i have been asked to install a rewire into a house including a new consumer unit. the customer would also like power run to a shed which i have never done before. my instinct says i would need swa as he doesnt want high or underground cable. it is only to supply a shed c.u for sockets and lights so am intrigued to find out my options from you professionals! any advice appreciated
 
i have been asked to install a rewire into a house including a new consumer unit. the customer would also like power run to a shed which i have never done before. my instinct says i would need swa as he doesnt want high or underground cable. it is only to supply a shed c.u for sockets and lights so am intrigued to find out my options from you professionals! any advice appreciated
 
and how many points will be in this shed?.....whats the intended use?.....whats the earthing arrangements here?....any water or gas extrainious conductive parts in this shed?.......check both earthing and bonding arrangements here first and upgrade/replace to the 17th edition standard before doing any work here....how longs the run from the origin of supply for this shed and the shed itself?....
 
3 sockets, 2 lights, man shed so prob radio and power tools, no water or gas but will double check. 10m run from supply to shed and 3m l, 2m h, 1m d shed.
 
so i would suggest a 16A MCB (for the outlets).....and a 6A MCB for lighting......need to know the earthing arrangements though mate as this will determine whether an s type RCD is required (for discrimination purposes)......
 
Oh lord... on your marks.....

But seriously. nothing to be afraid of. Plenty of guides around.. Check with your scheme provider and see what they advise..
 
my instinct says i would need swa as he doesnt want high or underground cable.
TBH I would bury SWA, out of sight, out of mind. As you're doing a complete rewire, run T+E under the floor space if you can, adaptable box onto SWA and off to the shed you go. Buried looks a hell of a lot tidier, if not, is there anything for you to clip the cable to?
 
i have been asked to install a rewire into a house including a new consumer unit. the customer would also like power run to a shed which i have never done before. my instinct says i would need swa as he doesnt want high or underground cable. it is only to supply a shed c.u for sockets and lights so am intrigued to find out my options from you professionals! any advice appreciated

The key word I`m afraid is professionals. I take it from this that you dont consider yourself a professional which begs the question should you be undertaking any of the work in the first place?
 

Reply to decision to make in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
859
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
818
Hello fellow professionals, I'm currently facing a challenging scenario that involves the integration of solar photovoltaic (PV) systems on roofs...
Replies
1
Views
327
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock