Discuss Doorbells and Voltage drop in the UK Electrical Forum area at ElectriciansForums.net

N

Nigel62

Hi All

First posting to the forum so I hope that I've posted in the correct place.

I'm looking to install a doorbell at my home in France. The distance between the bell push and the location of the bell/chime is about 40 m. I originally wanted a battery operated unit but I've been warned that, because of the distance involved, the voltage drop will be too high to operate the bell. I've also been told that this would apply to a transformer operated unit as well. Wireless units don't operate (past experience) due to the thickness of the house walls/configuration of line of sight.

Can anyone please advise me of a suitable solution, as when it comes to voltage drops I quickly need to reach for the nearest alcoholic beverage!!:grin:

Many thanks guys.
 
Using heavier cable and/or higher battery or transformer voltage will solve this. The drop will depend on the current demand of the bell. 40m of 1 mm² has a resistance of about 1.5 ohms. So the source needs to be increased by about 1.5V for every amp of current used by the bell. If using skinny cable of say 0.25mm² (four times the resistance) you would need to add four times the extra voltage, or 6V per amp of bell current. Just run it in 1.0 and will probably be fine as-is.
 
The voltage range over modern doorchimes, is anything from 3v to 10v. With most electronic chimes containing regulators, 1-1.5v volt drop is not going to make a difference.
 
No volt drop

bell_zpsbb85e720.jpg
 
With you pete, that's some length. lol
I got one which works at around 40 mtrs, I have had the reciever at the top of my garden before and it rings, the only set back with these are the pushes IMO, they seem to break easy, not visually but something inside, I seem to have to change the push every couple of years and before you ask it is not the battery in it lol
 
There's these things called mobile phones you know lads.
Visiteur- Bonjour Franque, Est tu dans la maison?
Franque - Mais oui, pour quoi?
Visiteur- Ouvré la porte. Sacré bleu!
See, easy. No volt drop, no wires.
That'll be a ÂŁ375 call out fee please
 
Last edited by a moderator:
Nigel
that is soem big house
40 metres
perhaps a butler would be the thing !!
had a similiar problem a few years back, we got round it by using a 240v bell push ( quite a chunky thing with a Neon) this clicked a relay in the main house and I used that to trigger soem door bells linked to a tranny ( the electric sort not a cross dresser)
regards jurassic Sparks
both old and stupid !
 
Using heavier cable and/or higher battery or transformer voltage will solve this. The drop will depend on the current demand of the bell. 40m of 1 mm² has a resistance of about 1.5 ohms. So the source needs to be increased by about 1.5V for every amp of current used by the bell. If using skinny cable of say 0.25mm² (four times the resistance) you would need to add four times the extra voltage, or 6V per amp of bell current. Just run it in 1.0 and will probably be fine as-is.

Thanks Lucien. So if I've understood correctly, if on a short run of say 5 m a 6V (1A) battery operated bell worked with normal bell wire, for my 40 m run I'd need to up the voltage to 7.5V (minimum) and use 1.0 mm2 cable?
 
Nigel
that is soem big house
40 metres
perhaps a butler would be the thing !!
had a similiar problem a few years back, we got round it by using a 240v bell push ( quite a chunky thing with a Neon) this clicked a relay in the main house and I used that to trigger soem door bells linked to a tranny ( the electric sort not a cross dresser)
regards jurassic Sparks
both old and stupid !

Thanks Jurassic. Actually we had a butler a few years back...only joking. Not sure about relays. In case I can't get an easier (for me) option to work could you point me towards a suitable one and explain how to wire it up please?
 

Reply to Doorbells and Voltage drop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hello All, Incase this reaches other non UK residents to confirm this doorbell has been fitted in England it regard to electricity distribution...
Replies
2
Views
4K
Hi Folks I've been trying to work out whether a doorbell will work with approximately 16m run of bell wire. I've tried to find out volt drop...
Replies
6
Views
7K
Hi All Apologies if this is not in the right forum or if I've joined the forum when I'm not supposed to as I'm not an electrician just an avid...
Replies
32
Views
21K
I've recently done a C&G 2396 Electrical Design Course and unfortunately the tutor who taught the course did so for the first time and in my...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock