Discuss Cooker outlet plate converted to double socket in the UK Electrical Forum area at ElectriciansForums.net

markco

-
Reaction score
17
Hi everyone found this today cooker outlet converted to a double socket which the cooker is plugged into it then a extension lead plugged into other socket which runs the gas hob ignition and garden sockets and garden light's all on 33amp mcb with 6mm from board to cooker then 1.5mm to outside socket then 2.5mm armoured cable split into two to run sockets and lighting any thoughts on this
 
Hi everyone found this today cooker outlet converted to a double socket which the cooker is plugged into it then a extension lead plugged into other socket which runs the gas hob ignition and garden sockets and garden light's all on 33amp mcb with 6mm from board to cooker then 1.5mm to outside socket then 2.5mm armoured cable split into two to run sockets and lighting any thoughts on this
Yes, where did they get the 33Amp CB and where did they stable their horses whilst doing the wiring, and how do they sleep at night?
 
Hi everyone found this today cooker outlet converted to a double socket which the cooker is plugged into it then a extension lead plugged into other socket which runs the gas hob ignition and garden sockets and garden light's all on 33amp mcb with 6mm from board to cooker then 1.5mm to outside socket then 2.5mm armoured cable split into two to run sockets and lighting any thoughts on this

Not a great set up. This should be split up and done properly. Please get an electrician to check it
 
You make sense of that, sounds like a cooker control unit has been changed to a two gang socket with all this ancillary stuff plugged into it.
 
Sorry mis type 32amp and the truth is the house belonged to a electrician who did the works himself got called to check why it was tripping rcd from new owners
 
Are the SWA radials hard wired into this double socket or are they coming of the extension?

As far as I see it nothing wrong with the set up. A bit weird agree, but ok.

Only the SWA would be a concern if it's hard wired.
 
Hi everyone found this today cooker outlet converted to a double socket which the cooker is plugged into it then a extension lead plugged into other socket which runs the gas hob ignition and garden sockets and garden light's all on 33amp mcb with 6mm from board to cooker then 1.5mm to outside socket then 2.5mm armoured cable split into two to run sockets and lighting any thoughts on this
I can't honestly see any issue on the face of it. The fixed wiring is one double socket protected by a 32a mcb with 6mm cable. No issue there at all unless the cable is 200m long.
Then there are two things plugged in, outside the scope of fixed wiring, and although dodgy sounds, the latter setup must be protected by a max 13A fuse. The load doesn't sound like it would overload the fuse, garden lighting and a socket, no kettles involved. Or heaters. Although someone might plug in some ir patio heaters perhaps.
So it all depends on the workmanship really.
 
Are the SWA radials hard wired into this double socket or are they coming of the extension?

As far as I see it nothing wrong with the set up. A bit weird agree, but ok.

Only the SWA would be a concern if it's hard wired.
somehow i can't envisage SWA being wired into a 1363 plug. hang on. seen it once. 2.5mm SWA connected into a RCD plug, installed by the company that installed the hot tub. armour wrapped in green/yellow insulation tape. class installation.:(:(:(.
 
somehow i can't envisage SWA being wired into a 1363 plug. hang on. seen it once. 2.5mm SWA connected into a RCD plug, installed by the company that installed the hot tub. armour wrapped in green/yellow insulation tape. class installation.:(:(:(.

Agree to a point. There are lots of things I cannot envision, but they exist all the same.

I've seen SWA terminated into a j/b then a flex coming out of j/b to a plug.

As johnduffell states this would be outside the scope of fixed wiring.
 
The two Swa cables are wired into a ip 56 box which is feed from one off the ip rated outside sockets one off the swa runs to any other double ip socket the other runs to a ip light switch the tripping caused by water in one of the boxes no gasket on it and no ip glands used
 
My point about the changing the 32A is because - as mentioned elsewhere on the forum - a normal domestic white double 13A socket is rated at 20A across the 2 outlets.
 
My point about the changing the 32A is because - as mentioned elsewhere on the forum - a normal domestic white double 13A socket is rated at 20A across the 2 outlets.
yes, but the 32A MCB is to protect the 6mm cable ,not the socket or whatever is plugged in.
 
The 32A MCB is to protect the 6mm cable and the CCU - The equipment the circuit was originally designed for.

Fitting a double socket onto a cooker circuit is a botch up when other solutions could have been used.
The OP may want to reinstate an oven that requires more than 13A...

Just checked the OP.... It is a cooker plugged into the socket? why not just leave it connected to the CCU?
 
somehow i can't envisage SWA being wired into a 1363 plug. hang on. seen it once. 2.5mm SWA connected into a RCD plug, installed by the company that installed the hot tub. armour wrapped in green/yellow insulation tape. class installation.:(:(:(.
SWA in a plug, how could there be a problem:praying::fire::speaknoevil::seenoevil::hearnoevil:, just ensure you use the right fuse:openmouth::openmouth::openmouth:!
SWA in plug.JPG
 
Fitting a double socket onto a cooker circuit is a botch up when other solutions could have been used.
I guess you agree it meets regs but you don't like that it is not what you'd fit if starting from scratch? Or that the original ccu backbox is reused?
Would it be ok if it were 32A then the double socket, but a second double socket were added elsewhere on the circuit? Or if the circuit was cut short and a double socket were added somewhere near the cu instead?
 
The 32A MCB is to protect the 6mm cable and the CCU - The equipment the circuit was originally designed for.

Fitting a double socket onto a cooker circuit is a botch up when other solutions could have been used.
The OP may want to reinstate an oven that requires more than 13A...

Just checked the OP.... It is a cooker plugged into the socket? why not just leave it connected to the CCU?
Changing a low level cooker connection point to a double socket is a solution I have frequently used for a single oven (<2kw) and gas hob setup where a 6.0mm 32a circuit previously fed a cooker.
The above sort of illogical nonsense is spouted by the same sort of people who faint at the sight of a neutral in a switch and at a shed with an 'exported earth'.
 
The 32A MCB is to protect the 6mm cable and the CCU - The equipment the circuit was originally designed for.

How do you know that? I expect the house was wired long before a cooker even appeared in it, the 32 MCB is there to protect the cable from melting and burning the house down, for all we know the cooker connected to the supply could be a 3 KW oven, so why a 32 amp then?
 
This install does make the fault finding easy - unplug extension lead and this separates 6mm to double socket from all of the ‘unorthodox but accepted’ wiring to the outdoors circuits. Tripping stops = explore further - perhaps all installs could be designed like this!
I’m only kidding - it’s Saturday have another Flat white!
 
Changing a low level cooker connection point to a double socket is a solution I have frequently used for a single oven (<2kw) and gas hob setup where a 6.0mm 32a circuit previously fed a cooker.
The above sort of illogical nonsense is spouted by the same sort of people who faint at the sight of a neutral in a switch and at a shed with an 'exported earth'.
The only thing I wouldn't like about it is if the box was mounted vertically...…..and the d socket 90 degrees out.;)..….break every reg going, would that:rolleyes:
 

Reply to Cooker outlet plate converted to double socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
408
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
276
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
682
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock