Discuss Earth/Neutral fault..Help Needed!! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Probably going to get slated for not knowing/doing something wrong but here goes!!

So, been asked to do a board change for a customer, when I turned up they explained that had had a new PME done a few weeks ago, when I mentioned that their house wasn't earthed the customer said that the installers had said it 'wasn't urgent but needed doing at some point' . Anyway I did a quick ZS test on a socket and found I was getting 1.20 ohms..not bad for no earth.

I then proceeded to start dead testing the existing board, upon testing a ring circuit in the house I found that I was getting voltage (190v) between the disconnected neutrals and live. At 1 point I even had the neutral tail disconnected from the meter with the ring neutrals connected on to the neutral block to find all the electrics working in the house!! (To try and explain to the customer what is happening)

Any suggestions on where I begin to start looking for this fault??

Cheers in advance
 
i'd start by sorting out the earth -- diss. all bonding then once you have a decent earth, proceed logically. ( my grandmother was a Vulcan).
 
I then proceeded to start dead testing the existing board, upon testing a ring circuit in the house I found that I was getting voltage (190v) between the disconnected neutrals and live.
Hi - this has me confused - are you saying the double pole isolation switch in the board was off and yet you were reading 190V?
 
Hi - this has me confused - are you saying the double pole isolation switch in the board was off and yet you were reading 190V?
No, the 2 neutrals of my ring circuit were disconnected and I was reading 190v between each leg and incoming live.
[automerge]1571767195[/automerge]
Hi - this has me confused - are you saying the double pole isolation switch in the board was off and yet you were reading 190V?
...and yes I had it live with the cover off if that's what you are referring to.
 
Last edited:
No, the 2 neutrals of my ring circuit were disconnected and I was reading 190v between each leg and incoming live.
I'd expect that :rolleyes: Were you using a multimeter by any chance ?
There's capacitance between the neutrals and earth, as well as possibly some conductance (inverse or resistance). You've formed a potential divider between L & E with your meter as one leg, and the N-E impedance as the other leg. The voltage (and phase) of the midpoint (the N wires) depends on the ratio of the impedances of your meter and N-E.
 
Hi,could i ask what detailed inspection and testing,was done,regarding the earthing arrangements,at origin?

I'd expect that :rolleyes: Were you using a multimeter by any chance ?
There's capacitance between the neutrals and earth, as well as possibly some conductance (inverse or resistance). You've formed a potential divider between L & E with your meter as one leg, and the N-E impedance as the other leg. The voltage (and phase) of the midpoint (the N wires) depends on the ratio of the impedances of your meter and N-E.
How does this explain disconnecting the neutral tail coming out of the meter and the board still being live across L-N? And no not using multimeter, checked it with both my multifunction tester and voltage testers.
 
I don't understand your initial question. You know you've got an N-E fault(s), you demonstrated it to yourself and the customer. You also have suspect earthing conductor connectivity or similar. The two don't sit nicely together - they can make lots of exposed stuff live.

As per Fairlight, start testing from the beginning, systematically, in order. Make no assumptions, take no guesses. When you find the circuit with the N-E fault, check it carefully for thermal damage. Your disconnected neutral tail would have sent the entire load current of the house down it, and if it's a lighting circuit... 1mm isn't really specced for that!
 

Reply to Earth/Neutral fault..Help Needed!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
980
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock