Discuss DNO earthing arrangement in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
A big Hi to all on here, please be gentle with me it my fist time !!
It's only a quick one but do the DNO have a legal requirement to supply suitable earthing at the point of origin of metered supply.
many thanks advance
 
No they are not legally bound to supply an earth but if they do then they must maintain it.
 
I would agree with the above.
In general they will supply an earth but it is not absolutely required.

From the ESQCR regulations:
Unless he can reasonably conclude that it is inappropriate for reasons of safety, a distributor shall, when providing a new connection at low voltage, make available his supply neutral conductor or, if appropriate, the protective conductor of his network for connection to the protective conductor of the consumer’s installation. In this regulation the expression “new connection” means the first electric line, or the replacement of an existing electric line, to one or more consumer’s installations.
 
Why do dno provide tncs conection when the new connection is soley for a static caravan park.. Too many times i see this then distributed around park which i know is ok as distribution but then straight to hook up box socket which is agginst esqcr.! Why dont they not provide an earth terminsl forcing the electrical contractor to provide their own earth arrangement and rcd at origin!!
 
The answer probably is,
It is cheap and simple for the DNO to provide TNCS for the site offices and so on, what the customer does with the supply is, well, up to the customer.
 
Cheaper and simpler than providing and maintaining an earth connection.?? Dont agree with that but i dont work for dno! If it wasnt provided it wouldnt be used by people who think they know what there doing
 

Reply to DNO earthing arrangement in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
376
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock