Interesting webcast yesterday from NICEIC covering the 3rd Ammendment BS7671, we were aware of nearly all of it.

The one thing that made us sit up though was that in accordance with the regs, they specifically mentioned that the two isolators (and any other switchgear) needed for the PV system - CU location and Inverter, they believe falls under clause 421.1.201 (similar switchgear) and so must be enclosed in a non-combustable (usually considered to me ferrous)) material.

Anyone else thought about this ?

(Little metal rotary isolators, double pole mcbs' / main switches in metal enclosures) ...
 
re: Domestic Installs Meta CU's also = Metal PV Isolators

Look at the definition of switchgear in section 2 of 7671. It includes the words 'main and auxiliary switching equipment'. A single isolator (or for that matter a single upfront rcd) does not meet that definition and so can continue to be in a plastic enclosure. Arguably.
 
re: Domestic Installs Meta CU's also = Metal PV Isolators

The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means those assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671:
‘Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’
An example of a similar switchgear assembly is a three phase distribution board that is intended to be operated by ordinary persons. This would have to have isolation that interrupts the three incoming line conductors and the neutral, rather than just double-pole isolation as mentioned in the above definition.

^The above is written by the IET (wiring matters)^ . If the NICEIC say they "believe" that is falls under 421.1.201 I would say I "believe" it doesn't and carry on as I am.
 
Last edited:
Re: Domestic Installs Meta CU's also = Metal PV Isolators

I was out working and did not listen to it.

There has been some discussion on the IET site in recent weeks, but not conclusive. It really does annoy me that this is another example of where the rules get changed but the people changing them issue little guidance that explains their thinking and intentions so the minutiae of the regulations get debated for months.

Personally I think I am a fan of plastic enclosures in a domestic situation for isolators. Metal enclosures means they must be earthed. That is one more point of failure. I currrently do not run an earth to a dc isolator unless I am running swa to it.
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

Interesting webcast yesterday from NICEIC covering the 3rd Ammendment BS7671, we were aware of nearly all of it.

The one thing that made us sit up though was that in accordance with the regs, they specifically mentioned that the two isolators (and any other switchgear) needed for the PV system - CU location and Inverter, they believe falls under clause 421.1.201 (similar switchgear) and so must be enclosed in a non-combustable (usually considered to me ferrous)) material.

Anyone else thought about this ?

(Little metal rotary isolators, double pole mcbs' / main switches in metal enclosures) ...
it doesn't say 'similar switchgear' it says 'similar switchgear assemblies'

A consumer unit is an assembly of multiple switch gear units, an individual isolator is a single unit of switch gear, not an assembly of multiple units.

therefore NIC are wrong.
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

it doesn't say 'similar switchgear' it says 'similar switchgear assemblies'

A consumer unit is an assembly of multiple switch gear units, an individual isolator is a single unit of switch gear, not an assembly of multiple units.

therefore NIC are wrong again.

edited post for you Lol.
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

A consumer unit is an assembly of multiple switch gear units, an individual isolator is a single unit of switch gear, not an assembly of multiple units.

Hi Gavin, they are also insistent it applies to an RCD protected TT system, where the RCD is on the main incoming as a stand alone unit. By your logic, it shouldn't apply to that either..

I think the PV scenario it's a misinterpretation, however we have fixed 3rd party installs with molten internals of rotary isolators because the connection wasn't properly tightened, which is precisely the reason for the non-combustible CU requirement.
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

Hi Gavin, they are also insistent it applies to an RCD protected TT system, where the RCD is on the main incoming as a stand alone unit. By your logic, it shouldn't apply to that either..

I think the PV scenario it's a misinterpretation, however we have fixed 3rd party installs with molten internals of rotary isolators because the connection wasn't properly tightened, which is precisely the reason for the non-combustible CU requirement.

If you take that logic on the rotary isolator then the same would apply to a double pole switch for an immersion heater....
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

it doesn't say 'similar switchgear' it says 'similar switchgear assemblies'

A consumer unit is an assembly of multiple switch gear units, an individual isolator is a single unit of switch gear, not an assembly of multiple units.

therefore NIC are wrong.

It says switchgear assemblies, not assemblies of switchgear. They're different things.
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

If you take that logic on the rotary isolator then the same would apply to a double pole switch for an immersion heater....

That was my argument too.
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

So...
Anyone a member of the IET and care to get some guidance in writing that we can all use?
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

As I read it the new regulation applies to "distribution boards" only as, apart from the non-combustible enclosure part, it also requires compliance with BS EN 61439-3.

So if an "assembly" meets a BS EN other that 61439-3 then it is not relevant to the new regulation.

See http://www.beama.org.uk/asset/7DF1EEE0-F314-452B-81E276BC561F4B89/ for the BEAMA report that is intended to clarify the amendment.

Item 4 in that report says exactly what Lee has been saying and follows that with a list of what they consider to be in and out of scope of the regulation but with the caveat "The above table provides general guidance and is not intended to be an exhaustive list of inclusions and exclusions."

"Photo-Voltaic combiner boxes" are in scope so, in future, these are going to have to be both BS EN 61439-3 compliant and non-combustible.
 
Last edited by a moderator:
Re: Domestic Installs Meta CU's also = Metal PV Isolators

It says switchgear assemblies, not assemblies of switchgear. They're different things.
hmmm it'd seem you're right.

In accordance with EN 60 439-1, Subparagraph2.1.1., a low-voltage switchgear and controlgearassembly is“A combination of one or more low-voltageswitching devices together with associated control,measuring, signalling, protective, regulatingequipment, etc., completely assembled under theresponsibility of the manufacturer with all theinternal electrical and mechanical interconnectionsand structural parts (…).”
http://www.nema7.com/PDF/allen_bradley_guide_switchgear-controlgear_assembly.pdf

Still not convinced that an individual isolator is really classed as being similar switch gear to a consumer unit. It's more similar to a dual pole switch than to a consumer unit - a dual pole fused switch would be more similar to a Consumer Unit due to having the fused protection within it.
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

Possibly in a large domestic system, such as those Worcester has some experience of, perhaps?

you'd need more than 2 inputs into the same MPPT on the inverter, which usually only happens on 20kW+ 3 phase inverters assuming dual trackers.

As earthing the metal enclosure would do bugger all for the safety of it on the DC side, I'd be inclined to stick with insulated enclosures anyway - citing regulation 712.412 as evidence to support that... "protection by the use of class 2 or equivalent insulation shall preferably be adopted on the dc side."
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

Hi folks, had it in writing from the IET themselves that Rotary isolators will need to be housed in metal enclosure!!
 
Re: Domestic Installs Meta CU's also = Metal PV Isolators

Hi folks, had it in writing from the IET themselves that Rotary isolators will need to be housed in metal enclosure!!
Can you forward a copy of your correspondence if possible and post it up, wording and interpretation can be key to such an important point.
 
E-Mail as follows:

Dear Matt,

Thakyou for your query. Richard Townsend, Senior Engineer with the Technical Regulations team has provided the below response

From me: "Would this mean that Rotary Isolators for a PV System,both on the AC and the DC side need to be metal or completely enclosed in a metal Enclosure?"

Richards response: "Yes a rotary isolator is classed as switchgear and therefore would need a metal enclosure, or an alternative isolator would need to used"
 
Hi Matt, could you please pm me the email address as I'd really like to nail them down on that for the DC side at least, as I don't think they've thought that through at all and it contradicts regulation 712.412
 
Interestingly, Napit technical on their forum have taken a different view a few days ago. At least they give a reason for their view. I hope they will not mind if I quote it:

"Regulation 421.1.201 Non-combustible Consumer Units and Similar Assemblies
Q. Would solar PV dedicated consumer units need to be metal?
A. Yes, if fitted in a domestic (household) premises. Regulation 421.1.201 applies to both consumer units and similar switchgear.
Q. Do solar PV rotary isolators have to meet Regulation 421.1.201?
A. Regulation 421.1.201 refers to similar switchgear assemblies complying with BS EN 61439-3, this standard is for low voltage switchgear and control assemblies. Distribution boards intended to be operated by ordinary persons.
The standard isolators used in PV systems fall under a different standard: BS EN 60947-3 Switches, disconnectors and switch-disconnectors. Therefore these isolators are exempt from this regulation."
 
That looks to me like Napit technical understand the new regulations better than the IET, and as I'm with NAPIT I think I'll go with their answer.
 
In my view there is some ambiguity in the answers from both the IET and Napit. Here’s my 2p’s worth.

Let us start with definitions:

Accessory. A device, other than current-using equipment, associated with such equipment or with the wiring of an installation.

Switchgear. An assembly of main and auxiliary switching equipment for operation, regulation, protection or other control of an electrical installation.

And the regulation:
421.1.201. Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS 61439-3 and shall etc………..

The IET asserts ‘a rotary isolator is classed as switchgear’. Why? It meets the definition of accessory above to my mind. To be switchgear it has to have ‘main and auxiliary switching equipment’. A single isolator is not switchgear by definition. Therefore in my view it falls outside ‘similar switchgear assemblies’ phrase in 421.1.201.


Napit I think comes to the right answer, although there is a slight misquote. It is wrong to say, ‘Regulation 421.1.201 refers to similar switchgear assemblies complying with BS EN 61439-3’; it actually says ‘……… shall comply with BS EN 61439-3’. So if it is a ‘similar switchgear assembly’ then it must comply with that BS. Isolators comply with BS EN 60947-3, but if in a consumer unit or forming part of a switchgear assembly then their enclosure must meet BS EN 61439-3, but a single isolator appears to fall outside the 421.1.201 requirement to meet that enclosure BS.

Personally I think I am happy to keep single isolators in plastic enclosures, as well as a REC2s or upfront rcd.
 
Last edited:
I thought we had already gone through all this sometime earlier.

Whether an item is simply "switchgear" or not seems beside the point to me.

It is a question of does the switchgear perform a function similar to that of a consumer unit - e.g. a garage or shower unit.

For any metal enclosure to conform to Amd 3 then it must comply with BS EN 61439-3 and therefore Amd 3 must apply only to assemblies that are capable of falling under the ambit of that standard.

An assembly that complies with any standard other than BS EN 61439-3 automatically does not fall under the Amd 3 reg and therefore does not need to be metal.
 
I had thought of that but there did not seem an 100% clear answer. There is no 7671 definition of main or auxilliary switching but would they meet the definition of an accessory or switchgear. I incline to the former if not 'main and auxilliary switching'.
 
The wording of

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:

(i) have their enclosure manufactured from non-combustible material, or

(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.

NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.

NOTE 2: The implementation date for this regulation is the 1st January 2016, but does not preclude compliance with the regulation prior to that date.

The British Standard; BS EN 61439-3, mentioned in the regulation, is entitled "Low-voltage switchgear and controlgear assemblies; Part 3: Distribution boards intended to be operated by ordinary persons (DBO)"


The key thing is the regulation says that the type of switchgear they are referring to SHALL comply with the above BS, so IF the isolators are covered by the interpretation of: "consumer units and similar switchgear assemblies" then they'll need to be built to comply with the BS, and not the other way round, (if they don't comply with the BS / built to a different BS, then they're not considered "consumer units and similar switchgear assemblies")

So I disagree with WHY napit says it doesn't apply to rotary isolatorsm though do agree with the outcome :)


From Part 2 definitions of Amd3:

Consumer Units: (See below)

Switchgear: An assembly of main and auxilliary swithcing eqipment for operation, regulation, protectionor other control of electrical installations


According to the IET: Consumer units - IET Electrical

Similar switchgear assemblies

The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means those assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671:
Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’

An example of a similar switchgear assembly is a three phase distribution board that is intended to be operated by ordinary persons. This would have to have isolation that interrupts the three incoming line conductors and the neutral, rather than just double-pole isolation as mentioned in the above definition
.

The key thing hear is that we are dealing with Part 3 of the BS, which specifically deals with CU's / DB's

Reading the above, I reckon NICEIC have it wrong, and Napit have it right, though for the wrong reason :)

Qn: Anyone got or seen a copy of BS EN 61439-3:2012 ?
 
My last comment above was in response to a post that has been deleted, so is looking a bit lonely now, but with no way to edit/delete.

For Ted: Rarely do I disagree with you, but to my mind the function question comes after being switchgear in the first place. I do not see how a single isolator (or even multiple isolators) falls within the definition of switchgear or has the characteristics of a consumer unit. I think isolators if not combined with for example rcds or mcbs etc are just 'accessories'.

In response to Worcester's Qn:
The BSI store says currently not available for some reason.
Here is part of it - go past the Danish front cover.
https://webshop.ds.dk/Files/Files/Products/M249414_attachPV.pdf
 
I don't think we are disagreeing (that might be a first!). What I was trying to say was:

If something isn't a consumer unit/switchgear assembly then it is out of scope. But if an assembly is switchgear then it is not automatically in scope - it must also perform the function of a consumer unit.

Can anything not be switchgear, not be a consumer unit and still perform the function of a consumer unit? I don't think so.
 
I agree with that! Perhaps I had been reading things out of order - I have posted sometimes without refreshing so others have got in first which messes up the flow.

I see I am not reading closely enough. My response #33 was in response to Sibert's which has not been deleted but is on a different page in my browser.
 
Last edited:
so we're all agreed on this other than the IET technical rep, who unfortunately would be among the authors of the stuff being discussed.

tbh he's posted on the IET forums before, I wonder if he'd come and defend his position / discuss it on here.
 
Examining the contraindicative position for a moment - i.e. assume that isolators do fall within the requirement of 421.1.201 - then what unit would you actually use?

I see that Wylex make a dual DC/AC isolator in a metal case and their (old, 2013) technical documentation says:

"Factory Built Assemblies BSEN60439-3 when fully assembled" but it is not clear from the context if this applies to all assemblies listed in the leaflet or only to consumer units.

http://storage.electrika.com/manu/man-0150/pdftech/0150-wylex-13-tech.pdf

So unless Wylex produce updated documentation to say that this unit complies with BS EN 61439-3 then you wouldn't be able to use it to comply with Amd 3 anyway.

Does anyone else know of any metal enclosure isolators that may or may not be approved to BS EN 61439-3?
 
Thanks for the link BruceB

This is the IMPORTANT bit from the BS:
Additional definition
3.1.104 Customer distribution board CDB
An integrated assembly, for the control and distribution of electrical energy, principally in a household or similar premise, incorporating manual means of double-pole isolation on the incoming circuit(s), with polarity observed throughout. They are designed for use exclusively with specific protective devices on the outgoing circuits, and type-tested for use when energized through the specified 100 amp fuse. NOTE Generally known in the UK as a Consumer unit.

So I think that both the IET and NICEIC guys according to the LETTER of the regulations are WRONG when relating to rotary isolators (the important words from above are "and distribution" ); if putting in a 'garage' / 'shower' or similar small unit with a main switch and at least one MCB, then it needs to be in a non-combustible enclosure.

If we consider the SPIRIT of the regulations, then see here for the reason for the introduction of non-combustible CU's: (Consumer units - IET Electrical)
Reason for the new regulation

Regulation 421.1.201 was introduced because of reports from fire investigators of a recent trend of increasing numbers of fires involving consumer units having a moulded thermoplastic enclosure

The cause of the fires investigated was almost invariably found to be resistance heating as a result of poor electrical connections due to poor workmanship or lack of maintenance. Examples of such poor workmanship are thought to include:

- failure to tighten neutral conductor connections to the same torque as line conductor connections due to a misconception that neutral conductors carry less current;
-inadvertently taking cable insulation inside the terminal at a connection, resulting in the securing screw or the clamp of the terminal not making proper contact with the conductor;
- failure to check factory installed connections for tightness where required to do so by the manufacturer; and
- tightening connections to an incorrect torque and/or with inappropriate tools.

The crucial importance of checking that all electrical connections are properly made, and of taking remedial action where necessary, should never be forgotten.

Whilst the main cause of fire within plastic consumer unit enclosures is without doubt poor workmanship, other potential causes of fire within plastic consumer unit enclosures are thought to include:

- the type of internal components, such as where terminations have only one securing screw or are of the 'cage clamp' type); and
-where increased heat transfer to the enclosure is caused by the close proximity to an internal item, such as a neutral bar or a conductor terminated at the neutral bar and protruding above it.

Intent of the new regulation

The intent of Regulation 421.1.201 is considered to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames.



Then on the basis that the same poor workmanship could occur on a a rotary isolator, double pole MCB or incoming RCD you can see why IET / NICEIC will send out the message that they wish it to be in a non-combustible enclosure

If you've never seen it, then you should seee the sparks and flames you can get when a short circuited DC cable (for Isc testing) on a small domestic installation is pulled apart - it's just like an arc welder.

HOWEVER, (and this is where the argument falls down) I would hope that MCS registered solar PV installers, the installation being of a specialist nature are particularly aware of the dangers of the above poor workmanship issues and so take particular care to ensure those errors don't occur. Unfortunately we have took often come across badly installed isolators.
 
Gordon, I think the BEAMA document I linked to earlier confirms the "and distribution" point you make and with which I agree, when it lists (albeit non-exhaustively) the "similar assemblies" that it says the new reg applies to.

But even if you want to comply with the spirit of the new regs and install a metal enclosed isolator then where are you going to get one from that is also stated to comply with BS EN 61439-3 by the manufacturer?
 
Now I have had time to read through the copy of EN 61439-3 that Bruce linked to, I would say that it is logically impossible for a simple isolator to pass all the tests specified in the standard for the simple reason that some tests (10.11.5.7.2 and 10.11.5.7.4) require testing of 'final circuit protective device(s)' which, of course, a simple isolator doesn't have.

Any manufacturer who states that their isolator complies with BS EN 61439-3 is not going to be telling the whole truth.
 
IET Forums - PV and BS7671 Amd 3

I understand that PV installers have been receiving conflicting advice from different bodies (IET, NICEIC, NAPIT) regarding the applicability of BS7671 Amd 3 421.1.201 and metal enclosures for AC and DC DP isolation switches, which are a standard part of any domestic PV system.

Some are being told that they must install isolation switches with only metal enclosures and others that it is OK to continue to use the normal plastic housed ones.

The BEAMA guidance document does not specifically list PV DP isolation switches as being 'in scope' in their (non-exhaustive) list of "similar assemblies".

As the new regulation has two parts - namely compliance with BS EN 61439-3 and the requirement for a metal enclosure - I have briefly looked at BS EN 61439-3 and it appears that some of the tests required for manufacturers to complete in order to show compliance with this standard can only be applied to assemblies that contain "final circuit protective device(s)" which are obviously absent from a simple DP switch.

There is also a definition in the standard that assemblies have a rated voltage no higher than 300V AC, which would appear to preclude 1000V DC units.

It would therefore appear to be logically impossible for any manufacturer to state that their isolator switch assemblies are BS EN 61439-3 compliant.

And it would then appear that it would be impossible for any PV installer to obtain any isolation switches that can comply with 421.1.201 - whether they have metal enclosures or not.

My interpretation is therefore that DP isolation switches as used in PV installations are, in fact, outside the scope of 421.1.201 and that metal enclosures are not required.

Can anyone provide any clarification on this matter?

Thanks,

Ted
 
I have had a reply from the IET moderators saying they have drawn Richard Townsend's attention to the thread on the IET website so hopefully we willl soon understand his thinking.
 

Reply to Domestic Installs Metal CU's also = Metal PV Isolators in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I'm looking at installing a plastic distribution board to feed a 3 phase vehicle charger. I've never been clear on whether flats being present in...
Replies
6
Views
1K
I have read a few posts with regard to Reg 421.1.201 & Similar Switchgear Assemblies, with regard to the definition of such. When 421.1.201 came...
Replies
14
Views
4K
Hi, A really simple question, so please go easy on me!! I've been asked to do a CU change on a domestic property which has PV panels...
Replies
6
Views
7K
Hi Due to the location of the meter on an upcoming job I am installing a new consumer unit in a space where there will be a full height kitchen...
Replies
17
Views
2K
So, I've been trawling through every bit of info available on AMD 3, specifically info regarding non-combustible DBs in domestic premises. Others...
Replies
57
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top