Discuss Do you test the suppliers earth conductor for continuity??? (Initial verification) in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
23
Hi guys,

QUESTION: Do you test the suppliers earth conductor for continuity???

The guidance note 3 2.6.5 refers to regulation 643.2.11 which requires a continuity check be carried out on all protective conductors including: EARTHING CONDUCTOR, CPC's and bonding conductors. I am aware of the bonding conductors and CPC's being tested. But the earthing conductor to be tested? Does this mean that when I have carried out safe isolation, I am supposed to remove the main earthing conductor (from the supplier) from the MET (to remove parallel paths) and carry out a continuity test of this short piece of suppliers earth?

I am currently writing my NVQ inspection and testing unit. I have completed my AM2, and testing units and never come across this test for initial verification, I don't think I've seen it done on any youtube revision videos too.

It would make sense to test it though right? As I was taught you carry out the sequence of test in the order it is in, because the next test always depends on the previous test if that makes sense lol? There would be no point in testing the bonding conductor/ CPC's if there is no suppliers earth right?

Thanks in advance for anyone who can help out!
 
Test the Ze of the incoming earth whilst disconnected from the installation. A live test.
Continuity testing of bonding and cpc's is required, even if there is a problem with the incomer.....for when it is reinstated.
 

Reply to Do you test the suppliers earth conductor for continuity??? (Initial verification) in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
728
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock