here's the question

scenario: a TN-S system, where the main earthing terminal is external to the distribution board.

the cable connected to the suppliers earth and the main earthing terminal is the main earthing conductor.

what is the title given to the protective conductor connecting the main earthing terminal to the distribution board (this is also the earth fault path for each cpc)

is it a main bonding conductor, or would it still be classed as the main earthing conductor?

your thoughts are appreciated...:)
 
here's the question

scenario: a TN-S system, where the main earthing terminal is external to the distribution board.

the cable connected to the suppliers earth and the main earthing terminal is the main earthing conductor.

what is the title given to the protective conductor connecting the main earthing terminal to the distribution board (this is also the earth fault path for each cpc)

is it a main bonding conductor, or would it still be classed as the main earthing conductor?

your thoughts are appreciated...:)

IMO the cable would be the main earthing conductor as the cable I take it is continious to MET new cable to distribution board would be bonding.

Interesting question be interested in other peoples views:)


Chris
 
I usually refer to this as the main earthing conductor, as well as the bit the other side of the MET, although the definition in the BRB states that this is between earth and the MET only. Given the apparent absence of a defined name for this bit of cable and given what it does I hearby christen it the main CPC.:D
 
Given the apparent absence of a defined name for this bit of cable and given what it does I hearby christen it the main CPC.:D

LOL - I'll make city and guilds aware of the revelation :D :D

as defined, main bonding conductors are used to connect extraneous conductive parts, not exposed conductive parts, so that should rule that option out

and the main earthing conductor is clearly defined as the connection from the suppliers means of earthing to the MET

here's a surprising one

definition:

Circuit protective conductors (CPC’s)
A protective conductor connecting exposed-conductive-parts of equipment to the main earthing terminal


I would say that's fairly definitive - a susprising answer but definitive
 
Last edited by a moderator:
right you are, so with 'B' being the main earthing terminal (external to the db), doesn't show connection to a CU or DB

if it's connecting to the exposed conductive part of the CU i.e. mettalic covering, then it's bonding.

but i'm asking specifically what the conductor that connects the MET to the earth bar in a DB.

purely on definition i'd say CPC
on practicality and it's function i'd say main earthing conductor
 

Reply to earthing conductor query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
785
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
858
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
709

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock