel the tension
[automerge]1601670108[/automerge]
I don't regularly fit consumer units - in fact I've fitted a grand total of one and the use of power tools was limited to mounting it.
Good man stick to the hand tools once mounted ?
 
Ok so you’re under the category of experienced but I’m sure you agree with the fact that it’s more sensible to hand tighten terminations so you can feel the tension
There's a time and a place, if its an obsolete MCCB it'll be hand tools only, if its a board change and mistakes can rectified the returns outweigh the risk.

What does grind my gears is certain manufacturers applying thread lock to terminal screws, not sure how that helps come EICR time.
 
I don't know how these manufacturers calibrate their torque screwdrivers, but mine was so far out it could not be tightened to 2.1N required by Hager without bending the Din rail the RCBO was fixed too, anyone want to buy a full set of Armeg drivers?
 
I don't know how these manufacturers calibrate their torque screwdrivers, but mine was so far out it could not be tightened to 2.1N required by Hager without bending the Din rail the RCBO was fixed too, anyone want to buy a full set of Armeg drivers?
Normally it’s 1.7N isn’t it? Only 2.1 or higher for main switch you don’t need torque settings to know the correct torque I don’t think aslong as you understand the recommendations
[automerge]1601671339[/automerge]
Normally it’s 1.7N isn’t it? Only 2.1 or higher for main switch you don’t need torque settings to know the correct torque I don’t think aslong as you understand the recommendations
Difficult area but again like I said it all boils down to experience and knowledge
 
None of Hagar's equipment is recommended to be torqued to as low as 1.7N, in fact it can be as high as 3.6N.
 

Attachments

  • Hager Torque settings copy.pdf
    43 KB · Views: 16
What does grind my gears is certain manufacturers applying thread lock to terminal screws, not sure how that helps come EICR time.
It would depend on the type of threadlock.

Some is soft and easy to undo, only to stop gross loosening from vibration, etc. But some (e.g. "studlock") is like superglue and never expected to be undone without serious force!

If you do need to stop an adjuster from moving unintentionally and don't have anything special to hand you can use a dab of nail varnish, which you can get pretty much in any local chemist or supermarket.
 
i have a small bottle of Loktite on the van. still half full after 20 years of occasiona luse.
 
It would depend on the type of threadlock.

Some is soft and easy to undo, only to stop gross loosening from vibration, etc. But some (e.g. "studlock") is like superglue and never expected to be undone without serious force!

If you do need to stop an adjuster from moving unintentionally and don't have anything special to hand you can use a dab of nail varnish, which you can get pretty much in any local chemist or supermarket.

It's a good excuse for why you're carrying nail varnish as well. I always carry women's tights as well in case my fan belt breaks.
 
You should connect the cpcs first.
So when you test N-E for a particular circuit you will have all the CPC's connected in the earth bar? What would be wrong with doing the IR testing of N-E without having the CPC's in the earth bar? Are you saying parallel paths could cause different results? Are we not testing that particular circuit, i.e that particular cable, which is why we put the test result in the little box related to that one circuit?
A lot of questions there!
 
So when you test N-E for a particular circuit you will have all the CPC's connected in the earth bar? What would be wrong with doing the IR testing of N-E without having the CPC's in the earth bar? Are you saying parallel paths could cause different results? Are we not testing that particular circuit, i.e that particular cable, which is why we put the test result in the little box related to that one circuit?
A lot of questions there!
There could be Parallel paths to earth. I’ve never know anyone to not IR test with everything connected to the MET
 
What would be wrong with doing the IR testing of N-E without having the CPC's in the earth bar?
The CPC of the circuit being tested is probably isolated from all the others CPCs and the Earth, so you would not see a leak from N to true Earth (e.g. a screw, etc, that is touching the N copper and in to plasterboard, etc) as it would not be guaranteed to complete the circuit from true Earth to CPC and back to your IR tester.
[automerge]1601722401[/automerge]
Basic idea is this (sorry for poor diagram):
IMG_20201003_114658420_HDR.jpg

[automerge]1601722565[/automerge]
So IR testing with the CPC isolated will pick up on an internal cable fault (say N to E), but not for external faults (N to some other CPC or true Earth).
 
Last edited:

Reply to Consumer unit change - How do you do it? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
679
I was just googling for skeleton boards after reading the last thread and various pictures of consumer units popped up, some wired terribly and...
Replies
6
Views
710
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
I’ve had a disagreement with one of the Engineers in work. So we are doing an install. Installing an Intruder Alarm. Rather than go with my...
Replies
48
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock