Discuss Cooker circuit mcb in the UK Electrical Forum area at ElectriciansForums.net

Assuming this is a fan oven I would not consider it a fixed load because it isn't purely resistive.
But 433.3.1 (ii) does not require a resistive or a fixed load. The qualifier is "not likely to carry overload current". I think a 10A oven on a 16A flex seems to comply?
 
If might, it's because a light bulb can't overload the light cable (got it).
If might not ?

For the oven, isn't it the same principle - sorry am I being daft again?
The chances of a cord from a ceiling rose overloading is negligible even if it is 0.5mm it will happily take 750w. I wouldn't chance this with an oven and I am not convinced this Reg is applicable.
 
Understood.
Does that mean you would only be happy with 6mm flex to match the 6mm circuit?
Edit - Personally I wouldnt use less than 2.5mm for some margin, but I'd been happy up to now that the "last metre" was ok.
 
Last edited:
2.5 was my thinking , just to give itva bit to spare , but the connection unit at the back of the oven will not take it without bending out of shape . so 1.5 it is. The user guide say heat flex must be used as it gets very hot at the rear (I thought it cooked on the inside ). So let's hope the rubbish units it fitts in are heat resistance
 
Understood.
Does that mean you would only be happy with 6mm flex to match the 6mm circuit?
Edit - Personally I wouldnt use less than 2.5mm for some margin, but I'd been happy up to now that the "last metre" was ok.
I would change the breaker if I could not fit a larger cable but that is just me.
 

Reply to Cooker circuit mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
729
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
832
Hi all, I'm getting a 32a induction hob and a 13a oven installed as part of a kitchen refurb. The existing cooker circuit is 6mm protected by a...
Replies
7
Views
2K
I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's...
Replies
43
Views
6K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock