I am at a standstill installing the new cooktop until I can determine if the new one works with the present wiring/breaker. (I am keeping in mind the contractor may not have installed the right wiring/breaker for the original (current) cooktop either, so tell me if you determine this is the case.)
Photo one is my current house wiring to the original cooktop. The breaker to this is a 30 amp, double breaker. Photo two is the original cooktop appliance wiring. In the junction box, the black was wired to black, the red to white, and the bare grounds together. The new cooktop instructions in the booklet are confusing regarding what wiring to connect.
Photo three is a closeup of the writing on the black wire of the original cooktop appliance.
Photo four is the wiring of the new cooktop I wish to install. Photos five and six are electrical requirements from the instruction booklet of the new cooktop. The seventh photo is the sticker off the new cooktop that has information needed according to the instructions in photos five and six.
Photos eight, nine, and ten show instruction booklet wiring instructions and warnings.
As best as I can figure it out, the new cooktop wants a 40 amp breaker. This means it wants a heavier wire too. If so, I have to replace the wire and the breaker in order to install the new cooktop. Please advise on this.
I am in the USA.
Photo one is my current house wiring to the original cooktop. The breaker to this is a 30 amp, double breaker. Photo two is the original cooktop appliance wiring. In the junction box, the black was wired to black, the red to white, and the bare grounds together. The new cooktop instructions in the booklet are confusing regarding what wiring to connect.
Photo three is a closeup of the writing on the black wire of the original cooktop appliance.
Photo four is the wiring of the new cooktop I wish to install. Photos five and six are electrical requirements from the instruction booklet of the new cooktop. The seventh photo is the sticker off the new cooktop that has information needed according to the instructions in photos five and six.
Photos eight, nine, and ten show instruction booklet wiring instructions and warnings.
As best as I can figure it out, the new cooktop wants a 40 amp breaker. This means it wants a heavier wire too. If so, I have to replace the wire and the breaker in order to install the new cooktop. Please advise on this.
I am in the USA.
Attachments
-
current household wiring to cooktop.jpg242.4 KB · Views: 22
-
new cooktop insturstions showing wiring.jpg996.8 KB · Views: 16
-
new cooktop more instrustions 3.jpg769.6 KB · Views: 16
-
new cooktop more instructions 4.jpg63.8 KB · Views: 19
-
new cooktop sticker.jpg162.2 KB · Views: 15
-
cooktop instructions 1.jpg1.1 MB · Views: 22
-
cooktop instructions 2.jpg1.1 MB · Views: 15
-
new cooktop wiring.jpg252.3 KB · Views: 15
-
current cooktop closeup of what is written on black wire.jpg269.5 KB · Views: 10
-
current cooktop wiring.jpg249.2 KB · Views: 13