mrnine324

DIY
Reaction score
0
Hello all, I'm an amateur DIY home-owner that recently moved into an apartment for a 6-month military assignment and these maintenance workers here are clearly incompetent and just do the bare minimum at EVERYTHING, including electrical work.

So I moved in here and my dryer had the 3-prong cord, but the apartment outlet is the 4-prong with that L-shaped neutral, so I go and buy a 4-prong cord at lowes to change on the dryer. Well, I plug it into the outlet and no power to the dryer. Checked circuit breaker, checked my dryer wiring, and then resorted to checking outlet with multimeter. The two HOT's are good with 220ish volts, ground to each hot is proper 120vish, but no power from neutral. So, I take the outlet cover off and discover they wired the white wire from the wall to the ground terminal, and nothing to the neutral terminal. However, I'm not seeing a green or bare metal ground wire coming from the wall. So, I'm not sure what to do here and I certainly don't want to fry my dryer or burn the place down. Could I temporarily install a 3-prong outlet with the white/red/black wires coming from the wall, using white as ground? That sounds bad in my head but it makes me wonder if they wired the white as ground in the circuit panel. Again, this is an apartment so I don't want to get too heavy into fixing their wiring inaccuracies, I just want to be able to use my dryer for the next 6 months and then I'll move back home and restore it to the way it was when I moved into this apartment. Thanks for your help in advance.
276160253_10159643101927567_6015704525261373834_n.jpg
 
Last edited by a moderator:
It looks like the original cable had no ground so someone has repurposed the white. @Megawatt one of our US based members will be able to advise a way forward.
 
Hello all, I'm an amateur DIY home-owner that recently moved into an apartment for a 6-month military assignment and these maintenance workers here are clearly incompetent and just do the bare minimum at EVERYTHING, including electrical work.

So I moved in here and my dryer had the 3-prong cord, but the apartment outlet is the 4-prong with that L-shaped neutral, so I go and buy a 4-prong cord at lowes to change on the dryer. Well, I plug it into the outlet and no power to the dryer. Checked circuit breaker, checked my dryer wiring, and then resorted to checking outlet with multimeter. The two HOT's are good with 220ish volts, ground to each hot is proper 120vish, but no power from neutral. So, I take the outlet cover off and discover they wired the white wire from the wall to the ground terminal, and nothing to the neutral terminal. However, I'm not seeing a green or bare metal ground wire coming from the wall. So, I'm not sure what to do here and I certainly don't want to fry my dryer or burn the place down. Could I temporarily install a 3-prong outlet with the white/red/black wires coming from the wall, using white as ground? That sounds bad in my head but it makes me wonder if they wired the white as ground in the circuit panel. Again, this is an apartment so I don't want to get too heavy into fixing their wiring inaccuracies, I just want to be able to use my dryer for the next 6 months and then I'll move back home and restore it to the way it was when I moved into this apartment. Thanks for your help in advance.View attachment 96179
We still have dryers wired with 3 wires unfortunately. Since it’s an apartment and your just staying there temporarily get a 3 prong cord for the dryer. By code if you work on a dryer you are supposed to bring in up to today’s standards but that’s not your problem. It should work fine with no problems. Good luck my friend and thank you for your service. 🇺🇸🇬🇧
 
Hello all, I'm an amateur DIY home-owner that recently moved into an apartment for a 6-month military assignment and these maintenance workers here are clearly incompetent and just do the bare minimum at EVERYTHING, including electrical work.

So I moved in here and my dryer had the 3-prong cord, but the apartment outlet is the 4-prong with that L-shaped neutral, so I go and buy a 4-prong cord at lowes to change on the dryer. Well, I plug it into the outlet and no power to the dryer. Checked circuit breaker, checked my dryer wiring, and then resorted to checking outlet with multimeter. The two HOT's are good with 220ish volts, ground to each hot is proper 120vish, but no power from neutral. So, I take the outlet cover off and discover they wired the white wire from the wall to the ground terminal, and nothing to the neutral terminal. However, I'm not seeing a green or bare metal ground wire coming from the wall. So, I'm not sure what to do here and I certainly don't want to fry my dryer or burn the place down. Could I temporarily install a 3-prong outlet with the white/red/black wires coming from the wall, using white as ground? That sounds bad in my head but it makes me wonder if they wired the white as ground in the circuit panel. Again, this is an apartment so I don't want to get too heavy into fixing their wiring inaccuracies, I just want to be able to use my dryer for the next 6 months and then I'll move back home and restore it to the way it was when I moved into this apartment. Thanks for your help in advance.View attachment 96179
I’m sorry but I misread your post. That looks like a 3 prong outlet, could the maintenance people have installed a 4 prong cover over a 3 prong outlet just for fooling an inspector. With the power off and leave the cover off see if the 3 prong cord plugs into the outlet. Maybe I’m brain dead and my eyes are getting bad but it appears to be a 3 prong outlet. Sorry
 
Hello all, I'm an amateur DIY home-owner that recently moved into an apartment for a 6-month military assignment and these maintenance workers here are clearly incompetent and just do the bare minimum at EVERYTHING, including electrical work.

So I moved in here and my dryer had the 3-prong cord, but the apartment outlet is the 4-prong with that L-shaped neutral, so I go and buy a 4-prong cord at lowes to change on the dryer. Well, I plug it into the outlet and no power to the dryer. Checked circuit breaker, checked my dryer wiring, and then resorted to checking outlet with multimeter. The two HOT's are good with 220ish volts, ground to each hot is proper 120vish, but no power from neutral. So, I take the outlet cover off and discover they wired the white wire from the wall to the ground terminal, and nothing to the neutral terminal. However, I'm not seeing a green or bare metal ground wire coming from the wall. So, I'm not sure what to do here and I certainly don't want to fry my dryer or burn the place down. Could I temporarily install a 3-prong outlet with the white/red/black wires coming from the wall, using white as ground? That sounds bad in my head but it makes me wonder if they wired the white as ground in the circuit panel. Again, this is an apartment so I don't want to get too heavy into fixing their wiring inaccuracies, I just want to be able to use my dryer for the next 6 months and then I'll move back home and restore it to the way it was when I moved into this apartment. Thanks for your help in advance.View attachment 96179
After studying the picture turn off the power and move the white wire over to the screw on the right. It will work then. Sorry but it’s been a long hard day
 
After studying the picture turn off the power and move the white wire over to the screw on the right. It will work then. Sorry but it’s been a long hard day
Thank you. My only concern, is that if I do that, moving the white wire to the pin to the right (which connected behind to the neutral plug), then I would lose ground, correct? Wouldn't I be asking for problems without a ground? But, I do see your point about how they probably just put a four prong outlet on three wires to fool the city/state inspectors. If I test the wires with a multimeter, how can I make sure that white wire is ground and not neutral, or vice versa? It's very possible they put the white wire as ground at the circuit breaker box, I just can't see behind there to trace that. But, what if it's in fact neutral? I just don't want to 1) blow up my dryer, or 2) cause a fire. Thank you.
 
Thank you. My only concern, is that if I do that, moving the white wire to the pin to the right (which connected behind to the neutral plug), then I would lose ground, correct? Wouldn't I be asking for problems without a ground? But, I do see your point about how they probably just put a four prong outlet on three wires to fool the city/state inspectors. If I test the wires with a multimeter, how can I make sure that white wire is ground and not neutral, or vice versa? It's very possible they put the white wire as ground at the circuit breaker box, I just can't see behind there to trace that. But, what if it's in fact neutral? I just don't want to 1) blow up my dryer, or 2) cause a fire. Thank you.
Put your meter on ac voltage and check hot to neutral and you should get around 120 to neutral
 
It looks like the receptacle is miswired, it never should have been changed to 4 wire, as there is no grounding conductor and doofy the wannabe electrician connected the neutral to the grounding terminal, a 3 wire dryer cap is a dual voltage non grounding device, the landlord should have it rewired but a lot of them are slumlords, but the 3 wire is permitted in existing installations and that is another way to fix it, by changing the receptacle, I am no fan of the 3 wire dryer receptacles as they should have been canned 40 years prior, they were prohibited in new installations with the adoption of the 1996 NEC.

BTW 220V is a prewar voltage, around WWII it was 115/230V, before it changed to the present standard of 120/240V
 

Reply to DIY - Apartment wrong 4-prong 220v wiring, how to fix myself? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
559
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
352
Looking for advice for the following: Bosch Induction cooktop model NIT8669SUC ) came with 3 bare wires (Black, Red, Green) but my wall has a 4...
Replies
0
Views
730
I have an existing but unused 50A disconnect on the side of the house. It had been connected to an AC unit that got replaced. It has just 3...
Replies
4
Views
953
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
771

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock