Just wired the 1st house on a new site, consumer unit wired to location marked on plan which was in kitchen unit at high level.

Building inspector comes in and okays everything but the consumer unit height, says they have to be at 1350-1450mm, was a new one on me and we ended up pulling in a few new legs in to allow for dropping it down abit. Funnily enough 1400 would've been half in and half out of the kitchen unit so it couldn't go at his stated height anyway.

Just wondered if anyone has a better knowledge of the building regs than me and could enlighten me, I know I asked the NIC in the past (for what it's worth) and they said no requirements other than accessible.

Cheers
 
building reg. it's so that the kids can reach it to squirt jam and stuff in it.
 
I can understand the accessibility issue with part M.... but where does that rather precise height come from ? plucked out of thin air ?
 
I can understand the accessibility issue with part M.... but where does that rather precise height come from ? plucked out of thin air ?

That's what I'm wondering, my mate spoke to him not me, he said we've never done that on other sites before and the inspector said well maybe they're not working to the latest regs!

I would have asked to see something written down but I think the consensus between the builders and my mate was just keep him happy.
 
That's what I'm wondering, my mate spoke to him not me, he said we've never done that on other sites before and the inspector said well maybe they're not working to the latest regs!

I would have asked to see something written down but I think the consensus between the builders and my mate was just keep him happy.

If it's going to be a continued pain in the arse to mount at that height as you continue through these new builds, I would ask him for the written regs passages. I don't do new builds but I am aware that BS7671 and the building regs are not the only things you may be asked to satisfy.
If you are happy to comply then don't kick up a fuss, as a militant clerk of works/building inspector with a bee in his bonnet can be a right waste of your time and money.
 
Where abouts should I be looking for that ? I can't find any specific height for consumer units in the approved document.


You would need part M page 46 letter f
"Controls that need close vision" or in simple terms as I was told be able to read the labels we put on the CU.
 
You would need part M page 46 letter f
"Controls that need close vision" or in simple terms as I was told be able to read the labels we put on the CU.

I did see that note, and I would disagree with that but hey, I'm not about to hijack this thread. :D
 
So what height would you put CU so all can read/operate (sitting & standing persons)

Oh don't get me wrong, I completely agree that a person in a wheelchair should be ale to operate their circuit breakers...... It's the part about it needing close vision to normally operate. I would agree with that if the operator in question is vision impaired though. It's just another poorly worded piece of guidance.....
As I have said before I have not been involved with new builds since working for myself. Probably a good job as I would be constantly arguing about things like this... lol
 
New dwellings
1.4
Wall-mounted socket-outlets, switches and consumer units in new dwellings should be easy to
reach, in accordance with Part M of the Building Regulations (Access to and use of buildings).
NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting.
 
New dwellings
1.4
Wall-mounted socket-outlets, switches and consumer units in new dwellings should be easy to
reach, in accordance with Part M of the Building Regulations (Access to and use of buildings).
NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting.
?

put it level with the top of the door like every other new build.

in my eyes its not functional, the circuits should not be switched back on till fault has been found and fixed.

there is no max hight for spotlights or batterns?

surely you swap the lamps more often than touch th ccu in your own home.


many people now have lived in there house for 5-10 years and dont know where the ccu is because they havent needed to use iit
 
New dwellings
1.4
Wall-mounted socket-outlets, switches and consumer units in new dwellings should be easy to
reach, in accordance with Part M of the Building Regulations (Access to and use of buildings).
NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting.
?

put it level with the top of the door like every other new build.

in my eyes its not functional, the circuits should not be switched back on till fault has been found and fixed.

there is no max hight for spotlights or batterns?

surely you swap the lamps more often than touch th ccu in your own home.


many people now have lived in there house for 5-10 years and dont know where the ccu is because they havent needed to use iit
 
New dwellings
1.4
Wall-mounted socket-outlets, switches and consumer units in new dwellings should be easy to
reach, in accordance with Part M of the Building Regulations (Access to and use of buildings).
NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting.

Where is this copied from?
 
the ccu can be at whatever height you want. personally as long as someone 6' can easily reach it.

put it above a door if you like and its still accessible

37772b51ad90e0d1a5d57a9d9b87ea6e.jpg


1f533fb0f91bb59a0089ae46b5715e68.jpg
 
Comes down to the way you ask the question imo.
"I've not heard that one before mate, where does it come from?" is more likely to be well received than
"That's complete and utter BS you bloody clown. You haven't got a clue so show me where you get that from and I'll believe you"
Ah, calling em clock suckers was clearly impolite :D
 
I'm not a fan of putting them too low so kids can play with them. Also a mate of mine had his badly damaged in his new house with furniture removal men. While carrying his sofa into his house his CU was smashed and badly damaged! It needed replacing and I ended up having to sort it for him. Bloody mates rates!!
 
I'm not a fan of putting them too low so kids can play with them. Also a mate of mine had his badly damaged in his new house with furniture removal men. While carrying his sofa into his house his CU was smashed and badly damaged! It needed replacing and I ended up having to sort it for him. Luckily the removal mens insurance covered the cost of it.

i think you made a typo in your reply.
 
Don't we all just love these ambigious regs!

NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting


 
Don't we all just love these ambigious regs!

NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting


go for a bs88 board so there are no switches so they cant fail it lol
 
Don't we all just love these ambigious regs!

NOTE:
Approved Document M recommends that in new dwellings only, switches and socket-
outlets for lighting and other equipment should be between 450mm and 1200mm from finished
floor level. Approved Document M does not recommend a height for new consumer units.
However, one way of complying with Part M in new dwellings is to mount consumer units so that
the switches are between 1350mm and 1450mm above floor level. At this height, the consumer unit
is out of reach of young children yet accessible to other people when standing or sitting



sitting on what? a stepladder?
 
why do you think MCBs are up for on?. it's so a walking stick can reset.
 
Anyone ever had a successful arguement with building control that Part M only applies to new builds that are to be unoccupied on completion? (e.g. you dont know who is going to purchase the property so you have to assume it could be by say a wheelchair user and hence follow the Part M dimension guidlines. )

If doing an installation for a current owner then you re-wire to his spec for socket/switch heights, location of consumer unit etc ..... and Part M doesnt apply?

Not got the answer and never debated it before so be interesting to hear any views from anyone who has had the debate with an inspector .......
 
Anyone ever had a successful arguement with building control that Part M only applies to new builds that are to be unoccupied on completion? (e.g. you dont know who is going to purchase the property so you have to assume it could be by say a wheelchair user and hence follow the Part M dimension guidlines. )

If doing an installation for a current owner then you re-wire to his spec for socket/switch heights, location of consumer unit etc ..... and Part M doesnt apply?

Not got the answer and never debated it before so be interesting to hear any views from anyone who has had the debate with an inspector .......

where have you gleaned that bit of BS from?
 
I know of one interesting case

I heard about this from my father who is a retired building control officer

A disabled gentleman who uses a wheelchair was having a house built for himself, so he is pretty much the kind of person part M is talking about.
He was adamant that he wanted his sockets and switches at the normal height and not the part M height, particularly the sockets as he thought they were an eyesore at that height.
So the local BC guy was quite happy with his request and allowed the deviation. However the NHBC inspector was far more troublesome and if took a lot of arguing and letter writing to get them to allow the deviation.

You can just imagine the nhbc inspector telling the guy in the wheelchair that he can't have his sockets at the height he wants them just in case someone in a wheelchair wants to use them!
 
Last edited:
where have you gleaned that bit of BS from?

It was put to me in a chat over applicability of Part M. Something along the lines of a 7ft family have a house built and want their switches at 5ft because its convenient for them. Do they then have to be inconvenienced and have them installed at a max of 4ft (1200mm) to comply with building regs, even though they will be the sole users of the property?

Hence the notion of Part M applicability to empty property when the new owner isnt known.

I'd never thought of it in that sense before, thus interested in hearing of any experience with building control .....
 
I can see the reasons for allowing it too be changed like the example both yourself and Dave have given, but you would need LABC permission for it too happen as its not actually part of Part M for variables to it.
 
these people need to protect their income so--- every so often they come up with another plan
hence the 16ths too the 17 regs

same with the building so called regulations
greed is good
 
Thanks for all replies, needless to say we aren't going to kick up a fuss not worth the hassle but interesting to know what the actual truth of it is just so to know for another time.
 
Brought my house which at the time was about 10 yrs old. About 5 years later decided I wanted access into Con-unit. I could not remove the lid! Con-unit was mounted in the kitchen at high level...well sort of high level...The top of a wall mounted cupboard was directly in front of the con unit. Half the con -unit was above the wall cupboard other half below and inside the cupboard. Whilst fitters had cut round con -unit with about 25mm clearance, there was no way the lid could be removed completely. At the time it was a Hagar split board. Now replaced and moved to a much better position.
 

Reply to Consumer unit heights and building regs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Customer asking me to fix 3 phase consumer unit on a new shop . Its brand new installation . He want to use every part of shops and he...
Replies
9
Views
3K
Hello, you all helped me out recently when we had a water leak (mostly in kitchen ceiling), and my landlord's contractor was saying the household...
Replies
7
Views
2K
Hi all, New homeowner here... hoping it's okay to seek some advice on a quote. I've recently had some wiring done for a new kitchen in a small...
Replies
27
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I work with someone who really isn't happy installing new circuits into plastic consumer units. Sometimes he refuses to do it if the board in...
Replies
44
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock