Hi,

Been back in the trade a few years now & a regular lurker here (236 I & II & C, 2391, time served etc, 17th) - I have always managed to track down answers using the search however need some help on this one.

New kitchen install in a 2 bed bungalow involving a board swap to RCBO's as only three circuits (lights, ring & cooker).

2nd fix day went fine, all tests carried out with satisfactory results - cooker hood flicked off & on to check function before leaving - job done.

Call via kitchen company I'm subbing for that RCBO is tripping out when fan speed increased on cooker fault. Go back & double check IR tests (all over 200 MOhms), test RCBO again (X1 19.7 X5 7.8 ramped at 27 mS).

Earth leakage clamped & when fan speed increased see a jump to 70 mA - aha I think faulty cooker hood.

Replacement arrives but fitters call to say same thing happening.

Go back again & found that if I connect hood to short leg of ring back to board it trips - connect it to other longer side of ring it doesn't! So remove all other circuits from board & same thing happens. Then swap over to similar length cooker circuit (2M) & it trips! Connect to short leg via extension lead it doesn't trip. This all after double checking IR etc. Swapped RCBO's , double checked connections in consumer unit.

I have installed numerous kitchens recently & never seen this fault. I realise that the common factor here is the short length of the circuit but can't work out why a common Bosch cooker hood would generate 70mA leakage because of it!

I spoke to Bosch technical who after unhelpfully suggesting removal of the RCBO have asked me to email them & will send an engineer out - just wondering if anyone has any ideas?

Cheers,

Rob
 
Hi,

Well disconnected all other circuits and was testing from a 2M run 2.5 T&E that is the first leg of the ring to the socket for the hood - even replaced this piece of twin (even though previous tested fine) & replaced single socket. Done the same again with the socket on the CCU with only the cooker connected in board. Tripped both times.

I didn't wire the hood directly into the RCBO as moulded plug.

When connected via extension lead or longer side of ring the fan operates correctly with an EL of 1.58 mA - the whole installation between 4-6mA total.

Cheers
 
Have you tried IR testing the cooker hood? maybe at 250V. It certainly sounds like the cooker hood fan is vibrating against an earthed part at speed, it may be a design fault that is not enough to cause problems in factory testing.
possibly there is enough capacitance in a long length of cable to mitigate the effect of a transient earth leakage fault.
 
Clamped the fan CPC via a stripped extension lead & got same readings - fine when connected to a longer circuit but spikes when fan speed increased on short leg.
 
Hi,

Well disconnected all other circuits and was testing from a 2M run 2.5 T&E that is the first leg of the ring to the socket for the hood - even replaced this piece of twin (even though previous tested fine) & replaced single socket. Done the same again with the socket on the CCU with only the cooker connected in board. Tripped both times.

I didn't wire the hood directly into the RCBO as moulded plug.

When connected via extension lead or longer side of ring the fan operates correctly with an EL of 1.58 mA - the whole installation between 4-6mA total.

Cheers

Thats a bit of a clue where to look!
 
@Richard - was thinking along those lines though I'm not aware of the method to prove this theory - ring circuit tests were r1 0.63 rn 0.57 & r2 0.97 - average 2 bed bungalow so around 80 square meters.

Trouble is I know when the Bosch engy comes out he will say it works on one socket so must be 'lectrics'!
 
MFT calibrated - EL clamp meter six months old. RCBO's ramp tested (25mA -27mA) Even though RCBO's were new swapped for new ones.

Murdoch - I'm looking believe me but trying to understand the science behind it.
 
MFT calibrated - EL clamp meter six months old. RCBO's ramp tested (25mA -27mA) Even though RCBO's were new swapped for new ones.

Murdoch - I'm looking believe me but trying to understand the science behind it.

Mate, of the leakage is low on 1 leg and an extension, but high on the other............
 
I think you have proved the theory quite well with your testing!!:smile5:
Put a nice tightly wound coil of cable behind the socket, problem solved, though possibly causing other problems!:sick:

80m of ring on a 2 bed bungalow sounds quite high really, and if you are testing on a 2m length then on a 78m length there is a major difference. Though the extension lead is a smaller change, but possibly higher resistance joints.
The only other thought would be a loose connection arcing somewhere, but with all the changes you have made this sounds unlikely.

Take all the covers off the cooker hood and put tape around any metal where the motor /fan rotates and see if the tape gets scraped when it runs.


@Richard - was thinking along those lines though I'm not aware of the method to prove this theory - ring circuit tests were r1 0.63 rn 0.57 & r2 0.97 - average 2 bed bungalow so around 80 square meters.

Trouble is I know when the Bosch engy comes out he will say it works on one socket so must be 'lectrics'!
 
yeah, I know mate. So as above replaced short leg 2M with IR tests of > 900 Meg - no other circuits connected in board.

Duplicated fault on cooker ciruit with similar length.

So if the longer leg is absorbing 70mA it doesn't compare with other faults I have dealt with such as leakage on a long ring from garden supply?

Appreciate the help & will atke it on the chin if i am missing the obvious!
 
@Richard

Yeah, pretty straightforward now at home - straight 2M run to board = trip, longer run = no trip.

Would open hood up but will leave it I think until Bosch have had a look.

These faults are sent to test us lol.
 
if the longer leg is absorbing 70mA

I don't buy this. A longer cable won't make 70mA of leakage 'disappear', that's enough to run a 15W lamp. If the leakage from the hood were from L-E then it's going into one of two cores at almost the same potential - the leakage added by the cable's capacitance L-CPC will be hundreds of times more than that removed by the capacitance N-CPC. In any case, when the long and short legs are both connected the RCBO wouldn't trip.

Much more inclined to think it's an N-E fault. Then with the short cable it's much lower resistance and diverts more current. In that case the 70mA is probably quite arbitrary and you will tend to get different numbers with different loads on elsewhere.

Suppose there is a stock fault on the hoods that causes N-E fault on high speed? Have you tested the hood leakage on high speed when isolated from the outside world, e.g. PAT with it sat on the worktop?
 
I don't buy this. A longer cable won't make 70mA of leakage 'disappear', that's enough to run a 15W lamp. If the leakage from the hood were from L-E then it's going into one of two cores at almost the same potential - the leakage added by the cable's capacitance L-CPC will be hundreds of times more than that removed by the capacitance N-CPC. In any case, when the long and short legs are both connected the RCBO wouldn't trip.

Much more inclined to think it's an N-E fault. Then with the short cable it's much lower resistance and diverts more current. In that case the 70mA is probably quite arbitrary and you will tend to get different numbers with different loads on elsewhere.

Suppose there is a stock fault on the hoods that causes N-E fault on high speed? Have you tested the hood leakage on high speed when isolated from the outside world, e.g. PAT with it sat on the worktop?

I was thinking it was a short duration fault (<10ms) as the motor rotated that could be just "smoothed" enough on a long cable rather than a short one, though as you say it should not then happen on the fully connected ring.
However I would agree with the NE fault, but this would be dependent on current drawn and should have shown up on running a kettle, etc. unless it was only present at high fan speed.
 
Last edited:

Reply to Cooker hood tripping RCBO - head scratcher in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
830
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
664
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
408
I will start with apologies, as I have not thought this through very much (at all) yet and have just sat down with a beer.... meaning I thought...
Replies
3
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
757

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock