Under reg.311.1 the maximum demand shall be determined, however by the nature of what they do, there is often no room for diversity in an AC installation, especially the units that heat in addition to cool. On a cold morning all the units go on as people arrive for work. On a hot summer afternoon, everyone wants to be cool, so again, all the units are on simultaneously. Not much room for diversity there...
 
Under reg.311.1 the maximum demand shall be determined, however by the nature of what they do, there is often no room for diversity in an AC installation, especially the units that heat in addition to cool. On a cold morning all the units go on as people arrive for work. On a hot summer afternoon, everyone wants to be cool, so again, all the units are on simultaneously. Not much room for diversity there...
Thank you. That is what I have gone with.
 
When calculating diversity, the recommended values are only advice. Sometimes it's necessary to increase/decrease their values based on the circumstances. If you're unsure, you can't go wrong with 100%.
 

Reply to Diversity on AC condensers in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi there currently doing some diversity calcs for college work and had a query about what diversity factor to apply to a 16A 3 phase commercial...
Replies
3
Views
1K
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
385
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
996
Hi everyone, a landlord is converting a house into two flats and wants a separate consumer unit for both flats upstairs and downstairs. He also...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock