Discuss Cooker installation first time in the UK Electrical Forum area at ElectriciansForums.net

J

James has

Hello just wondering if this is correct its all working fine just want to double check


DSC_0718.JPG
 
No. You will have basic insulation visible outside of the enclosure. You should be clamping the sheath. You should be measuring and recording the Zs and rcd trip times in order to confirm compliance (safety).
 
ok i will correct that but are they in the right order ?

That's difficult to tell from here. The connection unit appears to be marked right to left, L, E, N. It appears you may have the connections incorrect, without being able to see the colour markings of the 'supply cable', which appears to be recent colours?

I would recommend you employ an electrician.
 
Don't know about anyone else, but I can't see two conductors in the earth connection.
 

Reply to Cooker installation first time in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
664
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
807
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
884
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
573

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock