Discuss Cooker circuit (cable size?) in the UK Electrical Forum area at ElectriciansForums.net

Zdb

-
Esteemed
Reaction score
496
Hi guys, I've been given the task of installing a 32A commando socket w/ isolator, which will have a 27A oven plugged into it. It will be on a C32 30mA RCBO. The cable from the oven is 4mm which will have the 32a commando plug fitted to it.

My question is, should I wire the 32A commando socket in 4mm or 6mm? The cable run isn't very long so voltage drop won't be an issue.
 
Hi guys, I've been given the task of installing a 32A commando socket w/ isolator, which will have a 27A oven plugged into it. It will be on a C32 30mA RCBO. The cable from the oven is 4mm which will have the 32a commando plug fitted to it.

My question is, should I wire the 32A commando socket in 4mm or 6mm? The cable run isn't very long so voltage drop won't be an issue.
Installation method
Length of run
What do your calculations tell you
 
you using singles? any diversity applicable to the cooker?
 
then base your calcs on the multicore cable as that will probably have the lowest ccc.
 

Reply to Cooker circuit (cable size?) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
958
Came across a cooker circuit with 10mm and 40A rcbo. Last leg was 6mm. Isolator to outlet. I downgraded to rcbo to 32A to accommodate the 6mm...
Replies
8
Views
1K
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
664
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
921

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock