Discuss Consumer unit TT system far from DNO fuse in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Evening all, I’d appreciate your opinions here:
I’m looking at an old (150 years+) stone house. Complete rewire and renovation. DNO fuse is currently where the master bedroom will be (upstairs). Client wants it to be moved to a more accessible location downstairs about 15m away depending on the routing of cable.
The timescale for DNO to move their supply and make my life easier is too great so to be avoided if theres any other option.
So the plan is DNO fuse -> meter tails (1m long) -> 100mA Type S RCD (100A) -> SWA (15m x 3c25mm)-> new CU.
Perhaps I can get away with a main switch instead of Type S RCD if tails are properly protected.
Conveniently (or not) there is an earth rod pit on the other side of the wall to where he wants the new CU.
This means I can fairly easily install the MET next to the new CU and bond the CU and incoming SWA to that.
All ccts from CU will be RCBO protected radials.
Any thoughts on this?
What about fitting backboxes to old stone? Its going to be an absolute nightmare to drill, thankfully he plans to dot and dab so no chasing needed.
Thanks
 
Last edited:
Hmm, usually you would look at a switched-fuse on the SWA in case of a fault, but on TT then it would need a (delay) RCD for clearing L-E faults. Relying on the DNO fuse for L-N fault clearance is slightly suspect, but that is less likely than L-E in the event of someone nailing the SWA by mistake. As it is a TT system you don't need 3C cable as the armour on 2C will do for CPC since its impedance will be several orders of magnitude less than your earth rod(s). However, if it is ever "upgraded" to PME the installation would need the 10mm main bond conductors back to the DNO cut-out point as even 3C 25mm SWA is only 7.7mm Cu equivalent in the armour (though obviously with 3C you have your >= 10mm CPC internally).

Just to note that 25mm SWA in duct is marginal for 100A incidentally. Meets it for 90C insulation types but you would need to check accessories are up for that. In the 100A case I would be tempted to go for 35mm 2C SWA, but if 80A or less 25mm has no worries.

Going all-RCBO is certainly the best plan, and I will avoid commenting on RFC-versus-radial to keep out of those wars here. However, I would suggest you get DP switching RCBOs such as Wylex. Crabtree, or Fusebox, so a N-E fault is not going to take out the 100mA delay RCD feeding the lot.
 
Last edited:
Drilling stone isn't a problem with SDS.
What can be a problem is if the walls are 600mm + thick, twin leaf with loose infill, as the fill drops when you pull the drill bit out.
The solution is to remove the drill and push the drill bit through with a sleeve, as I had to with my Son's house in Northumberland.

If the DNO head (and meter) are upstairs presumably it's overhead supply?
If so why not run SWA back outside for now and in to the new CU postition, then when the DNO move their cable and head, do away with the SWA and switch fuse.
 

Reply to Consumer unit TT system far from DNO fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
773
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock