Ok so the above drawing would work?

My last corrected/Edited drawing (in response to Richard kindly pointing out my mistake earlier) in Post #94 is electrically almost the same as Richards and should work (it follows the drawings I did earlier).

Richard has got the Stop button as N/O when it should be N/C, which he has already pointed out.

It's been a long week! lol
 
Lol.
Beautiful! Well a huge thank you ladies and gentlemen and I'll post ttomorrow and see how I get on. I'm wondering if I should buy a stc-1000 off eBay to give digi temp reading
 
Lol.
Beautiful! Well a huge thank you ladies and gentlemen and I'll post ttomorrow and see how I get on. I'm wondering if I should buy a stc-1000 off eBay to give digi temp reading
Have I finally cracked it?

Untitled.jpg
 
You are getting there JP, lol

That would work, my only preference would be to have the supply to terminal no.3 of the contactor coming from after the the N/C stop button (from the terminal blocks at the top left of your drawing) rather than from the permanent live.

The reason for that is because if you have a latching/locking type stop button this will kill all of the power to the contactor/s.
 
You are getting there JP, lol

That would work, my only preference would be to have the supply to terminal no.3 of the contactor coming from after the the N/C stop button (from the terminal blocks at the top left of your drawing) rather than from the permanent live.

The reason for that is because if you have a latching/locking type stop button this will kill all of the power to the contactor/s.

The button is a spring loaded stop button.
Mill modify drawing :)
 
If you’re hoping to sell this thing, just think about the legal aspects to it.
With you’re lack of knowledge there is no way this is going to be designed safely or to legislation.
 
Im drunk.com but just realised i explained in post 89 how to wire it correctly from OP's diagram and there's a whole page of different wiring configerations before it was corrected to the same suggestion as i did .....no offense meant but made me chuckle :)
 
Im drunk.com but just realised i explained in post 89 how to wire it correctly from OP's diagram and there's a whole page of different wiring configerations before it was corrected to the same suggestion as i did .....no offense meant but made me chuckle :)

Howdy all!
Panel is all working and just installing the lamp holders for the push buttons... What you rekon to the below? Going to link live in from the start button? Good/Bad idea?
J


photojyg.jpg
 
I normaly take the live feed (run signal) for a light through a N/O contact on the relevant contactor/relay....that way i always know that if the run light is shineing the contactor is definitely engaged.

X1 = live in
X2 = Neutral
 
Also not sure how your fusing all this but indication lamps in your set-up would be wise to have own fused feed so a lamp blowing wont take the rest of the control out and shutting the system down as i highlighted in an early post you have a basic circuit set-up and far from the system that would be classed as a marketable, it falls short in many areas and i strongly suggest you get reading up.... although you have a funtional system now which operates correctly its a crude set-up for the job and this will have knock on effects from early failure of contactors if stat control starts hunting to unecessary down time for minor issues. Designing systems isn't just about getting a working model but also about seeing all the senerio's if any part of the system fails and what can be implemented to keep the system going safely, your use of a 240v control circuit limits you as to how you can expand or add if customer asks for additions or changes.
Dont get me wrong here; its good to see enthusiam like yours but be aware of the complexity of control systems goes way beyond what you know at the moment as ive tried highlighting with your system so be cautious not to jump in the deep end before you have learnt to swim.
Id would invest in a control wiring schematic software programme that let you try your circuits on your computer and will let you operate the virtual design to see what happens long before you put it into practice.

Edit .... just to understand what i mean by forseeing all circumstances then tell me what would happen if you had a leak and lost the water or the system was switch on while drained ????? Massive repair bill comes to mind replacing elements maybe even pump if run dry well you get my drift.
 
Last edited:
Well put DW,

I was going to say, we only gave the basic outline of the functional blocks and nowhere near a final design, as you say there are many other factors to consider.
I believe Tony also mentioned this a few posts back.

OCPD's just being one of them.
 
Bet there's still bits missing from this. I hope the OP has taken time to learn how to read a drawing.

View attachment 14083

Yes understood. I have learned so much in the past week, and thank each and every one of you who took time to write me a reply and do a drawing. This is what forums are all about, and understand that although my present solution is far from prefect, their is room for improvement.

I am looking at your drawing Tony and already in the process of not just putting 1 level switch in, but two (one for min and one for max).

I am just on ebay getting a PID sensor with SSR.
 
Hi JP,

Glad you got the basics working.

As DW and Tony have said though, this is far from the finished article.

If you noticed on my drawing, and I think Tony's too, we never marked the control circuits with a L or N, this was because generally it is better not to use 230V for the controls (unless all controls are staying inside the panel), as DW pointed out too, it is usually much better to use say 24V DC for these circuits, this would have made it much easier, for example to add your floats or other safety/inhibit sensors which may be remote from the panel.

Using SELV for the controls makes it far easier to comply with electrical regs, where sensors etc. are to be used outside of the control panel, also consider seperate fusing of the controls, as well as the heater side of things, there are other things too to consider, such as earthing the metal work of the panel, a seperate earth strap to any doors and/or any removable covers/gland plates, IP ratings of the panel, safety and voltage labels. As you can see the list just goes on and on, and this is far from easy, if not impossible on an internet forum.

As Tony and Dw also pointed out, it is a massive legal can of worms to design and build an electrical panel which will have to satisfy a number of different statutory regs, and pass mandatory general electrical safety tests too, from a legal point of view, when offering such items for sale.

I do wish you good luck with your project, and Iam also sure different people will have many different views on the best way forward (many ways to skin a cat).
 

Reply to Control Panel for 3ph Heaters in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
864
Hi guys I have a faulty pactrol weather watcher which controls the night storage heaters this is now obsolete and I can't find a replacement...
Replies
2
Views
747
Hi - we have an inline heater for a vent system that appears to always be on. I believe the electrician may have wired it incorrectly with only a...
Replies
3
Views
688
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
444

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock