Discuss CRISPEIR - To Remember the sequence of tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

A

Ashley2

Has anyone heard of this:

C: Continuity of protective conductors, including main & supplementary bonding
R: Ring final circuit conductors continuity
I: Insulation Resistance
S: SELV, PELV or by electrical protection
P: Polarity
E: Earth electrode resistance
I: Impedence, (Zs & Ze) & Pfc
R: RCDs & Functional testing

As a form for remembering the sequence of tests, what do you think. (Pfc is put with Zs/Ze only in order to remember the sequence). Does it make sense & is it appropriate?
 
Thanks for letting me know Lenny. I haven't seen CRIPPLER in GN3 (Green cover).

With CRISPEIR, this follows the sequence as set out in GN3: 2.7.4: Sequence of tests.

Would appreciate full details of CRIPPLER, & your opinion of CRISPEIR (bearing in mind it is for remembering the sequence of tests).
 
I only know the CRIPPLER

C ontinuity of cpc and bonding conductors
R ing cont'
I .R test
P olarity DEAD test
P olarity LIVE test
L oop impedance test, Ze and Zs
E arth fault and PSC fault current
R cd and other functinal tests
 
I only know the CRIPPLER

C ontinuity of cpc and bonding conductors
R ing cont'
I .R test
P olarity DEAD test
P olarity LIVE test
L oop impedance test, Ze and Zs
E arth fault and PSC fault current
R cd and other functinal tests

Fresh out of college and this is what we was taught
 
I think i'll stick with "CRIPPLER" until some young dude from IET'S HR department decides it breaches their discrimination policy....then again,i still use words like wireless,urchin and tyro.
 
Although CRIPPLER doesn't seem to ring true the the sequence as it is given - the sequence includes many tests that are not in your everyday I&T.

All the assessments with C&G including the questions in the 2391's are satisfied if CRIPPLER is used.
 
I would have thought protection by SELV, PELV or by electrical separation would have been part & parcel of the tests that are integral to testing, especially as they apply to special locations such as Baths/showers, swimming pools, saunas, & irrespective of the voltage, Ref Chap 41.
 

Reply to CRISPEIR - To Remember the sequence of tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
663
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
803
Evening all, Recently started working for a company carrying out electrical installations - I've found a job today that didn't have any bonding...
Replies
8
Views
2K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock