A thing that has made me doubt what ive always done. When testing various domestic premises I have been doing a PEFC test and a PSCC test to determine if the installation is TN-S OR TN-C-S.

I was always told this is fine as the ka value will be the exact same on a TN-C-S. However today I got a Value of Pefc 617 and PSCC 586. That would make me think it was TN- S but I highly suspect this premises was TNCS. Is their an allowance for that much of a difference when testing to find out the earthing arrangement. Got a Zdb of .4 and a Ze of .21

Any help appreciated

Sent from my SM-G920F using Tapatalk
 
if it's PME then the N and E are shorted at the cut-out, so the pefc and pssc will be the same.if not, it;s not PME. or there could be a bit of hogh resistance on the N-E connection, as your figures are fairly close.
 
if it's PME then the N and E are shorted at the cut-out, so the pefc and pssc will be the same.if not, it;s not PME. or there could be a bit of hogh resistance on the N-E connection, as your figures are fairly close.
Yeah I'm 99% sure it's a TNCS system. Never thought about the high resistance in the N and E link. The cable is small enough that it looks to be TNCS aswell. I was always taught to test or ring the DNO. You can't always tell by simply looking.

Sent from my SM-G920F using Tapatalk
 
The Ze alone suggests TN-C-S.
The difference between the Ze and Zdb though, does suggest a high resistance somewhere.
How long are the meter tails?
 
Last edited by a moderator:
For a do,estimated supply I does seem to suggest that, but could equally be a sign that the DNO has been in the area bodging old lead distribution and service cables with randomly installed N-E connections all over the place.
Concur with davesparks. I recently asked the DNO about converting a TN-S system to TNC-S, mainly cos the installation had an earth rod as well and I wonder if the lead sheath was unstable or something. DNO came and had a look, and said to convert to a TNC-S myself. He said the lead sheathed supply cable was probably connected to a new PME supply somewhere out in the road anyway!
 
Last edited:

Reply to Earthing arrangement in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
745
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
680
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
944
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock