    Hi testing today and my colleague came out with c50s are a code 2 from now on ,have i missed a post or publication saying this thanks
     
  2. Taylortwocities
    Online

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    C50 is a valid MCB. The only things that might make it a C2 could be if the EFLI is out of range, or that the cable(s) connected to it are not good for an Ib of 50amps.

    A deviation on a report should give the regulation number that has been breached. Which one did he/she quote?
     
    • Agree Agree x 1
  3. IAN WARREN
    Offline

    IAN WARREN New EF Member

    Location:
    Pontypridd CF373AY
    Thanks he said due to the tripping times there out dated
     
    • Disagree Disagree x 1
  4. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    C50s are the name of the breaker from Crabtree and doesn't relate to the breaker design current of 50 amp.
     
    • Agree Agree x 1
  5. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    What type is it?
    Type 2 or type 3 and the rated current of the mcb or do you actually mean it's a 50 amp c type mcb?
     
  6. spinlondon
    Online

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    Is this guy NICEIC?
    Think they like to condem anything that isn't in the current big book.
     
    • Agree Agree x 2
    • Funny Funny x 1
    • Dumb Dumb x 1
  7. Andy78
    Online

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    Utter ********.
    C50 range was produced to BS3871. Exact Zs values for all types of BS3871 breakers can be found in the back of GN3. As long as they meet these values they should meet the times for disconnection.
     
  8. westward10
    Offline

    westward10 Please don't bore me with your life story. Electrician's Arms

    Location:
    Northamptonshire
    A C50 is either a 3871 type 2 or 3871 type C (yes) there is no type 3. You need to check the side of each breaker if there is nothing indicating a type then assume 3871 type C but some actually state 3871 type 2 or 3871 type C. New versions which were still being made up to recently will be 60898 type C and is written on them. The colour of the writing does not indicate its type but it's ka rating which off the top of my head I cannot recall. This information will be confirmed by Crabtree and they are perfectly safe for continued use. Ignore where it states Part 1 on the side this is not a type but it's compliance with BS3871 Part 1.
     
  9. westward10
    Offline

    westward10 Please don't bore me with your life story. Electrician's Arms

    Location:
    Northamptonshire
    Your colleague should not be carrying out EICRs if he quotes this advice.
     
    • Agree Agree x 2
  10. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Think white colours were 3ka rated and yellow were 4.5 ka rated don't know 100%, if anyone can confirm?
     
  11. westward10
    Offline

    westward10 Please don't bore me with your life story. Electrician's Arms

    Location:
    Northamptonshire
    Those figures sound familiar I know the yellow was the latter and higher.
     
    • Agree Agree x 1
  12. Risteard
    Offline

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    There is no requirement to quote the Regulation number.
     
    • Agree Agree x 2
    • Dumb Dumb x 1
  13. spinlondon
    Online

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    No requirement for the report to be legible.
     
    • Dumb Dumb x 1
  14. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    But without reference to a regulation how can it be recorded as an observation on an eicr?
     
    • Agree Agree x 2
  15. Risteard
    Offline

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Didn't say I agreed with it but it is a fact that the proposal to require the Regulation breached to be recorded against the Observation was rejected when the final draft of BS7671 was published.
     
    • Like Like x 1
Loading...
Similar Threads - Crabtree code Forum Date
crabtree c50 3 phase mcb Electrical Forum Jul 11, 2017
Converting Crabtree Starbreaker Electrical Forum Mar 12, 2017
Crabtree Grid Switch new vs old Electrical Forum Feb 14, 2017
Crabtree 50a pullswitch...chrome Electrical Forum Nov 13, 2016
Crabtree polestar Electrical Forum Nov 7, 2016
Crabtree Starbreaker M6 MCB BS3871 RCBO replacement? Electrical Tools and Products Oct 4, 2016

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job