Discuss Earthing and bonding in the UK Electrical Forum area at ElectriciansForums.net

If I've understood correctly...
For TNS and TT - line conductor over 35mm bonding goes to 16mm, from table 54.7 and reg 544.1.1
For TNCS - DNO neutral conductor over 35mm bonding goes to 16mm, from reg 544.1.1 and table 54.8.
 
Not all TNCS supplies are PME but all PME supplies are TNCS so how do you know if it's PME, will the DNO always put a sticker on?
 
Not all TNCS supplies are PME but all PME supplies are TNCS so how do you know if it's PME, will the DNO always put a sticker on?
I had not heard this ... I look in BYB section 312.2.1 fig 3.9 where TNCS and PME seem to be the same thing (?).
 
Just what I've read elsewhere, so not sure, I think you might be right though.

I suppose you could have a on site Tx which TNCS supply with no multible earthing. So if no tx on site then the TNCS supply will always be PME?
 
Last edited:
TN-C-S is generally considered PME with some exceptions, the example you give could be one.
 
Page 47/48/49 of GN8 explain (and show) the difference between PME and PNB.
Daz
 
Don't understand why you're having trouble with this?
The conductance ratio between steel and copper is about 9:1.
By the time you've found an SWA cable where the armour has a sufficient CSA to be a bonding conductor, you will require a larger bonding conductor.

95mm2 SWA has armour which has the equivalent conductance of a 10mm2 copper conductor. Unfortunately a 95mm2 SWA cable, would where PME conditions apply require a bonding conductor with the equivalent conductance of a 35mm2 copper conductor.
 
These cables would be used for supplies to other buildings where bonding would be required, the size of main bonding has already been decided at the DNO source. We are not discussing DNO supply cables.
 
These cables would be used for supplies to other buildings where bonding would be required, the size of main bonding has already been decided at the DNO source. We are not discussing DNO supply cables.
In this case then, what's to stop you using a 4C 10mm SWA (even if you don't need one), and using the 4th core for the Bonding conductor?
 
These cables would be used for supplies to other buildings where bonding would be required, the size of main bonding has already been decided at the DNO source. We are not discussing DNO supply cables.
Lol.
What does that mean?
Are you suggesting that this supply to another building would be larger than the DNO supply at source?
 
I think it is you that is having a problem with understanding.
If the main incomer requires 10mm2 bonding conductors, that would suggest the supply conductors are no greater than 35mm2.
Why would you then use 95mm2 SWA for a sub main?
 
I think it is you that is having a problem with understanding.
If the main incomer requires 10mm2 bonding conductors, that would suggest the supply conductors are no greater than 35mm2.
Why would you then use 95mm2 SWA for a sub main?
length of run ,volt drop earth loop imp. etc
 
I think it is you that is having a problem with understanding.
If the main incomer requires 10mm2 bonding conductors, that would suggest the supply conductors are no greater than 35mm2.
Why would you then use 95mm2 SWA for a sub main?
I have no idea why you keep referring to the supply conductor size, the point is can a sub main swa cable support bonding when the armour is used as the earth. This will nearly always apply to a three phase supply where the minimum size to support bonding would be 50.0. In this day and age people nearly always use three core cable utilising a core as the cpc for single phase supplies. Otherwise it would have to be 95.0 for a two core.
 

Reply to Earthing and bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
701
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
548
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
766

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock